Old 21-08-2008   #1 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 723
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Questions asked on your testing assessment

whether your with niceic, napit, elesca etc, please state what questions u can remeber which you had on ur assessment for testing and inspection, include which scheme you was assessed by?......


If You Build It, They Will Come n If it aint broken don't fix it!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-08-2008   #2 (permalink)
PAUL M
Respected Member
 
Join Date: May 2008
Posts: 505
View PAUL M's Photo Album
Default Re: Questions asked on your testing assessment

Quote:
Originally Posted by LukeScotty View Post
whether your with niceic, napit, elesca etc, please state what questions u can remeber which you had on ur assessment for testing and inspection, include which scheme you was assessed by?......
1)Did you test the installation. 2)How do you do r1+r2 test,3)how do you test a ring main continuity 3)what should the expected values be 4)how do you perform insulation resistance test 5)what are the minimum values acceptable 6)how do you check polarity/why do you haxe to check polarity 7)how do you test ELI 8)BLAH BLAH RCD each time i explained a test to him he came back with "now you have explained how to do the test can you perform it explaining why results are acceptable" 9)can i pinch one of your fags, hope thats mature enough for you luke its all i can remember but the guy was ok,give me some good advice. he did ask me one more question now i come to think of it "WHY ARE YOU PUTTING THSE CROCK CLIPS ON MY TESTACLES" SORRY NICEIC
PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-08-2008   #3 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Questions asked on your testing assessment

Assessed by NICEIC:

1, Explain the TT earthing system
2, What is the max Ze of TNC-s & TN-s (0.35ohm & 0.8ohm)
3, What is the max time for a BS EN61008 at x1
4, What is the max trip time allowed for an rcd trip under x5 test
5, Why are rcd's required on TT systems (on 16th assessment).
6, What is the max rated ocpd for a 2.5mm radial circuit & what could it be if the conductors were 4mm.
7, where is the max Zs for a BS60898 32amp type B found in 7671 (show the bloke).
8, Explain how you would undertake the ring final continuity test.
9, What csa of MEC would be used on TNC-s system.
10, Which result would you use on cert after undertaking PSCC & PFC.
11, Why are the max Zs values different in the osg & 7671.

Thats a few I've been asked that I can remember.

Forgot one

12, Do you use croc clips

Last edited by EasyFox; 21-08-2008 at 09:52 PM.
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #4 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 622
View sparkyork's Photo Album
Default Re: Questions asked on your testing assessment

1, Explain the TT earthing system, overhead line & neatral supply with no earth provided, earthing is generally gained by using earth rod(s), 100ma time delay main sw? 30ma sockets etc. in event of a fault the current flows to earth through the rod through the general mass of earth back to the transformer winding centre tap thing?!

3, What is the max time for a BS EN61008 at x1 300ms?
What is the max trip time allowed for an rcd trip under x5 test 40ms?

5, Why are rcd's required on TT systems cos of normally high Zs readings

6, What is the max rated ocpd for a 2.5mm radial circuit & what could it be if the conductors were 4mm

20a and 32a

7, where is the max Zs for a BS60898 32amp type B found in 7671 page 49

8, Explain how you would undertake the ring final continuity test.

low ohm meter test L1 to L2, then N1 N2 then E1 to E2 L and N should be about the same, E should be (on 2.5 t&e) 1.67 times greater
link L1 N2 and L2 to N1 and go round every socket reading should be the same, if higher could be a spur if lot lower could be a cross connect?
link L1 to E2 and L2 to E1 (R1 + R2) again go round every socket, recording highest reading?


9, What csa of MEC would be used on TNC-s system

16mm unsure on this half size of line?

10, Which result would you use on cert after undertaking PSCC & PFC.

the highest

11, Why are the max Zs values different in the osg & 7671.

cos they typed it wrong? dont know this one either!
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #5 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: Questions asked on your testing assessment

Isn't it because the regs book has the maximum Zs vaule permitted, and the OSG has the "Rule of thumb" values - IE 75% of maximum?

Had me thinking too!
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #6 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Questions asked on your testing assessment

Quote:
Originally Posted by greekislandlover View Post
Isn't it because the regs book has the maximum Zs vaule permitted, and the OSG has the "Rule of thumb" values - IE 75% of maximum?

Had me thinking too!
Correct
& if the assessor asks why are they corrected to 75% in the osg, it's to account for the temperature of the conductors when under test/use as opposed to the osg being a cold (for want of a better word) value.
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #7 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 622
View sparkyork's Photo Album
Default Re: Questions asked on your testing assessment

R1 + R2 on say a loop in celing rose circuit, link between cpc and line at consumer then go to end of circuit and test there on low ohm scale?

polarity, go to every socket, switch ceiling rose and test line to earth, when energized

anyone on who can say if this is right! been thinking in me sleep aswell!

rich
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #8 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Questions asked on your testing assessment

Quote:
polarity, go to every socket, switch ceiling rose and test line to earth, when energized
No No No
Polarity is prooved as a dead test.
On sockets it's prooved during the Ring cont test
On lighting it's prooved while undertaking the R1+R2 method of continuity.

Quote:
R1 + R2 on say a loop in celing rose circuit, link between cpc and line at consumer then go to end of circuit and test there on low ohm scale?
Yes (make sure you isolate the whole cu)

Quote:
3, What is the max time for a BS EN61008 at x1
Watch out for the wording on this question. He could ask what the max time for a BS 61008 at x1 is.

Last edited by EasyFox; 22-08-2008 at 09:24 AM. Reason: Automerged Doublepost
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #9 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Thumbs up Re: Questions asked on your testing assessment

Quote:
Originally Posted by EasyFox View Post
No No No
Polarity is prooved as a dead test.
On sockets it's prooved during the Ring cont test
On lighting it's prooved while undertaking the R1+R2 method of continuity.



Yes (make sure you isolate the whole cu)



Watch out for the wording on this question. He could ask what the max time for a BS 61008 at x1 is.

He's good isn't he?
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #10 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 622
View sparkyork's Photo Album
Default Re: Questions asked on your testing assessment

sorry bout the above questions i was just reading a book and im sure it said what it said! lol

niceic, wanted to see all proper books etc, liability and knowledge of buidling regs is important.

on testing and inspection:

1) asked if i did the work
2) remove cover and proove safe isolation etc, proove main switch isolated.
3) insulation test on cooker circuit between line and cpc at 500v, asked what voltage
what min reading etc
4) perform Ze test and what max reading is for TT, TN-s, TNCS
5) perform PSCC at consumer earth bar with main earth connected. explain which
reading you give and why this test is important (prooving Short circuit capacity is
lower than OCPD's limits)
6) End of ring test on ring main line
6) Then on Minor Job, test Zs and RCD times and explain what readings to expect
at certain ratings (1/2, 1 and 5)(o and 180) also asked if the Zs was ok and what
the maz Zs is for OCPD
7) all results were compared with test sheets
8) explain how to Do R1 + R2 on a ring final circuit and on a radial and that it also
confirms polarity (partially)

cant think of owt else

rich

sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Risk Assessment Bane General Electrical Discussion 2 28-09-2008 10:01 PM
testing for a minor major work scampy Inspection, Testing and Certification of Electrical Installations 7 29-06-2008 12:19 PM
Testing - an idiots guide stevie h General Electrical Discussion 3 13-05-2008 09:42 PM
PAT testing jobs : Opinion? LukeScotty General Electrical Discussion 3 06-11-2007 08:56 PM
lighting chain testing Preacher man General Electrical Discussion 2 12-09-2007 10:09 PM

Google Search
Google

All times are GMT +1. The time now is 11:54 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38