Volt Drop

Discuss Volt Drop in the Inspection, Testing and Certification of Electrical Installations at Electricians Forums Discussion Boards; This is a 2391 question DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop. ...
  1. #1
    Electricians Arms Member

    Join Date
    Jul 2010
    Posts
    104
    Thanks
    22
    Thanked 6 Times in 5 Posts

    Default Volt Drop

    This is a 2391 question

    DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.

    45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)

    Apparently this is a closed exam. How can this be calculated without reference to the tables??


  2. #2
    JUD
    JUD is offline
    Electricians Arms Member JUD's Avatar
    Join Date
    Jul 2009
    Location
    East Yorkshire
    Posts
    1,259
    Thanks
    33
    Thanked 188 Times in 150 Posts

    Default Re: Volt Drop

    Quote Originally Posted by buttonmoon View Post
    This is a 2391 question

    DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.

    45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)

    Apparently this is a closed exam. How can this be calculated without reference to the tables??
    You wouldn't need reference to the tables as all info has been provided.

    To get VD the calculation would be (mΩ/m x 1.2 x 2) x Ib x L ÷ 1000:

    (1.83 x 1.2 x 2) x 45 x 80 ÷ 1000 = 15.8V (6.9%)

    You multiply the conductor resistance by 1.2 to correct it for 70°C, then multiply by 2 to include the neutral.

    Now multiply by 45A and then by 80m and divide by 1000.

    This is how the values in the VD tables are worked out (mΩ/m x 1.2 x 2 = mV/A/m). Remember that and you won't go far wrong.



    Calculation from the VD tables is mV/A/m x Ib x L ÷ 1000:

    4.4 x 45 x 80 ÷ 1000 = 15.8V (6.9%)

    This is no good as it's over 11.5V (5%)

  3. Last edited by JUD; 21-07-2010 at 09:07 PM.

    'Trying is the first step towards failure' - Homer J. Simpson

Similar Threads

  1. Volt Drop
    By Phaze-3 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 2
    Last Post: 20-07-2012, 07:18 PM
  2. 1% AC volt drop
    By hduz5 in forum Photovoltaic / Solar Panels & Green Energy Forum
    Replies: 5
    Last Post: 09-06-2012, 04:22 PM
  3. volt drop
    By gordysolar in forum Photovoltaic / Solar Panels & Green Energy Forum
    Replies: 1
    Last Post: 23-10-2011, 08:55 PM
  4. Commercial Volt Drop
    By Inteificio in forum Electrical Forum, General Electrical Forum
    Replies: 21
    Last Post: 12-10-2011, 07:15 AM
  5. Volt Drop
    By switched on in forum Electrical Forum, General Electrical Forum
    Replies: 22
    Last Post: 08-09-2011, 12:44 AM
  6. volt drop
    By blue eyes in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 3
    Last Post: 09-05-2011, 08:14 PM
  7. volt drop or not
    By shocked in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 13
    Last Post: 20-11-2010, 01:59 PM
  8. volt drop
    By Peter Woodford in forum Electrical Forum, General Electrical Forum
    Replies: 9
    Last Post: 08-04-2010, 05:35 AM
  9. Volt drop
    By ajelec10 in forum Electrical Forum, General Electrical Forum
    Replies: 3
    Last Post: 29-06-2009, 06:09 PM

Visitors found this page by searching for:

2391 question volt drop

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31