Old 22-08-2008   #1 (permalink)
Reg Man
Member
 
Join Date: Apr 2008
Location: Northern Ireland
Posts: 34
View Reg Man's Photo Album
Default R1+R2 Periodic nightmare

I have been carrying out a periodic inspection of an old stone barn conversion (now a single dwelling with a mezzanine floor) for rental purposes. There is no loft space at all. The ceilings are open right up to the apex of the roof. The problem I have encountered is this: measuring R1 + R2 at a light fitting I find there is no earth, although the wire is there. So I have deduced after further investigation there must be a hidden JB somewhere under the plasterboard and the earth is broken or not connected ( I have already found several earths not connected). This is of course not right BUT the cast chandalier type light fitting in question is out of reach, unless you use an extended ladder. The customer wants a cert so he may rent the place out.
How do I deal with this then without dissmantling half the barn to get an earth from somewhere else?.
Any suggestions?
Should I just mark it down as a '1 fail' and let customer make his own mind up whether he deals with it or not? I'm covered then

Reg Man is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #2 (permalink)
PAUL M
Respected Member
 
Join Date: May 2008
Posts: 505
View PAUL M's Photo Album
Default Re: R1+R2 Periodic nightmare

well if you have no earth you have no r1+r2 which means no Zs so i would note it on the cert as cat 1.if you pass it as satisfactory and something did happen who is in the firing line.?
PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-08-2008   #3 (permalink)
Carter
Senior Member
 
Carter's Avatar
 
Join Date: Aug 2008
Posts: 171
View Carter's Photo Album
Default Re: R1+R2 Periodic nightmare

If you've already found several missing cpcs then that would raise doubts about the integrity of the whole installation ie what else is lurking in the studwork. Sounds like a nightmare in the making for sure. If ever there was a case for installing singles in conduit it's these sort of high ceilinged lighting runs, if only for reasons of maintainability. Digging out a faulted twin 'n skin cable from behind his immaculate ceiling plasterboard is going to make a mess no matter how minimal the invasion. Are you being paid to fault find and undertake any remedial work? Either way your man won't be renting until it's fixed so the ball is in his court.
Carter is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-08-2008   #4 (permalink)
Reg Man
Member
 
Join Date: Apr 2008
Location: Northern Ireland
Posts: 34
View Reg Man's Photo Album
Default Re: R1+R2 Periodic nightmare

Quote:
Originally Posted by Carter View Post
If you've already found several missing cpcs then that would raise doubts about the integrity of the whole installation ie what else is lurking in the studwork. Sounds like a nightmare in the making for sure. If ever there was a case for installing singles in conduit it's these sort of high ceilinged lighting runs, if only for reasons of maintainability. Digging out a faulted twin 'n skin cable from behind his immaculate ceiling plasterboard is going to make a mess no matter how minimal the invasion. Are you being paid to fault find and undertake any remedial work? Either way your man won't be renting until it's fixed so the ball is in his court.

I have been asked to do any minor repairs of which are mainly earths not connected. Its just this one I cannot do without running a single earth along lovely exposed wooden beams to the next known good spot.
He says he will state in a 'rental contract' that no one is to attempt to go up there because of the height of fitting and he will arrange electrician. So whether I like it or not he will rent it out. What he does with the periodic and recommendations I don't know. I will leave it as a 'Cat 1 fail' of course and see what happens.
Reg Man is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-08-2008   #5 (permalink)
Carter
Senior Member
 
Carter's Avatar
 
Join Date: Aug 2008
Posts: 171
View Carter's Photo Album
Default Re: R1+R2 Periodic nightmare

Quote:
Originally Posted by Reg Man View Post
I have been asked to do any minor repairs of which are mainly earths not connected. Its just this one I cannot do without running a single earth along lovely exposed wooden beams to the next known good spot.
Hmmm I see your difficulty. Your only options are to run it surface and try to disguise it or open up 2" holes either side of the joist/rafter just enough to get a drill and fish wires/draw tape in. By judicious drilling and fishing you WILL be able to run the earth to where it needs to be. Not a decorator but am sure with a decent plasterer/decorator it could be reinstated successfully.
With exposed beams I find myself for some reason thinking of unsheathed pyro which needn't look that intrusive once the sheath has lost its just fitted glare.

Quote:
He says he will state in a 'rental contract' that no one is to attempt to go up there because of the height of fitting and he will arrange electrician.
Aha so he's invoking section 417.1 basic protection by placing out of reach. So we must assume that he is providing electrical training to all his tenants such that they can be deemed "...instructed or skilled persons..." (reg. 410.3.5)

Doubt that that would stop anyone and similarly don't think it will wash in front of a court. He can't predict the future but the regs do attempt to mitigate the consequences. What if, for whatever reason, (dispute with a future tenant maybe) he is reluctant to indulge the tenant's requests to "get the sodding lights fixed as they are tripping out the whole house!" There's nothing to stop them having a dabble. Matey boy gets a belt at the top of his double extension and ....ner-ner, ner-ner.
If he wants to play fast and loose with his accreditation then he's a 24carat twot.


Quote:
So whether I like it or not he will rent it out. What he does with the periodic and recommendations I don't know. I will leave it as a 'Cat 1 fail' of course and see what happens.
Gotta be a fail/reqs urgent attention. Nothing more that can be done if he's got that attitude short of leaving the breaker off just to make the point.
Not a landlord myself but pretty sure his fire/building & contents insurance would be compromised. There is a large body of law governing domestic lets and those which are applicable depend on whether one is a private individual letting one prop or letting agent or Reg'd social landlord etc etc yahda yahda...l don't think there's a statutory requirement to have rented property formally inspected for electrical safety at set periods (gonna double check that actually), BUT, landlords are legally required to provide a dwelling that is safe. The laws affecting them include:

* The Electrical Equipment (Safety) Regulations 1994
* The Plugs and Sockets (Safety) Regulations 1994
* The Consumer Protection Act 1987
* The Low Voltage Electrical Equipment Regulations 1989
* The General Product Safety Regulations 1994.

Without a P.I.R. how's he going to prove to a loss adjuster or jury, in the event of a fire, that his installation was IN FACT safe and wasn't the cause of the damage/fatality? Bloke's a kn0b in my opinion. Scribble the following down and wave it under his nose...

# A fine of £5,000 per item not complying
# Six month's imprisonment
# Possible manslaughter charges in the event of deaths
# The Tenant may also sue him for civil damages
# Your property insurance may (almost certainly will) be invalidated

Oh I forgot the possible additional charge of negligence if a fault is reported that he is aware of and yet refuses to repair.

If it comes to the worst case (stiff tenant electrocuted by HIS PROPERTY) then an up to date P.I.R. allows him to pursue a legitimate defence of "due diligence" his obligations having been fulfilled. Not something I'd want to flip a coin on in my opinion.

Last edited by Carter; 26-08-2008 at 05:10 PM.
Carter is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-08-2008   #6 (permalink)
Reg Man
Member
 
Join Date: Apr 2008
Location: Northern Ireland
Posts: 34
View Reg Man's Photo Album
Default Re: R1+R2 Periodic nightmare

Nice one Carter. Have taken all that on board and you are 100% right.
Its simply a fail and 'Unsatisfactory' will be on the PIR. Let you know what he says in a day or so. Cheers
Reg Man is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-08-2008   #7 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 536
View tony.towa's Photo Album
Default Re: R1+R2 Periodic nightmare

Yet again Carter you have provided a first class thread which I know I found both interesting and informative.
Many thanks.
tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-08-2008   #8 (permalink)
Carter
Senior Member
 
Carter's Avatar
 
Join Date: Aug 2008
Posts: 171
View Carter's Photo Album
Default Re: R1+R2 Periodic nightmare

Y' do what y' can.
Carter is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 27-08-2008   #9 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Default Re: R1+R2 Periodic nightmare

Phew! What a reply eh? Must admit, I found this to be the most interesting part...

Quote:
Originally Posted by Carter View Post
Bloke's a kn0b in my opinion.
*Falls on floor laughing*
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 31-08-2008   #10 (permalink)
Reg Man
Member
 
Join Date: Apr 2008
Location: Northern Ireland
Posts: 34
View Reg Man's Photo Album
Default Re: R1+R2 Periodic nightmare

Just wanted to give you a quick up date on this situation.
Have completed PIR for the property and it reads unsatisfactory because of the lack of earth on two light fittings. Customer isn't at all interested in fixing it and says its unlikely anyone will ever go near lights because of height and its worth a risk!!!!!!

Just remember, if your holidaying in Ireland at all, don't go playing with the lights!!!

Reg Man is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
17th Edition Periodic report changes Mike P Inspection, Testing and Certification of Electrical Installations 14 11-10-2008 11:41 AM
does 2392 allow periodic inspections? partp General Electrical Discussion 22 01-09-2008 09:28 AM
periodic test problem TONY JONES Inspection, Testing and Certification of Electrical Installations 4 25-08-2008 08:34 AM
periodic tests Ross Trician Inspection, Testing and Certification of Electrical Installations 3 18-04-2008 07:52 AM
periodic test ????? charlie Inspection, Testing and Certification of Electrical Installations 3 27-02-2008 11:49 PM

Google Search
Google

All times are GMT +1. The time now is 12:57 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38