Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Inspection, Testing and Certification of Electrical Installations
Forgot Password? Join Us!

Inspection, Testing and Certification of Electrical Installations This Section is STRICTLY for testing PROBLEMS which members have occured, misunderstood readings, Periodic Inspection Reporting, Mathematical Equations/Solutions, Part P and other legislation which require you to Inspect and Test.

Reply
 
LinkBack Thread Tools Display Modes
Old 22-05-2008   #1 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Problem: Voltage Drop...?

I was asked to solve this and I was wondering if I was going about solving it in the proper manner so wanted some info and hoping I could get some help.

There is a voltage of 120V, and resistance of 16 amps at the start of the ground connected to the breaker. The wire goes into the ground and goes for 600ft. The wire is also 1 ott in size, which I'm thinking is around 10mm-15mm in diameter. I'm not sure what exactly that is in mm or anything like that, I still have to look that up. What is the voltage drop over the length of the wire?

Thanks,
Luke


Last edited by lukas86; 22-05-2008 at 07:24 PM.
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-05-2008   #2 (permalink)
jimmus
Junior Member
 
Join Date: Apr 2008
Location: portsmouth
Posts: 18
View jimmus's Photo Album
Default Re: Problem: Voltage Drop...?

Luke, who asked you this question?

Resistance of 16 AMPS!
ground connected to the breaker

If the cable is 600ft long, volt drop will probably be high but still

Is it a wind up?
jimmus is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-05-2008   #3 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 574
View ian.settle1's Photo Album
Default Re: Problem: Voltage Drop...?

Jimmus

I think you will find that this gent is one of our former colonial cousins(USA) with 120v and ground being mentioned.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #4 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Re: Problem: Voltage Drop...?

Hey,

Canada ya. The high current mentioned is apparently right, but the voltage drop shouldn't be 6.7V, it should be closer to 1V.
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #5 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: Problem: Voltage Drop...?

resistance is measured in ohms - current is in Amperes
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #6 (permalink)
jimmus
Junior Member
 
Join Date: Apr 2008
Location: portsmouth
Posts: 18
View jimmus's Photo Album
Default Re: Problem: Voltage Drop...?

thats why i asked if it was a wind up
jimmus is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #7 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Re: Problem: Voltage Drop...?

I'm not too sure, I don't believe so no. I have done a few calculations, with the current being 16 Amps, to get a voltage drop of 6.7 volts, the resistance would have to be 0.4188 ohms. But in this case, the resistance of the cable is approximately 0.0294 ohms, and with this resistance, the voltage drop should only be 0.470 so I don't know. Maybe I'll grab an electrician to come down with me and show me where exactly the measurements were taken from. Check all the connections again.

Also, the 4/0 awg wire, has 19 strands of 12 gauge wire. Now the resistance compared to a 4/0 wire of solid copper will be less or more? I'm thinking less and there's very little different, but would just like to know as well.

Thanks

Last edited by lukas86; 26-05-2008 at 08:44 PM. Reason: Automerged Doublepost
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #8 (permalink)
Des 56
Member
 
Join Date: May 2008
Posts: 43
View Des 56's Photo Album
Default Re: Problem: Voltage Drop...?

Is it possible to ask these questions in Welsh
I have a little difficulty understanding the flow
Des 56 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #9 (permalink)
Moog
Member
 
Join Date: May 2008
Location: midlands
Posts: 76
View Moog's Photo Album
Default Re: Problem: Voltage Drop...?

Yeah im confused too are you saying voltage =120volts Current =16Amps length of cable = 600ft = 600*12*25.4 =182880mm = 182.88m resistance of cable =pl / a where p=resistance of Copper l=length of run a=CSA of conductor and using V=IR? What was that about ground? why not just type the whole question as it was posed. All the UK tables are metric and hence the resistance of Cu vairable that we use is based upon this scale. i.e. R of 1 metre of Cu is different to 1ft of Cu even if CSA the same. Ignoring reactance the resistance equation should work but you would have to use your own tables for the specific resistance of copper per unit length. Stranded wire has higher resistance than solid as lower usable CSA. Also ask whomever posed this question whether the borg effect is being taken into account as this will make the resistance futile


Last edited by Moog; 11-06-2008 at 05:19 AM.
Moog is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
New wiring - need some help please pablo General Electrical Discussion 17 3 Days Ago 12:35 PM
Problems Caused by 'Voltage Optimisers' billm General Electrical Discussion 0 20-09-2008 07:28 PM
touch voltage sparkyork General Electrical Discussion 9 10-09-2008 03:14 PM
IEE Regulations Voltage Drop Noel Wiring, Theories and the Regulations 7 07-04-2008 06:30 PM
Testing Voltage drop using circuit impedance TonyM58 Inspection, Testing and Certification of Electrical Installations 12 08-02-2008 11:32 PM

Google Search
Google

All times are GMT +1. The time now is 11:06 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38