High Ze reading
I have recently re-wired a property with T-N-S earthing to find out that the Ze was 13.41ohm. I checked all the supply have to the spilt concentric incomer that looked pretty new. All connection were ok so i rang norweb. The question is does the DNO have to supply an earth to the property? An electrician i know said that the can just make to sort it yourself with an earth spike.
Cheers Paul
P'S before i left i put a 30ma RCD between the tails and the consumer unit
.Last edited by Strickers; 08-03-2010 at 09:32 PM.
- 08-03-2010 #2Electricians Arms Member
- Join Date
- Jul 2009
- Location
- Leeds, Gods County of Yorkshire
- Posts
- 815
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High Ze reading
Last time i came across similar problem i called YEDL on behalf of the customer, they sent an engineer within the hour and PME'd it.
Cheers............HowardTHE IMPOSSIBLE I CAN DO AT ONCE, MIRACLES CAN TAKE A LITTLE LONGER
- 08-03-2010 #3Electricians Arms Member
- Join Date
- Jul 2009
- Location
- London
- Posts
- 550
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High Ze reading
Yep, there is a possibility that they can say that, or they could PME or fix the fault in the cable. The question has to be though, do you feel lucky?
Another question would also be how comes you didn't check the Ze before rewiring the property though, I thought that the first thing to do would be to check whether there was an adequate earth in line with reg 131.8.
But at least you've left it safe which some people wouldn't have done....
- 14-03-2010 #4
Re: High Ze reading
The Supply company has no obligation to supply an earth however if an earth has been supplied, there is an obligation to maintain it.
I came upon a similar situation a few months back and the DNO were out within 2 hours and found the fault after a further 2 hours.
Ze 16.7 Ohms originally, 0.25 Ohms on completion!
- 19-03-2010 #5Electricians Arms Member
- Join Date
- Jan 2009
- Location
- Colne, Lancs
- Posts
- 81
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High Ze reading
Problem sorted thanks guys, the came out this week and i got a phone call from customer and a ze reading of 0.17 ohm.
Similar Threads
-
High R1 + R2 reading...
By sambuca2907 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 1Last Post: 24-11-2009, 02:34 PM -
Loop Test Reading too high ??
By hoobean in forum Electrical Forum | General Electrical ForumReplies: 2Last Post: 23-11-2009, 05:17 PM -
Slightly high ZS reading
By andyww in forum Electrical Forum | General Electrical ForumReplies: 15Last Post: 27-08-2009, 02:56 PM -
High Ze reading on a tt install
By a.e.s in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 18Last Post: 15-07-2009, 08:24 PM -
High Zs reading how to rectify
By BristolSpark in forum Electrical Forum | General Electrical ForumReplies: 5Last Post: 07-04-2009, 06:46 AM


LinkBack URL
About LinkBacks



Reply With Quote







Bookmarks