Old 22-07-2008   #11 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: very high earth loop readings

thanks guys, the house is empy and getting refurbed at the minute, ive pulled the fuse on the circuit that concerns me for now and turned the board off.
im going back on the 11th august and will be fitting a 17th board so rcd wise it will be fine. like you say checking other circuits to see what reading getting off them would be good for next time. would of done that when i was there but it was the end of the day and just did a quick test on that circuit for me own benefit.

from what ive seen at this stage, is theres an swa coming across the basement ceiling that appears to be the mains incomer, i did see an ec15 atached to the sheathing of this cable and am concerned that this is what the elcetric board has in mind for a suitable earth connection!! lol

any ways im back on that job soon so will let yas all know me findings.
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #12 (permalink)
linzilou72
Junior Member
 
Join Date: May 2008
Location: Brighton
Posts: 28
View linzilou72's Photo Album
Default Re: very high earth loop readings

Quote:
Originally Posted by sparkyork View Post
thanks guys, the house is empy and getting refurbed at the minute, ive pulled the fuse on the circuit that concerns me for now and turned the board off.
im going back on the 11th august
What the hell are the other trades using for power then
linzilou72 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #13 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: very high earth loop readings

no other trades in there, the owner is a good friend of mine and is currently in france, having power off is no problem.
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-09-2008   #14 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: very high earth loop readings

finally got back to this job...

turns out the swa coming across the basment cieling is definately the incomer and when it enters the service cut out there was a bonding clamp on it, which at first looked like some sort of tn-s setup....

i was getting high readings and did a quick earth loop at socket outlet and got 67 ohms, i went to the old board and connected on the tails and on to thei eath clamp on the incomer...Error 4 .. no earth connection, then founf a 2.5 earth going down some pipe boxing and turns out that the main earth was onto the water supply! tut!

so phoned up yedl and have arranged for them to come out and convert it to PME for £31. things is they cant do it for 12 weeks so im gonna sink an earth rod in for now just to get the new board sorted out etc...
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-09-2008   #15 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 574
View ian.settle1's Photo Album
Default Re: very high earth loop readings

Quote:
Originally Posted by sparkyork View Post
finally got back to this job...

turns out the swa coming across the basment cieling is definately the incomer and when it enters the service cut out there was a bonding clamp on it, which at first looked like some sort of tn-s setup....

i was getting high readings and did a quick earth loop at socket outlet and got 67 ohms, i went to the old board and connected on the tails and on to thei eath clamp on the incomer...Error 4 .. no earth connection, then founf a 2.5 earth going down some pipe boxing and turns out that the main earth was onto the water supply! tut!

so phoned up yedl and have arranged for them to come out and convert it to PME for £31. things is they cant do it for 12 weeks so im gonna sink an earth rod in for now just to get the new board sorted out etc...
What type of meter are you using? used a Megger 2500LC somw time back kept getting the same error code booklet said it was a buffer overflow when i contacted AVO, the engineer said that it was detecting noise on the circuit whic I was testing thats why the error kept coming up.

Now is the hour that we must say good-bye, while I'm away oh please remember me
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-09-2008   #16 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: very high earth loop readings

yeah ive had this before, however all fuses were pulled and nothing was connected, tuned out that the armouring didnt have any sort of earth on it!! surely the other end must be connected to something!? so electric board said they can make it pme but got a good reading after sinking earth rod in so its up to customer now.

sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
'No trip' function. High readings?? Silk6911 Inspection, Testing and Certification of Electrical Installations 6 05-09-2008 05:36 PM
loop readings carlhenry01 Inspection, Testing and Certification of Electrical Installations 7 04-08-2008 11:10 PM
High Zs readings Rory Inspection, Testing and Certification of Electrical Installations 1 05-06-2008 10:46 PM
earh loop thunder General Electrical Discussion 5 25-11-2007 06:35 PM

Google Search
Google

All times are GMT +1. The time now is 10:35 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38