Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > General Electrical Discussion
Forgot Password? Join Us!

General Electrical Discussion All your electrical questions regarding electrics from within the United Kingdom. Anything that doesn't fit into any other forum that is electrical related can be posted in here.

Reply
 
LinkBack Thread Tools Display Modes
Old 17-08-2008   #1 (permalink)
KFORDHUNTER
Member
 
Join Date: Jul 2008
Posts: 54
View KFORDHUNTER's Photo Album
Default Size of equipotential bonding????????

If you do a board change and the installation only has 6mm2 earth cable to its gas and water is it a requirement of the regulations that you change it for 10mm2? Or can you recommend its upgrade but if its declined just leave it?

Help appreciated

KFORDHUNTER is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 17-08-2008   #2 (permalink)
mpfisher@hotmai
Senior Member
 
mpfisher@hotmai's Avatar
 
Join Date: Jul 2008
Location: Leeds
Posts: 124
View mpfisher@hotmai's Photo Album
Default Re: Size of equipotential bonding????????

Good question........ i believe if its TNS and you do the calculations its ok but TNC-S I'm sure you gotta upgrade.

We need Shakey to give us the "real answer"
mpfisher@hotmai is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 17-08-2008   #3 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Size of equipotential bonding????????

Quote:
Originally Posted by KFORDHUNTER View Post
If you do a board change and the installation only has 6mm2 earth cable to its gas and water is it a requirement of the regulations that you change it for 10mm2? Or can you recommend its upgrade but if its declined just leave it?

Help appreciated
well 130-07-01 (16th edition), is now 130.8.1 in the 17th, and that says that the earthing and bonding must be adequate, but 130.8.1 now also says 'if neccesary for the protective measure applied for safety', and assuming your using ADS for protection, then i would say yes.

Additionally, NOT upgrading the main protective bonding, would mean, for example, that you would have to use supplementary in the bathroom (should you need to work on any circuits in there)

to be honest, the regs doesnt specifically answer this question )in my opinion) but obviously, it would be better upgraded
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 17-08-2008   #4 (permalink)
KFORDHUNTER
Member
 
Join Date: Jul 2008
Posts: 54
View KFORDHUNTER's Photo Album
Default Re: Size of equipotential bonding????????

Once again, thx mate.

KFORDHUNTER is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Main equipotential bonding conductors montybaber General Electrical Discussion 8 21-09-2008 10:30 PM
Main bonding to Alkathene water pipe. U Jay General Electrical Discussion 23 19-09-2008 09:14 PM
main bonding conductors gbrock69 Inspection, Testing and Certification of Electrical Installations 2 24-06-2008 06:18 PM
Bonding cupra52 General Electrical Discussion 13 18-02-2008 08:34 PM
Main and supplementary bonding s6stu Wiring, Theories and the Regulations 6 08-01-2008 05:50 PM

Google Search
Google

All times are GMT +1. The time now is 04:27 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38