Old 05-02-2008   #11 (permalink)
Martin
Junior Member
 
Join Date: Dec 2007
Posts: 5
View Martin's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

For loop testing with the Fluke, choosing L-PE will do a low current "no trip" 3 wire test. Choosing L-P will do a high current 2 wire test. For this connect the L probe to live and N to earth. Remember that the 2 wire test will trip any RCDs.
Martin is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2008   #12 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

so the Fluke IS the same as the Megger

thought it would be

also think that two lead test will be virtually redundant under the 17th, all except PFC's at the CU
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-02-2008   #13 (permalink)
alex
Senior Member
 
alex's Avatar
 
Join Date: Dec 2007
Posts: 122
View alex's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by ian.settle1 View Post
The neutral is to allow the meter to work. So why not connect the neutral to earth to allow meter to work?


couldnt agree more.
alex is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-04-2008   #14 (permalink)
Malcg
Junior Member
 
Join Date: Apr 2008
Posts: 19
View Malcg's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Hi
R1+R2 is only available at light drop / ceiling rose (also much easier to do).

Switch off main switch. Temp short MCB live to earth. at furthest rose, test using two leads (as L & E available).

Record result and remove temp link.

As shown on page 217/218 NICEIC Inspection, Testing, Certification and Reporting.

Hi

Also if you want to include switch drop, still test at ceiling rose with light switch on. Use Switch live, Neutral and earth. Then you get longest path of Live.

Last edited by Malcg; 05-05-2008 at 12:25 PM. Reason: Text error
Malcg is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 19-04-2008   #15 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by Malcg View Post
Hi
R1+R2 is only available at light drop / ceiling rose (also much easier to do).

Switch off main switch. Temp short MCB live to earth. at furthest rose, test using two or three leads (as L, N & E available).

Record result and remove temp link.

As shown on page 217/218 NICEIC Inspection, Testing, Certification and Reporting.

Hi

Also if you want to include switch drop, still test at ceiling rose with light switch on. Use Switch live, Neutral and earth. Then you get longest path of Live.
Malc,

how/why would you use three leads to test R1+R2
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-05-2008   #16 (permalink)
Malcg
Junior Member
 
Join Date: Apr 2008
Posts: 19
View Malcg's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

modified
Malcg is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-05-2008   #17 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 294
View ian.settle1's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by Shakey View Post
Malc,

how/why would you use three leads to test R1+R2
Because some meters require L + N for meter to work
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-05-2008   #18 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by ian.settle1 View Post
Because some meters require L + N for meter to work
Not testing R1+R2 they dont, you are talking about Zs surely?
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-05-2008   #19 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 294
View ian.settle1's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by Shakey View Post
Not testing R1+R2 they dont, you are talking about Zs surely?
Depends if your using a Megger (can't remember the model) as when you take the Ze reading and record it in the meter then when you take Zs at end of circuit it will calculate the R1+R2 for you when downloaded into computer.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-05-2008   #20 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

hmmmm, dont really like that Ian

R1+R2 is a resistance reading (as you know) i.e dead

Zs and Ze are impedence (live) (yes, egg sucking and all that)

We know that Zs = Ze + (R1 +R2) but adding R1+R2 to Ze does not automatically give the the same result as Zs (for many reasons which I know I dont need to explain to you!)

so taking Ze from Zs will not give an accurate R1+R2 either

Personally I would never do this, as Zs is the least preferable of the readings (due to the EAWR's)

Interesting that Megger use it though! Everyday is a school day......

my point was of course that you never MEASURE R1+R2 using three leads, what you saying is that you would measure Zs, and the meter would kick out an R1+R2 from it......... got a meeting with Megger soon, I will discuss it with them!


Last edited by Shakey; 06-05-2008 at 05:15 PM.
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
lighting snatch Commercial and Industrial Electrical 9 19-04-2008 04:12 PM
lighting chain testing Preacher man General Electrical Discussion 2 12-09-2007 10:09 PM

Google Search
Google

All times are GMT +1. The time now is 05:54 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Personal Loans : Loans : Song Lyrics : MPAA : Compare

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32