Old 04-07-2008   #1 (permalink)
the sparky
Junior Member
 
Join Date: Jul 2008
Posts: 2
View the sparky's Photo Album
Question non electrician but with 2391 work on live boards?

Hi all newby here,

can a non qualified electrician but with the 2391 work on live boards??

live working is a no full stop but in this instants its unavoidable.

i know the training for the 2391 has to have live tests but are they qualified enough to be working on live boards?


thanks

the sparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2008   #2 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Not sure you can take the 2391 without having at least part 1. The college I took mine at wouldn't let you sit 2391 without passing part two of 2360 (or whatever they call it now). Our apprentice who has qualified found that they now won't take you on 2391 unless you have had a decent amount of practical experience as well. There is a very high failure rate, and I think most colleges want to keep their pass rates as high as possible, and allowing non qualified people to do the course won't help their statistics.
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2008   #3 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Quote:
Originally Posted by the sparky View Post
Hi all newby here,

can a non qualified electrician but with the 2391 work on live boards??

live working is a no full stop but in this instants its unavoidable.

i know the training for the 2391 has to have live tests but are they qualified enough to be working on live boards?


thanks
Hi
Anyone can work on a "live" board it doesnt matter about what number qualification you have ,if you want to do it go right ahead,enjoy yourself ,you only live once
atvbitwww
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2008   #4 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Quote:
atvbitwww
Gosh - us old duffers might need a translation for this one!
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2008   #5 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: non electrician but with 2391 work on live boards?

all the very best in the whole wide world
isnt having the 239 but not being qualified a bit like a pub without beer?
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-07-2008   #6 (permalink)
Moog
Member
 
Join Date: May 2008
Location: midlands
Posts: 76
View Moog's Photo Album
Default Re: non electrician but with 2391 work on live boards?

electricity at work says NO think its section 14 or 15 on live working and competence

Quote:
Originally Posted by wayne View Post
all the very best in the whole wide world
isnt having the 239 but not being qualified a bit like a pub without beer?
It the reason they won't let you do lvl 3 certifcation anymore without already having experience or lvl 2 course (part P /2330 etc).

Quote:
Originally Posted by greekislandlover View Post
Gosh - us old duffers might need a translation for this one!
I thought he just had parkinsons or DTs

Last edited by Moog; 06-07-2008 at 05:08 PM. Reason: Automerged Doublepost
Moog is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-07-2008   #7 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Quote:
Originally Posted by greekislandlover View Post
Not sure you can take the 2391 without having at least part 1. The college I took mine at wouldn't let you sit 2391 without passing part two of 2360 (or whatever they call it now). Our apprentice who has qualified found that they now won't take you on 2391 unless you have had a decent amount of practical experience as well. There is a very high failure rate, and I think most colleges want to keep their pass rates as high as possible, and allowing non qualified people to do the course won't help their statistics.
there are no pre-requisites for sitting the 2391, - not even a regs qualifacation!

Of course, it is desirable to have experience etc etc but not an absolute

Re: working on live boards

2391 doesnt 'qualify' you to do anything, but is a good bench mark for competence, which is what is required. Sufficient knowledge experience to avoid danger etc etc

What exactly do you intend doing on these boards?

i differenttiate between 'working' and 'testing' - if you want to measure Ze, PFC's etc then you no option to go live
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-07-2008   #8 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Quote:
there are no pre-requisites for sitting the 2391, - not even a regs qualifacation!

Of course, it is desirable to have experience etc etc but not an absolute
OK - I understand this. To my knowledge all of the colleges around here that run 2391 are constantly over subscribed by a large number, and seem to feel the need to keep us the pass rate, so tend to want 2360 or equivalent plus some experience as course entry qualifications, or electricians that have been working in the trade for a decent lenght of time.

If most colleges are over subscribed nationwide (and I don't if this is the case or not - just assuming), then maybe this is a national picture. With that in mind, I just find it a little difficult to believe that someone has been accepted for, and passed a 2391 qualification without other qualifications or experience.
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-07-2008   #9 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Quote:
Originally Posted by greekislandlover View Post
OK - I understand this. To my knowledge all of the colleges around here that run 2391 are constantly over subscribed by a large number, and seem to feel the need to keep us the pass rate, so tend to want 2360 or equivalent plus some experience as course entry qualifications, or electricians that have been working in the trade for a decent lenght of time.

If most colleges are over subscribed nationwide (and I don't if this is the case or not - just assuming), then maybe this is a national picture. With that in mind, I just find it a little difficult to believe that someone has been accepted for, and passed a 2391 qualification without other qualifications or experience.
i would tend to agree with you

i each 2391 for a private training company, the vast majority of my 2391 students will have done the EAL DEI and 17th with me, most will also have their 2392 with me as well.

I am not interested in pass rates, i never even keep track of them. I am more concerned with putting students in for quals which are beyond their current capabilities. i have withdrawn students from 2391 previously because they have failed their regs exam

But my whole point is those are my rules not C&G's
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-07-2008   #10 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: non electrician but with 2391 work on live boards?

Fair play to you Shakey, common sense does appear at times in our industry. After more years than I care to think about in the industry I did 2391 last year as a proof of competance. Half of those on the course were retraining and had taken a Part P course and were then taking 2391 too (paid for as part of re-training), there was also one person who had been offered a job with a testing company and needed it to show customers, other than that he had no electrical experience. I wonder at times what I gained my qualifications for. seriously though, isn't it time our industry toughened itself up.

tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Help Finding Electrical Work Dan Business Related 7 2 Weeks Ago 06:57 PM
Becoming an Electrician : Information LukeScotty Electrical NVQ's & Courses 2 27-10-2008 03:26 AM
Looking for unpaid work!!! Trouble Electricians Unite - Jobs In Your Area 3 09-10-2008 08:55 PM
Electrician Mates Work Required Plymouth irishsailor Electricians Unite - Jobs In Your Area 0 30-07-2008 09:41 PM
Work Wanted as an Apprentice Electrician (liverpool) aconnor64 Electricians Unite - Jobs In Your Area 15 27-06-2008 11:45 PM

Google Search
Google

All times are GMT +1. The time now is 07:44 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38