Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Inspection, Testing and Certification of Electrical Installations
Forgot Password? Join Us!

Inspection, Testing and Certification of Electrical Installations This Section is STRICTLY for testing PROBLEMS which members have occured, misunderstood readings, Periodic Inspection Reporting, Mathematical Equations/Solutions, Part P and other legislation which require you to Inspect and Test.

Reply
 
LinkBack Thread Tools Display Modes
Old 18-06-2008   #1 (permalink)
charlie
Junior Member
 
Join Date: Feb 2008
Posts: 22
View charlie's Photo Album
Default 2391 results

Did the theory on 5/6/08.
Any ideas when results released ????

charlie is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-06-2008   #2 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 275
View ian.settle1's Photo Album
Default Re: 2391 results

Maybe August sometime
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-06-2008   #3 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,027
View Shakey's Photo Album
Default Re: 2391 results

Quote:
Originally Posted by charlie View Post
Did the theory on 5/6/08.
Any ideas when results released ????
Officially they publish the results within 42 working days, so yeah, you are looking at August minimum

the results are posted on the Walled Garden first, so your tutor/examiner will know before you do

Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 10:57 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Loans : Problem Mortgage : Loans : Free Credit Report : 1-breast-pump.com

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29