Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > General Electrical Discussion
Forgot Password? Join Us!

General Electrical Discussion All your electrical questions regarding electrics from within the United Kingdom. Anything that doesn't fit into any other forum that is electrical related can be posted in here.

Reply
 
LinkBack Thread Tools Display Modes
Old 04-08-2008   #1 (permalink)
gt67
Member
 
gt67's Avatar
 
Join Date: May 2008
Posts: 34
View gt67's Photo Album
Default shower cable help

So we are redecorating our rental flat in preparation for a new tenant and “she who must be obeyed” has bought an electric shower to replace the old one that just had connections to the hot and cold feeds.

The manufactures destructions say that “in most cases it can be wired with 1.5mm” but I think this is a tad small so I was going to use min 6mm cable and leave a note taped to the cu stating the cable size used. I cant see anywhere in the instructions to say the power rating.

Before anyone says that I should not be doing this (as I am not qualified) I intend to get all the electrics tested by a qualified electrician (mate) as part of the landlords checks etc that have to be done.

In your professional opinion, is using 6mm2 cable ok or should I be using 10mm? I am going to call the manufactures later to get their view but I would rather have the views of the workers who do it.

Thanks for the advice


Cheers,

GT
gt67 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-08-2008   #2 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: shower cable help

Quote:
Originally Posted by gt67 View Post
So we are redecorating our rental flat in preparation for a new tenant and “she who must be obeyed” has bought an electric shower to replace the old one that just had connections to the hot and cold feeds.

The manufactures destructions say that “in most cases it can be wired with 1.5mm” but I think this is a tad small so I was going to use min 6mm cable and leave a note taped to the cu stating the cable size used. I cant see anywhere in the instructions to say the power rating.

Before anyone says that I should not be doing this (as I am not qualified) I intend to get all the electrics tested by a qualified electrician (mate) as part of the landlords checks etc that have to be done.

In your professional opinion, is using 6mm2 cable ok or should I be using 10mm? I am going to call the manufactures later to get their view but I would rather have the views of the workers who do it.

Thanks for the advice
1.5mm

even clipped direct thats only 20A, which is only 4.6kW

10mm will give you 64A which gives you 14.7Kw

6mm will give you 47A 10.8Kw

note that these are all clipped diect, so no correction factors applied

how big is the shower?
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-08-2008   #3 (permalink)
gt67
Member
 
gt67's Avatar
 
Join Date: May 2008
Posts: 34
View gt67's Photo Album
Default Re: shower cable help

It is this one and it doesnt come with a power rating:

Galaxy Showers - G2000LX

I have just spoken to their technical support team and they said it doesnt have a power rating as such which I find very supprising. They recon it is a 13A low power requirement one.

Thoughts?

Cheers,

GT
gt67 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-08-2008   #4 (permalink)
KFORDHUNTER
Member
 
Join Date: Jul 2008
Posts: 54
View KFORDHUNTER's Photo Album
Default Re: shower cable help

Had a look at the instructions mate and the giveaway is that there is a hot and cold supply, therefore the water is heated throught the boiler instead of the actual unit, i would say and this is a guess that you are supplying power to a pump contained in the shower unit.

Do as the manufacturer says mate, i would spur off the ring main into a 3a fused spur and feed the shower from there, or tap into the lighting circuit and put a 3a spur before the shower whichever is easier, but make sure whatever circuit you tap into is covered by an rcd at the consumer unit, oh and make sure you have adequate bonding at your gas and water.

Hope this helps.
KFORDHUNTER is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-08-2008   #5 (permalink)
gt67
Member
 
gt67's Avatar
 
Join Date: May 2008
Posts: 34
View gt67's Photo Album
Default Re: shower cable help

Thanks for the replies. I will do as you say and run a spur off the ring which has a 30mA rcd device at the cu.


Cheers,

GT
gt67 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Cable for Insulated Concrete Form House adw223 General Electrical Discussion 2 17-08-2008 04:40 PM
Electric shower advice needed crofty83 General Electrical Discussion 7 05-08-2008 09:52 PM
Electric Shower & Consumer Unit within my flat Southsider General Electrical Discussion 11 04-08-2008 10:46 PM
12v downlights - help required DonaldJ General Electrical Discussion 10 20-06-2008 08:43 AM
Sizing DB and cable LOST319 General Electrical Discussion 3 01-05-2008 09:30 PM

Google Search
Google

All times are GMT +1. The time now is 03:39 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38