Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > Electricians Forum - Must Read > Electricians Forum Rules
Forgot Password? Join Us!

Electricians Forum Rules Please read these important rules before using the Electricians Forum.

Reply
 
LinkBack Thread Tools Display Modes
Old 25-12-2007   #1 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 571
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Any Rules you'd like to see?

Rule suggestions, which you want to see within this community forum are always welcome.

Please post them here or send me a PM

regards Luke


If You Build It, They Will Come!!!!!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-01-2008   #2 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 232
View Grae79's Photo Album
Default Re: Any Rules you'd like to see?

no eating after midnight!
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-01-2008   #3 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 262
View ian.settle1's Photo Album
Default Re: Any Rules you'd like to see?

Quote:
Originally Posted by LScotty View Post
Rule suggestions, which you want to see within this community forum are always welcome.

Please post them here or send me a PM

regards Luke
How about all new members get a twelve pack of beer sent to them.

Administat ors face on seeing this

Last edited by ian.settle1; 27-01-2008 at 10:07 PM.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-01-2008   #4 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 232
View Grae79's Photo Album
Default Re: Any Rules you'd like to see?

will second that....but make it a 24 crate
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-01-2008   #5 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 262
View ian.settle1's Photo Album
Default Re: Any Rules you'd like to see?

Plus a bottle of scotch as well I think now.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-01-2008   #6 (permalink)
EasyFox
Senior Member
 
EasyFox's Avatar
 
Join Date: Sep 2007
Posts: 322
View EasyFox's Photo Album
Default Re: Any Rules you'd like to see?

Quote:
Originally Posted by ian.settle1 View Post
How about all new members get a twelve pack of beer sent to them.

Administat ors face on seeing this
And it's not allowed to be LAGER !!!!!

EasyFox is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Forum Rules : Must Read UPDATED!! LukeScotty Electricians Forum Rules 7 02-07-2008 10:30 AM
Wots The Rules On Periodics MING Business Related 3 20-01-2008 09:53 PM

Google Search
Google

All times are GMT +1. The time now is 10:22 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Fast Loans : Repair Bad Credit : MPAA : Bad Credit Mortgages : Loans

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28