Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > General Electrical Discussion
Forgot Password? Join Us!

General Electrical Discussion All your electrical questions regarding electrics from within the United Kingdom. Anything that doesn't fit into any other forum that is electrical related can be posted in here.

Reply
 
LinkBack Thread Tools Display Modes
Old 14-08-2008   #1 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Mixed voltages in cables

Here's one chaps,

I was talking to a bloke the other day who claimed it was ok to have 415v AC and 24v DC running through the same cable (2.5,7 core) at the same time.
This was for a 3ph motor, with the 24v being for an early break control through a 4th pole in the isolator, and back to the contactor coil.
He has an NIC ticket on the job, so says its definitely ok.

Now, when I was at the water board, we had it drummed into us that this was a no no. They wouldnt even let us put mixed voltage cables in the same ducting.

All this was under the 16th edition by the way, and I want to know who is right, and has it changed under the 17th ?

Am hoping those with more regs know-how than me can help !

Will leave it with you , off for a curry and some beer !

Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-08-2008   #2 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Mixed voltages in cables

the waterboard has there own rules seperateto the regs
look up the rules in the osg page 64 (old book new 17th not out yet)
post back if still unsure
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-08-2008   #3 (permalink)
wattsup
Senior Member
 
Join Date: Jun 2008
Posts: 236
View wattsup's Photo Album
Default Re: Mixed voltages in cables

Normally, control voltage should be separate. But,... I'm not certain btw, if the interlock lv feeder is used on the same piece of equipment the mains feed is controling. I'm fairly sure it's ok to do so.

Last edited by wattsup; 14-08-2008 at 07:24 PM.
wattsup is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-08-2008   #4 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: Mixed voltages in cables

cheers for the replies fellas !
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #5 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: Mixed voltages in cables

hi
Absolute no no ,in my opinion,whatever ythe regs say ,and i would go as far as using screaned cable for the 24v, i have had variovs faults over the years ,mainly with plc controls where voltage has been induced from ac into dc lines,so for that reason alone i would not do it
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #6 (permalink)
spark-doctor
Senior Member
 
Join Date: Aug 2008
Location: Dorset
Posts: 295
View spark-doctor's Photo Album
Default Re: Mixed voltages in cables

The regs say you can do if you comply with one of the conditions in 528.1 but as Rum says be careful. You could get some strange goings on.

Last edited by spark-doctor; 15-08-2008 at 01:22 AM.
spark-doctor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #7 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: Mixed voltages in cables

Quote:
Originally Posted by rumrunner View Post
hi
Absolute no no ,in my opinion,whatever ythe regs say ,and i would go as far as using screaned cable for the 24v, i have had variovs faults over the years ,mainly with plc controls where voltage has been induced from ac into dc lines,so for that reason alone i would not do it

Cant say I would use screened, but certainly a separate SWA,as it was not driving a PLC input, but a contactor coil.


Rum is back lads !

Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Cables Selection homeboyworkshop Wiring, Theories and the Regulations 0 21-10-2008 04:39 PM
Barn Conversion Cables in Void Spike Wiring, Theories and the Regulations 4 31-05-2008 11:10 AM
Hidden cables bode2008 General Electrical Discussion 11 26-03-2008 02:22 PM
Insulation and Cables Pat Tester General Electrical Discussion 1 11-02-2008 11:17 PM
jim - problem with the insulation and pvc cables jim murdoch General Electrical Discussion 3 12-01-2008 11:52 AM

Google Search
Google

All times are GMT +1. The time now is 04:58 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38