Hi all,
this might seem a daft question ( mine usually are) but Having just passed my 2391 theory i need to book the practical and I am a bit confused about the sequence.
The only bit |I am confused about is the continuity of protective conductors. the way i do it is bonding to water and gas then link phase and cpc and measure at furthest point but then i cross link phase and neutral. The problem is I am sure I was told this was not nessasary and not one of the tests?
but the way I see it is it confirms continuity of neutral say in a lighting circuit or any radial.
Any ideas?
solo2771 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #2 (permalink)
xraytek
Senior Member
 

Join Date: May 2009
Posts: 177
Thanks: 6
Thanked 33 Times in 28 Posts
Default Re: tests

No point in checking neutral as it will get tested during functional tests.
xraytek is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #3 (permalink)
uksel
Senior Member
 

Join Date: Sep 2008
Posts: 317
Thanks: 14
Thanked 16 Times in 14 Posts
Default Re: tests

are you confusing the continuity of ring final circuit conductors with continuity of protective conductors??
uksel is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #4 (permalink)
solo2771
Senior Member
 

Join Date: Feb 2008
Posts: 140
Thanks: 5
Thanked 4 Times in 4 Posts
Default Re: tests

Quote:
Originally Posted by uksel View Post
are you confusing the continuity of ring final circuit conductors with continuity of protective conductors??
no on radial or lighting circuit.
r1 +r2 confirms phase and cpc but r1+rn would confirm neutral as a dead test

Just found this on the elecsa site and it confirms how I do it but I was told this was wrong so now really confused now.

2. Continuity of protective and bonding conductors
Reason: To check that all circuit protective conductors (green and yellow cables) are continuous and are present at every electrical accessory on the circuit. Also to check that the main earthing conductor and main bonding conductors are continuous and correctly connected.
Method 1: The line conductor is connected to the circuit protective conductor of the same circuit at the consumer unit and a measurement taken at ALL accesories on that circuit between line and c.p.c. The highest measurement obtained is recorded on the test report. Test result is R1 + R2. The line conductor and neutral conductor are then connected and the above repeated to obtain R1 + Rn
Method 2 (used for main earth and main bonding conductors): A wandering lead is connected to one end of the conductor to be tested and a measurement taken between the other end of this lead and the other end of the conductor. Test result is R2.
During this test polarity can be checked as well. The continuity of the neutral conductor can also be checked.

Last edited by solo2771; 4 Weeks Ago at 11:14 AM.. Reason: Automerged Doublepost
solo2771 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #5 (permalink)
uksel
Senior Member
 

Join Date: Sep 2008
Posts: 317
Thanks: 14
Thanked 16 Times in 14 Posts
Default Re: tests

what you found on the elecsa site is correct

this is pretty basic stuff, and i'm surprised you passed without knowing it.

but anyway congrats on passing the 2391, it's normally a pretty tough exam - the practical is a walk in the park compared to the written exam so you should have no trouble

ps. don't always listen to what people say, listen to what the books say!
uksel is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New to electrical work. When you do a small circuit at college, what tests are done? cairns Inspection, Testing and Certification of Electrical Installations 6 23-12-2009 09:30 PM
3 monthly tests on construction sites BristolSpark Inspection, Testing and Certification of Electrical Installations 10 13-04-2009 08:48 PM
ECS Tests available in Essex 1st Step Electrical Forum | General Electrical Forum 0 08-01-2009 12:13 PM
New installation - what tests should be undertaken? jsstevenson Electrical Forum | General Electrical Forum 1 05-12-2008 10:43 AM
Do you need to do continuity tests on minor work dazsafc Inspection, Testing and Certification of Electrical Installations 8 10-09-2008 12:06 PM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK