Thread: High Ze reading

  1. #1
    Electricians Arms Member Strickers's Avatar
    Join Date
    Jan 2009
    Location
    Colne, Lancs
    Posts
    81
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default High Ze reading

    I have recently re-wired a property with T-N-S earthing to find out that the Ze was 13.41ohm. I checked all the supply have to the spilt concentric incomer that looked pretty new. All connection were ok so i rang norweb. The question is does the DNO have to supply an earth to the property? An electrician i know said that the can just make to sort it yourself with an earth spike.

    Cheers Paul

    P'S before i left i put a 30ma RCD between the tails and the consumer unit
    .
    Last edited by Strickers; 08-03-2010 at 09:32 PM.

  2. #2
    Electricians Arms Member SirKit Breaker's Avatar
    Join Date
    Jul 2009
    Location
    Leeds, Gods County of Yorkshire
    Posts
    815
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: High Ze reading

    Last time i came across similar problem i called YEDL on behalf of the customer, they sent an engineer within the hour and PME'd it.

    Cheers............Howard
    THE IMPOSSIBLE I CAN DO AT ONCE, MIRACLES CAN TAKE A LITTLE LONGER

  3. #3
    Electricians Arms Member pevvers's Avatar
    Join Date
    Jul 2009
    Location
    London
    Posts
    550
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: High Ze reading

    Quote Originally Posted by Strickers View Post
    The question is does the DNO have to supply an earth to the property? An electrician i know said that the can just make to sort it yourself with an earth spike.
    Yep, there is a possibility that they can say that, or they could PME or fix the fault in the cable. The question has to be though, do you feel lucky?

    Another question would also be how comes you didn't check the Ze before rewiring the property though, I thought that the first thing to do would be to check whether there was an adequate earth in line with reg 131.8.

    But at least you've left it safe which some people wouldn't have done....

  4. #4
    Junior Member Baal's Avatar
    Join Date
    Aug 2009
    Posts
    25
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: High Ze reading

    The Supply company has no obligation to supply an earth however if an earth has been supplied, there is an obligation to maintain it.

    I came upon a similar situation a few months back and the DNO were out within 2 hours and found the fault after a further 2 hours.

    Ze 16.7 Ohms originally, 0.25 Ohms on completion!

  5. #5
    Electricians Arms Member Strickers's Avatar
    Join Date
    Jan 2009
    Location
    Colne, Lancs
    Posts
    81
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: High Ze reading

    Problem sorted thanks guys, the came out this week and i got a phone call from customer and a ze reading of 0.17 ohm.

Similar Threads

  1. High R1 + R2 reading...
    By sambuca2907 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 1
    Last Post: 24-11-2009, 02:34 PM
  2. Loop Test Reading too high ??
    By hoobean in forum Electrical Forum | General Electrical Forum
    Replies: 2
    Last Post: 23-11-2009, 05:17 PM
  3. Slightly high ZS reading
    By andyww in forum Electrical Forum | General Electrical Forum
    Replies: 15
    Last Post: 27-08-2009, 02:56 PM
  4. High Ze reading on a tt install
    By a.e.s in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 18
    Last Post: 15-07-2009, 08:24 PM
  5. High Zs reading how to rectify
    By BristolSpark in forum Electrical Forum | General Electrical Forum
    Replies: 5
    Last Post: 07-04-2009, 06:46 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24