Old 03-10-2008   #1 (permalink)
ElectricMick
Member
 
ElectricMick's Avatar
 
Join Date: Aug 2008
Location: Wiltshire
Posts: 47
View ElectricMick's Photo Album
Default Residual Current

Hi all, working on a 500W halogen today (just went to change bulb for inept owner) and found that there was 3V on the terminals when disconnected via the MCB. Its a TNC-S with a ZE of 0.15 and a ZS of 0.96 on that circuit. Its controlled by an IP66 switch with no earth facility. Any idea's why that 3V is still sat their with it all turned off?

ElectricMick is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-10-2008   #2 (permalink)
simonatlondon
Member
 
Join Date: Mar 2008
Posts: 52
View simonatlondon's Photo Album
Default Re: Residual Current

Inductance from a live cable, running close and parallel for considerable length buried in wall somewhere?

Similar thing with me today, TT system, 65V on cpc. Ze 6.4 ohms. But zero volts on met inside consumer unit. Cpc's were not connected at every terminal.
simonatlondon is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-10-2008   #3 (permalink)
ElectricMick
Member
 
ElectricMick's Avatar
 
Join Date: Aug 2008
Location: Wiltshire
Posts: 47
View ElectricMick's Photo Album
Default Re: Residual Current

Its all surface mounted and the cables that run alongside (2) are on the same circuit, which was off at the MCB. I must admit its had me baffled. I won't lose any sleep over it, 3v isn't much, I would just be facinated to know where it comes from as the only cables in the location are on the same circuit, which is switched off!!! Any more thoughts?
ElectricMick is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-10-2008   #4 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 573
View ian.settle1's Photo Album
Default Re: Residual Current

Quote:
Originally Posted by ElectricMick View Post
Its all surface mounted and the cables that run alongside (2) are on the same circuit, which was off at the MCB. I must admit its had me baffled. I won't lose any sleep over it, 3v isn't much, I would just be facinated to know where it comes from as the only cables in the location are on the same circuit, which is switched off!!! Any more thoughts?
As said previousl you can get an induced voltage in the cable if it run next to another cable, even if it is connected to another MCB

Now is the hour that we must say good-bye, while I'm away oh please remember me
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-10-2008   #5 (permalink)
ElectricMick
Member
 
ElectricMick's Avatar
 
Join Date: Aug 2008
Location: Wiltshire
Posts: 47
View ElectricMick's Photo Album
Default Re: Residual Current

I see where your coming from now - it was probably off the other lighting circuit. They all run through some trunking before branching off in their various directions. Now it makes sense. Cheers.
ElectricMick is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-10-2008   #6 (permalink)
4x4 mark
Member
 
4x4 mark's Avatar
 
Join Date: Jun 2008
Location: durham
Posts: 40
View 4x4 mark's Photo Album
Default Re: Residual Current

dragging some dim and distant memory up, would it not be eddy currants from other circuits causing the problem.
4x4 mark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-10-2008   #7 (permalink)
ElectricMick
Member
 
ElectricMick's Avatar
 
Join Date: Aug 2008
Location: Wiltshire
Posts: 47
View ElectricMick's Photo Album
Default Re: Residual Current

Could be any or all of above I suppose - but with 3V I'm not going to dwell on it too much. Re tested today with CU all off and no current was present at the halogen. Its sneaking through from somewhere when the whole installation is energised but its not doing any harm so will leave it. I could get the customer to pay me an arm and a leg to chase and rectify but I know they won't pay for it. Thanks all for your thoughts.

ElectricMick is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Under current / over current device DanBrown General Electrical Discussion 1 15-05-2008 08:30 PM
Sound Goes Off On T.v For Split Second Every Time The Wall Lights Ars Switched On . PAUL M General Electrical Discussion 9 08-05-2008 02:16 PM
where to find the protective device operating current (I2) in 7671??? LukeScotty Wiring, Theories and the Regulations 5 22-01-2008 12:05 PM
Cable selection taking into account ''Startup Current'' DanBrown General Electrical Discussion 3 06-01-2008 07:33 PM
residual current? robbiec202 General Electrical Discussion 1 23-08-2007 08:24 PM

Google Search
Google

All times are GMT +1. The time now is 02:26 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38