Default main bonding conductors

i have recently finished a periodic test of a fairly large castle and found that the building had no main equipotential bonding conductors. There is around 22 individual consumer units situated around the building all coming via sub main supplies from the main incoming area. Must the main bonding conductors come from the point of incoming supply or can they come from any of the individual consumer units?

gbrock69 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-06-2008   #2 (permalink)
BillR3
Junior Member
 
Join Date: Jun 2008
Posts: 4
View BillR3's Photo Album
Default Re: main bonding conductors

As long as you have an in spec Zdb at your local consumer units there should be relevant equipotential bonds run from these DB's to associated services/metalwork etc as there should be from the local DB to the point of origin.

Hope this helps

BillR3
BillR3 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-06-2008   #3 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 726
View wayne's Photo Album
Default Re: main bonding conductors

often find two voices singing the same tune helps .as BillR3 said

wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 10:04 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Secured Loans : MPAA : Web Advertising : Loans : Payday Loans

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28