Old 15-08-2008   #1 (permalink)
oldschool8604
Junior Member
 
Join Date: Aug 2008
Posts: 2
View oldschool8604's Photo Album
Default humidity regulator...relay

Can someone help me wire this?

Basically, it is for a humidity control switch.

9 - NC
10 - COM
11 - NO


I have power to the unit. But now I need to connect it to my dehumidifier so it can be switched on and off by the relay depending on the humidity of the room.



The controller is from Love Controls.

The service manual: http://www.dwyer-inst.com/PDF_files/HS_iom.pdf

I am not an electrician...I'm a biologist...so be nice about my stupidity.

oldschool8604 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #2 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: humidity regulator...relay

Am presuming that the 'power' to the relay is coming from some sort of humidistat.

Think of the relay as being an electricaly operated switch and is switched on when power is applied to the coil. You need to switch the dehumidifier with the C and NO terminals.

If you think you could wire it up to a normal switch , then just use the relay instead.

Failing that, GET A SPARK TO DO IT, and get back to your lab and cut some more rats up, or whatever it is you do.
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #3 (permalink)
oldschool8604
Junior Member
 
Join Date: Aug 2008
Posts: 2
View oldschool8604's Photo Album
Default Re: humidity regulator...relay

Hahaha ok ok I'll go back to the rats. I've got an electrician for the rest of the place I just didn't want to bother him. I'm going to ask him now. Thanks for your help.


Quote:
Originally Posted by Spudmiester View Post
Am presuming that the 'power' to the relay is coming from some sort of humidistat.

Think of the relay as being an electricaly operated switch and is switched on when power is applied to the coil. You need to switch the dehumidifier with the C and NO terminals.

If you think you could wire it up to a normal switch , then just use the relay instead.

Failing that, GET A SPARK TO DO IT, and get back to your lab and cut some more rats up, or whatever it is you do.
oldschool8604 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #4 (permalink)
montybaber
Respected Member
 
montybaber's Avatar
 
Join Date: Aug 2008
Posts: 404
View montybaber's Photo Album
Default Re: humidity regulator...relay

I assume the controller is in an enclosure housing a relay/contactor for controlling the dehumidifier, you will need to find out the coil voltage and run a protected feed to terminal 10 and connect terminal 11 (assuming you will set up the controller using normally open contacts) to A1 of the coil of the relay/contactor, you will then have to supply the A2 of the coil with either a permanent neutral or negative.

obviously the feed for the dehumidifier will switch via the relay/contactor with the coil controlled via the humidity controller.

That is all based on assumption of the setup, can you give more details please
montybaber is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-08-2008   #5 (permalink)
wattsup
Senior Member
 
Join Date: Jun 2008
Posts: 236
View wattsup's Photo Album
Default Re: humidity regulator...relay

A quick look: it depends if you want run or fall of humi
If you want run on rise term n/c if you want fall term n/o.
I'm assuming your unit is not greater than 8 amps @230v (thats all the relay can handle)

If the above is correct, then it's a simple matter of the relay providing a supply to the said unit. If your unit is greater than 8 amps, then you will need to use a contactor....
As Mr Darwin said, if you cannot adapt then the gene will become extinct..sorry couldn't resistor it..
wattsup is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-08-2008   #6 (permalink)
montybaber
Respected Member
 
montybaber's Avatar
 
Join Date: Aug 2008
Posts: 404
View montybaber's Photo Album
Default Re: humidity regulator...relay

I would have thought the controller contacts would be used to supply a coil voltage to run the dehumidifier via a contactor/control relay etc.

montybaber is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 06:24 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38