Looking for a bit of advice going at the back of a company who carried out a periodic in a shopping centre.
In the observations they have listed as a code 1 that the Ka rating of the MCBs are unsuitable for all the circuits in the DB as they are 3Ka with the PSC 4.8Ka.
But i thought the 4.8Ka would be in reference to the supply MCCB feeding the DB rather than the individual MCBs contained within the DB.
To establish if the 3Ka mcbs were inadequate it would be the end of each cicuit fed from each MCB.
Am i enterprating that right?Cheers for any help.
tallpault is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-02-2010   #2 (permalink)
Graeme Harrold
Senior Member
 

Join Date: May 2009
Location: North Wales
Posts: 269
Thanks: 30
Thanked 37 Times in 36 Posts
Default Re: High PFC

What if the fault occurs at the MCB, that is where the max fault current will apply with respect to each circuit NOT at the end. What is the PSCC and PFC at the supply to the DB?
Graeme Harrold is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-02-2010   #3 (permalink)
tallpault
Junior Member
 

Join Date: Feb 2009
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: High PFC

Not checked that,ill check it tomorrow.
tallpault is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2010   #4 (permalink)
pevvers
Senior Member
 
Snake Champion! Card Toss Champion! Tetrollapse Champion!
Tournaments Won: 1

Join Date: Jul 2009
Posts: 217
Thanks: 10
Thanked 23 Times in 19 Posts
Default Re: High PFC

I think I've already posted this to another thread, but have a look at 536.1 in the BRB and do some research into energy let through of both your MCB at your board and the back-up MCCB.
pevvers is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2010   #5 (permalink)
tallpault
Junior Member
 

Join Date: Feb 2009
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: High PFC

Had a better look today.
It's a Dorman Smith Panelboard,with 3 3 Phase DB,s on it, all the Mcbs are rated at 3Ka but each one of the DBs are protected by a 63Amp Bs88 Type G fuses.
Would that mean the rating of the mcbs would be negated by the 80Ka BS88 fuses.
tallpault is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-02-2010   #6 (permalink)
zupos40
Senior Member
 

Join Date: Oct 2008
Location: Tottenham
Posts: 212
Thanks: 5
Thanked 44 Times in 39 Posts
Default Re: High PFC

Quote:
Originally Posted by tallpault View Post
Had a better look today.
It's a Dorman Smith Panelboard,with 3 3 Phase DB,s on it, all the Mcbs are rated at 3Ka but each one of the DBs are protected by a 63Amp Bs88 Type G fuses.
Would that mean the rating of the mcbs would be negated by the 80Ka BS88 fuses.
As Peever stated you will have to find out what the total thermal let through energy is for both the BS 88 Type G fuse and the mcb

If the let through energy of the fuse is less then the mcb (please note they are refered to as cb now bs767:2008) then the breaker are ok to use even when fault current is greater then stated kA, you will also have to ensure that Ksquared S squared of smallest circuit is greater then the total let through energy of fuse (sorry do not have BS7671 with me to quote reg number).

To give you an example from my own research, I found out that a 100A type II BS1361 fuse has a total let through of 27,000 A2S and that typical 6kA cb (Hager MEM, ABB etc) has a total let through of 29,500 A2S and 10kA about 34,000 A2S, as a result if the ccu/ dis-board complies with the relevant standards (read GN.3) for any fault currents upto 16Ka the fuse will disconnect the fault whether earth Pefc or short Pscc before damage can occur to the c.b. and circuit conductors.


All the main manufacturer type test their board with all combination of c.b and fuses upto 16ka to ensure compliance.

So find out if your combination comply
zupos40 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
super high pfc c.boy Inspection, Testing and Certification of Electrical Installations 9 27-10-2009 10:14 AM
3 phase motor, high resistance & high amps. Dave0098 Commercial and Industrial Electrical 3 14-10-2009 02:15 AM
High PFC bearlyable Inspection, Testing and Certification of Electrical Installations 12 19-07-2009 12:50 PM
Rcbo and high integrity earthing cop out tomasi Electrical Wiring, Theories and Electrical Regulations 3 06-06-2009 06:12 PM
High PFC andyb Electrical Wiring, Theories and Electrical Regulations 35 23-04-2009 10:42 AM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK