Old 22-06-2009   #31 (permalink)
kung
Respected Member
 
kung's Avatar
 

Join Date: Jan 2009
Location: Whitley/Reading/Berkshire.
Posts: 1,491
Thanks: 350
Thanked 149 Times in 136 Posts
Default Re: Distributors cut out fuse

If anyone does notify DNO then you may not be charged anyway so worth finding out ! if however you do get charged get the guys mobile number or home number as 99% will do this for you every time you need it done for a few beers or fags etc as Tesco say every little helps !
__________________
NURSE HE'S OUT OF BED AGAIN !
kung is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-06-2009   #32 (permalink)
platty1005
Junior Member
 

Join Date: Jun 2009
Location: St Helens Lancs
Posts: 17
Thanks: 2
Thanked 4 Times in 4 Posts
Default Re: Distributors cut out fuse

How can you be sure what fuse is inside the carrier if you do not remove it and look inside. It could be a 6 inch nail or piece of 16mm copper fitted previously by the 10 gallon hat and six shooter fraternity.

If you remove the fuse and it is OK the info you require is written on the side of the fuse BE EXTREMELY CAREFUL WHEN REMOVING SERVICE FUSE

If it is a nail or other unsafe item then ring your local Electricity supplier who owns that piece of equipment and explain that you have found an unsafe situation that requires urgent attention. An engineer should arrive soon to remedy the problem probably by fitting the correct type of fuse. so just ask them what they have put in.

PS there should be no cost for this service it is their equipment up to and including the meter

Last edited by platty1005; 23-06-2009 at 11:22 AM..
platty1005 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-07-2009   #33 (permalink)
rob1967
Member
 

Join Date: Aug 2008
Location: newcastle under lyme
Posts: 41
Thanks: 1
Thanked 4 Times in 4 Posts
Default Re: Distributors cut out fuse

I ask this same question here a few months ago weather or not I could pull the cut out fuse and most of the answers I got was no...
rob1967 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-07-2009   #34 (permalink)
darkwood
Respected Member
 

Join Date: Jun 2009
Location: Bradford area
Posts: 631
Thanks: 7
Thanked 109 Times in 103 Posts
Default Re: Distributors cut out fuse

Quote:
Originally Posted by platty1005 View Post
How can you be sure what fuse is inside the carrier if you do not remove it and look inside. It could be a 6 inch nail or piece of 16mm copper fitted previously by the 10 gallon hat and six shooter fraternity.

If you remove the fuse and it is OK the info you require is written on the side of the fuse BE EXTREMELY CAREFUL WHEN REMOVING SERVICE FUSE

If it is a nail or other unsafe item then ring your local Electricity supplier who owns that piece of equipment and explain that you have found an unsafe situation that requires urgent attention. An engineer should arrive soon to remedy the problem probably by fitting the correct type of fuse. so just ask them what they have put in.

PS there should be no cost for this service it is their equipment up to and including the meter
It is still illegal to remove the cutout fuse for any other reason except to remove an immediate hazard or danger so again i say No! you cant remove it to check the type and rating etc, you must ring the supplier and request this info and i agree they may drag their heels abit but they are legally bound to supply you this info for free. If their is a nail in it its not your responsibilty to check or find out its the suppliers job.
Having said all this i dont know a sparky that dosnt check it themselves im just telling it from a legal point of view.
darkwood is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-07-2009   #35 (permalink)
andekoch
Senior Member
 

Join Date: Apr 2009
Location: south croydon
Posts: 197
Thanks: 1
Thanked 20 Times in 19 Posts
Default Re: Distributors cut out fuse

I agree with all of the above. The official line is we can't remove the main fuse or tamper with it.
On the cert fill in what you can see, if you can't determine the capacity or type of the fuse just say so.
Normally if the house holder calls the elec co and askes them to remove the fuse for their sparky there is no charge to the house owner (also saves you half a day on the phone and a big phone bill).

If however there is some good reason for you to remove it make sure that there is no load on it so switch off all mcb's and the main switch.
andekoch is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-07-2009   #36 (permalink)
SirKit Breaker
Senior Member
 

Join Date: Jul 2009
Location: Leeds, Gods County of Yorkshire
Posts: 324
Thanks: 4
Thanked 64 Times in 60 Posts
Default Re: Distributors cut out fuse

I stopped dabbling with these cutout fuses because an Electician got killed removing one, he got hold of the carrier and it crumbled in his hand he finished up with a handful of live bits and didnt live to tell the tale.

I just disconnect at the meter with it live. Not ideal i know, and if i cant do that then its on the phone to get it sorted.

My preffered route is to ring supplier on behalf of the customer and get them to fit an isolator prior to me doing the job, its only about £40 and i include it in cost of rewire so that the customer doesnt see the expense.

Cheers...............Howard
__________________
GREAT BRITAIN...LOVE IT OR LEAVE IT
SirKit Breaker is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-07-2009   #37 (permalink)
saveloy
Senior Member
 

Join Date: Sep 2008
Posts: 289
Thanks: 19
Thanked 56 Times in 41 Posts
Default Re: Distributors cut out fuse

I work in the Scottish and Southern DNO area. If you are registered with the following trade associations,
NICEIC, ECA, NAPIT or SELECT then they have a policy that allows contractors to remove the cutout fuse for routine maintenance work.
You must inform SSE that you have removed the fuse and when finished reseal it with a temporary label obtained from their stores. They will then send someone out to fit a new seal.

Info here: (PDF download at top of page) Removal Of Fuses
saveloy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2009   #38 (permalink)
pjb1
Junior Member
 

Join Date: Jun 2009
Posts: 24
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Distributors cut out fuse

The EWR states it is illegal to work live,Unless the situation can not be avoid.So surely the DNO is treading on very stony ground stopping you.
pjb1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-07-2009   #39 (permalink)
Jason.S
Super Moderator
 
Jason.S's Avatar
 

Join Date: Mar 2008
Location: In MY world.
Posts: 4,374
Thanks: 151
Thanked 525 Times in 473 Posts
Default Re: Distributors cut out fuse

Quote:
Originally Posted by saveloy View Post
They will then send someone out to fit a new seal.
I work in their area and i bet that havent done one of mine yet.
__________________
Whatever happens, don't blame me.
--------------------------------------------------------------------------------------
All opinions expressed by myself, are not necessarily those of Electricians Forums.
Jason.S is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-07-2009   #40 (permalink)
saveloy
Senior Member
 

Join Date: Sep 2008
Posts: 289
Thanks: 19
Thanked 56 Times in 41 Posts
Default Re: Distributors cut out fuse

Got my copy of Switched On magazine today from the Electrical Safety Council. There is an article that outlines the problem contractors face, with regard to removal of distributors cutout, in order for work to be carried out safely

In short the ESC along with NICEIC, the ECA and other contracting bodies have been campaigning for the situation to be improved in the interest of safety. ESC are reporting that the concerns are being addressed by DCUSA. DCUSA is a multi party contract between all licsensed distributors, suppliers and generators in GB.

DCUSA has set up a working group to find out what practices are happening and why. They have issued a consultation document to gather information from the relavent interested parties.

In the ESC magazine they say they are hoping for a UK wide scheme to be introduced, that will allow contractors NOT employed by distribution companies, to remove domestic fuses for work to be carried out safely.

It does appear that at long last this issue is to be addressed. May take some time though.
saveloy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
The Following User Says Thank You to saveloy For This Useful Post:
electricAl (05-07-2009)
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Earthing and fuse question.... Dazzac Electrical Forum | General Electrical Forum 7 18-10-2009 03:37 PM
Useful information amberleaf Electrical Courses & Electrical NVQ's 10 29-05-2009 06:31 PM
Trying to identify distributors fuse ktech Electrical Forum | General Electrical Forum 5 29-03-2009 03:30 PM
blue fuse 15A fuse pushrod Electrical Forum | General Electrical Forum 8 20-12-2008 09:20 PM
To cut or Not to cut, that is the question. spark-doctor Electrical Forum | General Electrical Forum 4 07-09-2008 03:44 PM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK