Default Using MCB on DC system

Was asked a question today, and was not sure of the answer. Hopefully someone here will have a idea.

Someone wants to use a domestic DB on a narrow boat to distribute DC from the boats batteries to the required equipment, loads will only be small, no more than 20Amps per circuit.

Will MCB be ok to use on DC systems, as all DC sytems I have seen use fuses.

Look forward to your answers

sparky_135 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-08-2008   #2 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: Using MCB on DC system

Mcbs can be used on DC circuits but the characteristics can alter as a result. You need to check with the manufacturer that their mcbs are suitable for the application (I think you will find the majority will be for this type of use). One other thing is to check with regard to the wiring of narrow boats, they did used to have a seperate test procedure carried out by a waterways official cos the wiring standards were different. I am not sure if this is still the case as it has been some time since I was involved with one.
tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-08-2008   #3 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: Using MCB on DC system

For DC distribution in trailers I always use the good old Wylex fuse boards. This gives you the option to change to breakers if you want, and you will probably find the wholesalers will flog you them cheap. Mine did, £30 for about ten of the blighters.
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-08-2008   #4 (permalink)
spark-doctor
Senior Member
 
Join Date: Aug 2008
Location: Dorset
Posts: 295
View spark-doctor's Photo Album
Default Re: Using MCB on DC system

You can but re-setable blade fuses now. Merc vans use them but apart from merc i dont know where you can buy them.

It would be a much smaller fuse board.

spark-doctor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
4mm on 32a mcb?? KNIPEX General Electrical Discussion 13 12-10-2008 08:40 PM
electrical system design homeboyworkshop Wiring, Theories and the Regulations 4 29-09-2008 09:49 PM
Spurring from MCB DonaldJ General Electrical Discussion 2 07-07-2008 10:42 PM
MCB Tripping Jim Newman General Electrical Discussion 9 12-05-2008 11:47 AM
How does a MCB work ian.settle1 General Electrical Discussion 1 15-02-2008 09:24 AM

Google Search
Google

All times are GMT +1. The time now is 01:09 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38