Old 03-09-2007   #1 (permalink)
lawrenso
Junior Member
 
Join Date: Sep 2007
Posts: 2
View lawrenso's Photo Album
Default Help - Eubiq wiring

Hi,

bought these powerstrips (http://www.eubiq.com/assets/pdf/inst...nmanual/SC.pdf) to be fitted in our kitchen that has nearly finished a refit. Showed our electrician and he was happy with them - so had wiring all done and re-run with cable (ring man twin and earth 2.5mm) coming out of holes in the tiles. Well, now he has tried fitting them and they won't go because the cable is not flexible enough.

These units have a plastic clip on plate that is screwed to the wall and then the powerstrip clips onto this. The rear entry at one end has a cable strain relief as per on a plug etc... and the instructions actually show using 3 core for wiring them up but he is adament that 2.5mm has to be used - even though the cable is a spur coming off a fused box on a ring main, coming down the wall behind the cabinets and down behind some tiles and coming out of the tiles for connecting to

I believe that, because of the fused spur, that a flexible cable such as a 1.5mm multi-core can be used instead of the 2.5mm twin and earth, however, he has said no (from his supervisor who hasn't stepped near or seen them) - who is right and who is wrong??

answers quickly please before we have to take cabinets down and smash some tiles off and put in ordinary sockets with all the work that entails

Cheers

Lawrenso

lawrenso is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-09-2007   #2 (permalink)
yorkshiresparky
Member
 
Join Date: Aug 2007
Posts: 31
View yorkshiresparky's Photo Album
Default Re: Help - Eubiq wiring

A quick look at the manual tells us the rating to be 40A so i'm unsure if 2.5mm is big enough. That said, if your man says 2.5mm is to be used, whats wrong with using a fused spur with a flex outlet and 2.5mm flex from that to your unit.
yorkshiresparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-09-2007   #3 (permalink)
lawrenso
Junior Member
 
Join Date: Sep 2007
Posts: 2
View lawrenso's Photo Album
Default Re: Help - Eubiq wiring

Hi YorkshireSparky,

our guy was basically putting in a fused spare, and had run 2.5mm T&E down to connect to the powerstrip - however this is not flexible enought to do the flush fitting rear connection, which we would like as having nice grey T&E showing running into the side fitting is not the most endearing of sights!!

Then, also, there is the power limitations - one of them will be running a kettle and a toaster from the same strip, the other will be doing a microwave, with the 3rd left for a small LCD and a radio (3 spares - 3 fused boxes etc....).

Can I just double check that you are saying a 2.5mm flex rather than 2.5 mm T&E?? My spark is saying that it has to be T&E as this is toughened!!! (even though I find it in some ways to be very week (fractures etc..). if you are on about flex, what and where can I get it.

Cheers

Lawrenso
lawrenso is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-09-2007   #4 (permalink)
yorkshiresparky
Member
 
Join Date: Aug 2007
Posts: 31
View yorkshiresparky's Photo Album
Default Re: Help - Eubiq wiring

Toughened? are you sure about this guy? Flex is what it says, flexible. It has thicker insulation that is less brittle, the cores are stranded to create the flexibility needed and won't break as easily as solid cores on twin and earth (flat grey).
As for the power limitations, to the best of my recollections, flex is rated higher than twin and earth anyway therefore 2.5mm flex will carry more power than 2.5mm twin and earth.
I would fit a fused spur on the end of the t & e you already have and use 2.5mm flex from the flexoutlet of the spur. Or at a push if you need the cable to be in the wall use flex with a protective capping.
All the materials will be available from a local wholesaler.

yorkshiresparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Y plan wiring help needed flying lee General Electrical Discussion 5 12-09-2008 11:25 PM
central heating wiring simonatlondon General Electrical Discussion 11 19-08-2008 01:24 PM
HELP with wiring lighting dannyboy General Electrical Discussion 3 30-07-2008 04:02 PM
3 phase industrial motor wiring tonyrigley New Member Introductions 1 24-06-2008 08:29 AM
Fixed wiring tests - UK BIGEYE General Electrical Discussion 1 06-01-2008 04:54 PM

Google Search
Google

All times are GMT +1. The time now is 01:46 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38