    Default Shower Off, Tile, Shower Back On - Notifiable?

    Gents,

    Just checking....isolate shower, remove for tiling, replace....no change to switch, cable and shower. Is this notifiable work or nay?

    Thanks!

  2. #2
    Member
    Join Date
    Nov 2010
    Posts
    83
    Thanks
    11
    Thanked 12 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    Not, but would issue a minor works.

  3. #3
    Member
    Join Date
    Jan 2011
    Posts
    12
    Thanks
    1
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    i fort all work done it a bathroom and kitchen needs part p

  4. #4
    Electricians Arms Member steamboatwilly's Avatar
    Join Date
    Jun 2009
    Location
    Cornwall
    Posts
    348
    Thanks
    10
    Thanked 13 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    Quote Originally Posted by kiggie89 View Post
    i fort all work done it a bathroom and kitchen needs part p
    Yes, as a special location I'd agree. However, with simply removing and replacing a shower does that constitute 'work'? I have tested, of course, just trying to avoid paperwork if possible.

  5. #5
    Electricians Arms Member
    IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,578
    Thanks
    88
    Thanked 1,198 Times
    in 883 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    NICEIC advice:


    High risk locations
    Kitchens, bathrooms and gardens are classed as ‘special locations’ because the risk of electric shock is greater. Unless you are only replacing accessories, work in a kitchen, bathroom, garden or outbuilding must either be undertaken by a registered electrician or notified to building control.

    Now is a shower an accessory?


  6. #6
    Guest123
    Guest

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    Quote Originally Posted by IQ Electrical View Post
    NICEIC advice:


    High risk locations
    Kitchens, bathrooms and gardens are classed as ‘special locations’ because the risk of electric shock is greater. Unless you are only replacing accessories, work in a kitchen, bathroom, garden or outbuilding must either be undertaken by a registered electrician or notified to building control.



    Are you even replacing it because it's the same unit going back.........

  7. #7
    GT1
    GT1 is offline
    Electricians Arms Member
    Join Date
    Aug 2008
    Posts
    553
    Thanks
    3
    Thanked 24 Times
    in 24 Posts
    Tagged
    0 Thread(s)

    Default

    Part P isn't applicable if replacing like for like.
    Seeing as it's the same shower, it's EXACTLY like for like. !!

  8. #8
    Member
    Join Date
    Jan 2011
    Posts
    12
    Thanks
    1
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    even if its a minor works all work in a kitchen or bathroom needs part p
    i know its big pain but am i right? plz let me know some one

  9. #9
    Electricians Arms Member steamboatwilly's Avatar
    Join Date
    Jun 2009
    Location
    Cornwall
    Posts
    348
    Thanks
    10
    Thanked 13 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    Quote Originally Posted by kiggie89 View Post
    even if its a minor works all work in a kitchen or bathroom needs part p
    i know its big pain but am i right? plz let me know some one
    Hi kiggie....no, not quite. Lots of work in special locations is not notifiable according to the NICEIC...see their PDF download at http://niceic.com/Uploads/File1247.pdf

  10. The Following User Says Thank You to steamboatwilly For This Useful Post:

    kiggie89 (06-01-2011)

  11. #10
    Member
    Join Date
    Jan 2011
    Posts
    12
    Thanks
    1
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    thanks pal

  12. #11
    Electricians Arms Member steamboatwilly's Avatar
    Join Date
    Jun 2009
    Location
    Cornwall
    Posts
    348
    Thanks
    10
    Thanked 13 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    Quote Originally Posted by Lenny View Post
    Are you even replacing it because it's the same unit going back.........
    This is the key point I think....same cable, same route, same shower, same switch....

  13. #12
    Electricians Arms Member steamboatwilly's Avatar
    Join Date
    Jun 2009
    Location
    Cornwall
    Posts
    348
    Thanks
    10
    Thanked 13 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Shower Off, Tile, Shower Back On - Notifiable?

    It's difficult to find any DIRECT answers to this issue but the following from the ODPM seems to be clear at last:

    Is the replacement electric shower or shower pump in a bathroom notifiable?
    Answer: No despite the increased risk of electrical shock to persons in bathrooms and shower rooms, the ODPM does not consider such replacement work to be notifiable, unless it is not on a like for like basis or it involves the provision of a new circuit (such as to cope with an increased power rating). You are however advised due to this higher risk of electrocution to employ only competent electricians to undertake this work for you.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Shower light on and Switch light on when shower pull cord is off
    By sparky1966 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 7
    Last Post: 26-01-2013, 04:40 PM
  2. Domestic aqualisa quartz digital thermostatic exposed shower - notifiable?
    By Murdoch in forum Electrical Forum: General Electrical Forum
    Replies: 1
    Last Post: 19-04-2011, 08:48 AM
  3. Replacing a shower like for like is it part p notifiable
    By geordie in forum Electrical Forum: General Electrical Forum
    Replies: 3
    Last Post: 25-01-2011, 03:25 PM
  4. Disconecting shower to re-tile
    By oldstudent in forum Electrical Forum: General Electrical Forum
    Replies: 11
    Last Post: 05-11-2010, 09:38 PM
  5. Shower fan running off shower supply.
    By Amp David in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 13
    Last Post: 04-11-2009, 12:03 AM

Visitors found this page by searching for:

is installing shower pump notifiable

is replacing an electric shower notifiable

shower pump electrics notifiable

aqualisa quartz digital electric shock

aqualisa digital shower notifying building control