Discuss Main protective bonding and supplementary bonding, help please! in the Inspection, Testing and Certification of Electrical Installations at Tilers Forum; Have a query regarding bonding for periodic. 1, Main protective bond for gas supply goes to the supply box outside the house, is this ok as would be difficult to ...
  1. #1
    Member
    Join Date
    May 2011
    Location
    West Midlands
    Posts
    32
    Thanks
    7
    Thanked 0 Times
    in 0 Posts

    Default Main protective bonding and supplementary bonding, help please!

    Have a query regarding bonding for periodic.

    1, Main protective bond for gas supply goes to the supply box outside the house, is this ok as would be difficult to connect it in the house close to the supply as it goes under the floor. If it is a problem what code ?

    2, supplementary bonding below boiler 10mm (4 pipes all connected 10mm looks very neat with labels) but then goes into the a fused switch that feeds the boiler, so have a tight fit 1.5mm cpc along with 10mm going into the earthing connection. Is this ok, reading of the bonding to CU is still good 0.05 ohm, is this ok ?

  2. #2
    Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    1,529
    Thanks
    15
    Thanked 63 Times
    in 56 Posts

    Default

    bonding as close to the stop tap is the preferred method, so in the meter box outside is very common

  3. #3
    AWD
    AWD is offline
    Member
    Join Date
    Apr 2011
    Location
    Liverpool
    Posts
    35
    Thanks
    1
    Thanked 2 Times
    in 2 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    the boiler does not have 2 be bonded so i would not worry about it as long as the water and gas are!,

  4. #4
    Member
    IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,573
    Thanks
    88
    Thanked 1,195 Times
    in 882 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    Quote Originally Posted by Gazap View Post
    Have a query regarding bonding for periodic.

    1, Main protective bond for gas supply goes to the supply box outside the house, is this ok as would be difficult to connect it in the house close to the supply as it goes under the floor. If it is a problem what code ?

    2, supplementary bonding below boiler 10mm (4 pipes all connected 10mm looks very neat with labels) but then goes into the a fused switch that feeds the boiler, so have a tight fit 1.5mm cpc along with 10mm going into the earthing connection. Is this ok, reading of the bonding to CU is still good 0.05 ohm, is this ok ?
    1 You have within 600mm to make the connection but ideally, this should be done as close as practicable to the point of entry to the property (ie. the equipotential zone that you are creating).

    2 Supplementary bonding at boiler positions is not a requirement of BS 7671:2008, you need to brush up on earthing and bonding regulations if you are carrying out periodic inspections.
    Last edited by IQ Electrical; 11-05-2011 at 11:20 PM.
    tony mc likes this.

  5. #5
    Member
    Join Date
    May 2011
    Location
    West Midlands
    Posts
    32
    Thanks
    7
    Thanked 0 Times
    in 0 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    Quote Originally Posted by AWD View Post
    the boiler does not have 2 be bonded so i would not worry about it as long as the water and gas are!,
    yes realise its ok not to have it, but thought a strange way of connecting, and does it affect the switch regarding code

  6. #6
    AWD
    AWD is offline
    Member
    Join Date
    Apr 2011
    Location
    Liverpool
    Posts
    35
    Thanks
    1
    Thanked 2 Times
    in 2 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    i dont understand why you would come a fcu with a 10mm!, you want 2 make sure that the 10mm from the boiler is not the fcu means of earth i have come across that before

  7. #7
    AWD
    AWD is offline
    Member
    Join Date
    Apr 2011
    Location
    Liverpool
    Posts
    35
    Thanks
    1
    Thanked 2 Times
    in 2 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    come of """ a fcu

  8. #8
    Member
    Join Date
    May 2011
    Location
    West Midlands
    Posts
    32
    Thanks
    7
    Thanked 0 Times
    in 0 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    the fcu had its own 1.5mm cpc , but the 10mm was added from the bonding from the boiler

  9. #9
    Member
    Join Date
    May 2011
    Location
    West Midlands
    Posts
    32
    Thanks
    7
    Thanked 0 Times
    in 0 Posts

    Default Re: Main protective bonding and supplementary bonding, help please!

    thanks for your help guys

Similar Threads

  1. main protective bonding.... supplementry bonding
    By i=p/u in forum Electrical Forum: General Electrical Forum
    Replies: 18
    Last Post: 22-05-2012, 09:50 PM
  2. 30 metre run of Main Protective Bonding Conductor to Gas Main and Water Main
    By Les Macaulay in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 22
    Last Post: 18-10-2011, 08:38 AM
  3. Main protective bonding
    By Luminous in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 17
    Last Post: 26-05-2011, 07:55 AM
  4. Domestic Main protective bonding
    By waynelester in forum Electrical Forum: General Electrical Forum
    Replies: 2
    Last Post: 02-09-2010, 08:15 AM
  5. Main and supplementary bonding
    By s6stu in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 6
    Last Post: 08-01-2008, 05:50 PM

Visitors found this page by searching for:

list of requirements for inspection of the main protective bonding

requirements for inspecting supplementary bondinmg

supplementary bonding test

main protective bonding conductor test

supplementary bonding 6 mm or 10 mm

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36