Old 05-08-2008   #1 (permalink)
crofty83
Junior Member
 
Join Date: Aug 2008
Posts: 1
View crofty83's Photo Album
Default Electric shower advice needed

Recently my father fitted a new shower but after about 3 minutes of use the trip switch on the MCB trips (which is rather anoying). The only rating I can find on the MCB for the shower is B32, this could be wrong though.

Any ides on why this is happening would be greatfully appreciated. Thanks

The shower is rated to 8.5kw and a link to it is below

Buy Caselona II 8.5kW Electric Shower. at Argos.co.uk - Your Online Shop for .

crofty83 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #2 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Electric shower advice needed

basic power calculations can tell you your problem
replace fuse with a big nail that should sort everything out (we miss rum)
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #3 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: Electric shower advice needed

MCB is the right size for 6mm cable (assuming he used 6mm?). Needs further investigation. I would pay a spark to come round and sort the problem if I were you

Quote:
Originally Posted by wayne View Post
basic power calculations can tell you your problem
replace fuse with a big nail that should sort everything out (we miss rum)
Now now RumWayne

Last edited by Cirrus; 05-08-2008 at 07:45 PM. Reason: Automerged Doublepost
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #4 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: Electric shower advice needed

By my rough calcs, 32a breaker is too small. A 40a would probably sort it.
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #5 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: Electric shower advice needed

Sorry, went into auto pilot - I meant to say 40A, not 32. Just been messing about with cookers all day!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #6 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Electric shower advice needed

Quote:
Originally Posted by Cirrus View Post
MCB is the right size for 6mm cable (assuming he used 6mm?). Needs further investigation. I would pay a spark to come round and sort the problem if I were you



Now now RumWayne
sorry ,usually i give sound advice but every so often the other voices in my head make me post silly things....im off to see the wizard.....
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #7 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: Electric shower advice needed

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-08-2008   #8 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Electric shower advice needed

Quote:
Originally Posted by crofty83 View Post
Recently my father fitted a new shower but after about 3 minutes of use the trip switch on the MCB trips (which is rather anoying). The only rating I can find on the MCB for the shower is B32, this could be wrong though.

Any ides on why this is happening would be greatfully appreciated. Thanks

The shower is rated to 8.5kw and a link to it is below

Buy Caselona II 8.5kW Electric Shower. at Argos.co.uk - Your Online Shop for .
your shower pulls just on 37A

A type B MCB trips off instantaneously at 3 to 5 times its rating (90-150 amps approx)

it is designed to carry 32A indefintely, and above that its a matter of time against current

ie, the more current you overload it with the quicket it will blow

You will need a B40 in there and should be looking at at least 6mm cable, but maybe even 10mm even if there is thermal insulation etc

My advice? Get a sparks in, you have already overloaded the circuit

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Wanting career change - advice needed! hillcbt General Electrical Discussion 31 25-08-2008 03:07 PM
Electric Shower & Consumer Unit within my flat Southsider General Electrical Discussion 11 04-08-2008 10:46 PM
Advice needed please bazfalty Electrical NVQ's & Courses 4 02-06-2008 08:15 PM
Course advice needed CT13 Electrical NVQ's & Courses 4 07-05-2008 12:42 PM
Advice needed on doing some private work. jibspark General Electrical Discussion 8 29-11-2007 12:38 AM

Google Search
Google

All times are GMT +1. The time now is 05:19 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38