Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > General Electrical Discussion
Forgot Password? Join Us!

General Electrical Discussion All your electrical questions regarding electrics from within the United Kingdom. Anything that doesn't fit into any other forum that is electrical related can be posted in here.

Reply
 
LinkBack Thread Tools Display Modes
Old 13-06-2008   #1 (permalink)
lkpflk
Junior Member
 
Join Date: Jun 2008
Posts: 2
View lkpflk's Photo Album
Default connecting 415v 3 phase motor

i have replaced a 415v 3 phase motor at work. The old one had 3 terminals in a line, each with one internal wire connected, and one terminal on other side with 3 internal wires connected. The new one has 6 terminals, each with one internal wire connected. It came with 3 bridging links which i have used. However, when i run motor, it trips on overload after about 20 seconds, and blows a fuse. It also feels warm. Obviously, it is not connected correctly. Would appreciate any help. Thanx.

lkpflk is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-06-2008   #2 (permalink)
benji
Member
 
Join Date: Jun 2008
Posts: 43
View benji's Photo Album
Default Re: connecting 415v 3 phase motor

is the new motor same size/spec. as old one,check plate on motor ,when you connect motor are you connecting it in star or delta (check where you put the links)what size is the motor kw
yours benji
benji is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-06-2008   #3 (permalink)
lkpflk
Junior Member
 
Join Date: Jun 2008
Posts: 2
View lkpflk's Photo Album
Default Re: connecting 415v 3 phase motor

it is a 7.5kw motor, and the same spec as old one. As for star or delta, i don`t know. Just want it to work. Thanx.

sorry, that should read 0.75kw.

Last edited by lkpflk; 13-06-2008 at 10:03 PM. Reason: Automerged Doublepost
lkpflk is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-06-2008   #4 (permalink)
jibtech
Member
 
Join Date: Jun 2008
Posts: 79
View jibtech's Photo Album
Default Re: connecting 415v 3 phase motor

it sounds like the old motor was connected in "star" configuration

to achieve this the links need to go across the secondary terminals rather than between the two sets
jibtech is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-06-2008   #5 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: connecting 415v 3 phase motor

Read the rating plate and see what it says . Connect links accordingly.

Would draw a picture but dont know how, not much good with computers, but in star, the 3 phases need connecting to U1 V1 W1, and the links want to be accross U2 V2 W2.

In delta it should be the three phases conected to U1 V1 W1 and then linked as follows, U1 toW2, (one link) V1 to U2 (second link) and W1 to V2 (last link)

This is providing it is a standard motor with nothing oddball about it, would be worth checking to see if you have all three phases at the motor, and putting the clamp meter on under load conditions and setting overload accordingly. Have you found out what knackered the old one, because if there is say a phase missing, or a dodgy contactor, then the new motor probably wont last long either.

Let us know how you get on.

Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Single phase motor elmer phud Commercial and Industrial Electrical 10 12-10-2008 06:44 PM
Testing Zs for Three Phase Motor DanBrown Inspection, Testing and Certification of Electrical Installations 1 10-08-2008 08:58 PM
230v single phase motor wannabesparky General Electrical Discussion 9 06-07-2008 02:35 PM
3 phase industrial motor wiring tonyrigley New Member Introductions 1 24-06-2008 08:29 AM
Help me for selecting a AC motor!!!!!! thanhtongminh Commercial and Industrial Electrical 2 04-05-2008 12:48 PM

Google Search
Google

All times are GMT +1. The time now is 05:55 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38