New Consumer Unit - No main Earth to Gas - How to Report

Discuss New Consumer Unit - No main Earth to Gas - How to Report in the Inspection, Testing and Certification of Electrical Installations at Electricians Forums Discussion Boards; Hi guys Dont know whether this should be here or in general but I'm sure mods will move it. Friend of mine has numerous flats. He asked me to do ...
  1. #1
    Electricians Arms Member
    Join Date
    Jul 2008
    Location
    Preston - Lancs
    Posts
    117
    Thanks
    3
    Thanked 1 Time in 1 Post

    Default New Consumer Unit - No main Earth to Gas - How to Report

    Hi guys

    Dont know whether this should be here or in general but I'm sure mods will move it.

    Friend of mine has numerous flats. He asked me to do a consumer unit change at one of them and make sure it was electrically safe.
    I did a mini PIR, IR on all cabling R1 & R2 and checked all was good with the exception of the main earth to gas.
    This was a 4mm buried in the fabric of the building going to what I would describe as an out house. The gas is capped off just above the meter. No earth clamp, but continuity shows that the cable next to meter is the 4mm in the C/U area.

    As there is no gas in the flat I made a note on the PIR. The landlord also expressed that he did not want the fabric of the building destroyed to put a new 10mm in. (It can be done, but would be messy and I would have to conduit it around 2 walls of the flat.

    Then came the curve ball.

    When he gets tennants, they can apply for a grant to get a new boiler. So in the near future, the gas may be recommisioned.

    So after all that, what is best to cover myself.

    Do I remove the 4mm so it cannot be used by boiler fitters.
    Do I convince the landlord to put the 10mm in now.
    Or will the boiler fitters be responsible to upgrade the 4mm to 10mm.

    I am back next week to commision and PIR, so will the note in my observations be adequate for what may happen in the future.

    Thanks for your help

    DaveR


  2. #2
    Electricians Forums Member
    Join Date
    Jan 2010
    Location
    SW London
    Posts
    85
    Thanks
    20
    Thanked 4 Times in 4 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    If you are upgrading consumer unit, I would say the main earth, tails and earth bonding should be updated to suit, after all, you are altering the whole installation and it should be brought up to current regs.
    I would insist that the bonding to gas be in place for future use, being that looks possible so soon.
    Just my opinion.
    Rik


  3. #3
    Band Member
    paul.m's Avatar
    Join Date
    Aug 2010
    Location
    In a toolbox
    Posts
    4,947
    Thanks
    1,113
    Thanked 862 Times in 690 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    At present time the gas doesn't need bonding so you could leave it as it is.

    If the new tenants get a boiler installed then the company fitting it has to bond it before signing it off. Will your friend the landlord be happy where they put the 10mm? I doubt it.

  4. #4
    Electricians Arms Member
    Join Date
    Jul 2008
    Location
    Preston - Lancs
    Posts
    117
    Thanks
    3
    Thanked 1 Time in 1 Post

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Thanks guys, as usual a speedy response.

    I have changed tails, main earth and new 10mm to water. I think for the hassle, I will put new 10mm to gas and clamp in some fashion to the blanking cap that is to meter. At least I can then leave it and not have to rely on the gas fitters to put it in or utilise the 4mm that is already there.

    Thanks everyone.

    DaveR
    SirKit Breaker likes this.

  5. #5
    Electricians Arms Member IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,555
    Thanks
    89
    Thanked 1,191 Times in 883 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Quote Originally Posted by daver View Post
    Hi guys

    Dont know whether this should be here or in general but I'm sure mods will move it.

    Friend of mine has numerous flats. He asked me to do a consumer unit change at one of them and make sure it was electrically safe.
    I did a mini PIR, IR on all cabling R1 & R2 and checked all was good with the exception of the main earth to gas.
    This was a 4mm buried in the fabric of the building going to what I would describe as an out house. The gas is capped off just above the meter. No earth clamp, but continuity shows that the cable next to meter is the 4mm in the C/U area.

    As there is no gas in the flat I made a note on the PIR. The landlord also expressed that he did not want the fabric of the building destroyed to put a new 10mm in. (It can be done, but would be messy and I would have to conduit it around 2 walls of the flat.

    Then came the curve ball.

    When he gets tennants, they can apply for a grant to get a new boiler. So in the near future, the gas may be recommisioned.

    So after all that, what is best to cover myself.

    Do I remove the 4mm so it cannot be used by boiler fitters.
    Do I convince the landlord to put the 10mm in now.
    Or will the boiler fitters be responsible to upgrade the 4mm to 10mm.

    I am back next week to commision and PIR, so will the note in my observations be adequate for what may happen in the future.

    Thanks for your help

    DaveR
    If there is no electrical supply to this 'outhouse' then the gas service should be bonded within 600mm of the entry to the house/flat.
    Do it once, do it right....

    Fixed Wire Testing
    www.iqelectrical.co

  6. #6
    Band Member
    paul.m's Avatar
    Join Date
    Aug 2010
    Location
    In a toolbox
    Posts
    4,947
    Thanks
    1,113
    Thanked 862 Times in 690 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Quote Originally Posted by IQ Electrical View Post
    If there is no electrical supply to this 'outhouse' then the gas service should be bonded within 600mm of the entry to the house/flat.
    Even if the meter in the outhouse is capped off and no gas supply to the flat? Please correct me if my post above is wrong.

  7. #7
    Electricians Arms Member IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,555
    Thanks
    89
    Thanked 1,191 Times in 883 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Quote Originally Posted by paul.m View Post
    Even if the meter in the outhouse is capped off and no gas supply to the flat? Please correct me if my post above is wrong.
    Your post is spot on Paul, I should have said 'when the supply is recommissioned'
    Do it once, do it right....

    Fixed Wire Testing
    www.iqelectrical.co

  8. The Following User Says Thank You to IQ Electrical For This Useful Post:

    paul.m (28-04-2011)

  9. #8
    Band Member
    paul.m's Avatar
    Join Date
    Aug 2010
    Location
    In a toolbox
    Posts
    4,947
    Thanks
    1,113
    Thanked 862 Times in 690 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Thanks IQ, I confused myself for a moment then .

  10. #9
    Forum Admin JASON's Avatar
    Join Date
    Mar 2008
    Location
    Button Pressing
    Posts
    8,132
    Thanks
    940
    Thanked 921 Times in 662 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Just to put the boot in, you will probably find that even if you did bond the stub thats left, the plumbers will rip it off to connect to the meter and not bother re connecting it.

    And i think it may be our responsibility to ensure the bonding is in place and not the plumbers.

    All that will happen is, if the bond is not there, they wont commission the gas installation.
    Spark & A Half.


    Please Read The Electricians Forums Rules Here:
    http://www.electriciansforums.co.uk/...5-10-08-a.html





    <<<<If a member has assisted, please show your appreciation with the "THANKS" button!!!

  11. #10
    Electricians Arms Member Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    7,295
    Thanks
    386
    Thanked 694 Times in 643 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    "As there is no gas in the flat I made a note on the PIR. "

    Common sense suggests that you also make a note on the EIC and then you're covered. If theres no gas boiler present why alienate your friend and insist that the 10mm bonding be installed if its not required.

    Any new installation of a boiler, by a competent person, will ensure that the 10mm bonding be installed at the same time.

    Maybe I'm wrong.

    Tin hat on!

  12. #11
    Electricians Arms Member
    Join Date
    Jul 2008
    Location
    Preston - Lancs
    Posts
    117
    Thanks
    3
    Thanked 1 Time in 1 Post

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Sorry guys, I think I may have introduced a little confussion. It is a really weird build. But to explain the outhouse. It has access directly from the kitchen, but where as the flats are double brick, this is single brick and about 3 foot square. Its like a cool larder. The meter is in here. As the main build is 3 story, it would be impossible to feed in ceilings without popping holes everywhere. Theres 2 steps in kitchen so to run at low level in kitchen would look horrendous. My option if a little messy, is to go out of back of electrical cupboard, under bath to outside walls and then conduit around 2 walls and into the out house section.

    I know I will have to connect within 600mm, so will connect to blanking plug for now and await the boiler being fitted and then make a final visit to check.

    It may not happen at all, the previous tennant lasted for 5 years with only 2 storage heaters.

    Thanks anyway
    brucelee likes this.

  13. #12
    Electricians Arms Member pushrod's Avatar
    Join Date
    Sep 2008
    Location
    leicestershire
    Posts
    2,340
    Thanks
    89
    Thanked 368 Times in 313 Posts

    Default Re: New Consumer Unit - No main Earth to Gas - How to Report

    Quote Originally Posted by Murdoch View Post
    "As there is no gas in the flat I made a note on the PIR. "

    Common sense suggests that you also make a note on the EIC and then you're covered. If theres no gas boiler present why alienate your friend and insist that the 10mm bonding be installed if its not required.

    Any new installation of a boiler, by a competent person, will ensure that the 10mm bonding be installed at the same time.

    Maybe I'm wrong.

    Tin hat on!

    That would be my take on it as well.

    The only thing that would make me feel otherwise would be if there was any simultaneously accessible exposed-conductive-part or other extraneous-conductive-part. Then i would resistance test between the gas main and them and if it was >1667Ω i would supplementary bond

    The capped gas main is still an extraneous-conductive-part in the way that a metallic waste pipe is.
    Every day's a oops i mean learning day!

Similar Threads

  1. Consumer unit length from main cut out
    By currie123 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 4
    Last Post: 29-05-2012, 09:04 PM
  2. Domestic no earth to consumer unit? photos
    By Notaclue in forum Electrical Forum, General Electrical Forum
    Replies: 50
    Last Post: 11-05-2012, 11:17 PM
  3. Domestic No main earth to consumer unit!
    By Notaclue in forum Electrical Forum, General Electrical Forum
    Replies: 10
    Last Post: 02-04-2012, 08:06 PM
  4. Electrical Installation Condition report on a small flat - 2 way Consumer Unit.
    By 1shortcircuit in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 0
    Last Post: 14-02-2012, 07:34 PM
  5. consumer unit change with undersized main bonding.
    By payney 0 in forum Electrical Forum, General Electrical Forum
    Replies: 16
    Last Post: 21-01-2012, 06:47 PM
  6. 100 Main Switch (consumer unit)
    By j.capes in forum Electrical Forum, General Electrical Forum
    Replies: 7
    Last Post: 21-04-2011, 06:50 PM
  7. Adding a second consumer unit off the main switch
    By DomB in forum Electrical Forum, General Electrical Forum
    Replies: 8
    Last Post: 24-02-2011, 06:23 PM
  8. Domestic feeding off main consumer unit
    By voltage in forum Electrical Forum, General Electrical Forum
    Replies: 8
    Last Post: 28-10-2010, 10:11 AM
  9. Consumer unit near gas main...
    By screech in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 3
    Last Post: 31-05-2010, 03:43 PM
  10. Suggest a forum category
    By Dan in forum Electrical Forum News, Updates and Suggestions
    Replies: 18
    Last Post: 18-02-2008, 04:27 PM

Visitors found this page by searching for:

how to earth gas main

how to earth a new consumer unit

ireland earth bonding new boiler

no earth bonding can consumer unit be changed

earth bonding to gas meter explained

consumer unit earthing

new consumer unit no bonding

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31