Default Immersion and garage

Hi all
First i am not a spark. I do have a question though. Should a garage with internal plugs be on the same line as the immersion heater. Mine is. The garage also has no RCD protection but does have an mcb inside it. Would it be ok to turn this into an rcbo and so meet the requirment for sockets?.

John is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-06-2008   #2 (permalink)
danzor
Senior Member
 
danzor's Avatar
 
Join Date: Feb 2008
Posts: 191
View danzor's Photo Album
Default Re: Immersion and garage

immersion should be on its own circuit.

RCBO's and heating elements really don't go to well together either.
danzor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-06-2008   #3 (permalink)
Had8Lives
Member
 
Join Date: Apr 2008
Posts: 48
View Had8Lives's Photo Album
Default Re: Immersion and garage

Hi John, Does your consumer unit have any spare MCBs or spaces for extra MCBs? Possible solution would be to get a spark to rewire garage sockets onto a seperate RCBO in the consumer unit. If the wiring is really old it may be that the immersion heater has been tapped off the socket ring circuit :-O. I've seen it done when I've been doing a re-wire.
Had8Lives is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-06-2008   #4 (permalink)
John
Junior Member
 
Join Date: Jun 2008
Posts: 2
View John's Photo Album
Default Re: Immersion and garage

Thanks for the replies. I think i have got this sorted. The mcb supplied both the immersion and the garage. Im going to put the immersion on the mcb side only and use my rcb with 32a mcb for the garage. I think im going to use an rcbo for the sockets upstairs though so that things like morning alarms are not lost if the main rcb trips out. The more i think about it i really like the idea of rcbo's for everything needing an rcb (yes i know it costs a lot more) but the idea of single failures is more appealing than losing the lot on a trip.
John is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-07-2008   #5 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: Immersion and garage

Quote:
Originally Posted by John View Post
Thanks for the replies. I think i have got this sorted. The mcb supplied both the immersion and the garage. Im going to put the immersion on the mcb side only and use my rcb with 32a mcb for the garage. I think im going to use an rcbo for the sockets upstairs though so that things like morning alarms are not lost if the main rcb trips out. The more i think about it i really like the idea of rcbo's for everything needing an rcb (yes i know it costs a lot more) but the idea of single failures is more appealing than losing the lot on a trip.
and it satisfies the requirements of Reg 314.1

Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 07:58 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Loans : American Tax Relief : Debt Consolidation : Remortgages : Mortgage

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28