Old 06-05-2008   #21 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 444
View ian.settle1's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Shakey

It was a Megger LCB2500/2 meter but never used it that way. Took Ze & Zs readings as normal along with R1+R2 by continuity meter.
ian.settle1 is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-05-2008   #22 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,213
View Shakey's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by ian.settle1 View Post
Shakey

It was a Megger LCB2500/2 meter but never used it that way. Took Ze & Zs readings as normal along with R1+R2 by continuity meter.
Glad to hear it Ian, I would expect nothing less from you

good example to throw into my students though....

cheers
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #23 (permalink)
alancp
Junior Member
 
Join Date: Jun 2008
Posts: 14
View alancp's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

stop me if i am wrong but the certs ask for the MAX efli for that circuit, so if we have a pendant (end of line) at the top of stairs, and is 2 way switched, then obviously the max reading would be at the remote switch.
alancp is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #24 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,213
View Shakey's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Quote:
Originally Posted by alancp View Post
stop me if i am wrong but the certs ask for the MAX efli for that circuit, so if we have a pendant (end of line) at the top of stairs, and is 2 way switched, then obviously the max reading would be at the remote switch.
if its done 3 plating at the pendant, then thats where the max Zs would be
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #25 (permalink)
johnosman
Junior Member
 
Join Date: Dec 2007
Location: Southampton
Posts: 6
View johnosman's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

I would love to know what the megger rep says as some of the sparks I work with have been told that that particular test instrument does give you an r1+r2 reading. I have never used this reading myself as you are never asked to submit a ze reading that the machine can deduct the zs from ze to give you r1+r2 so as far as I can see it would be impossable for a tester to give a reading even if it was just deducting ze from zs. I probably have'nt explained it very well but according to the rep just by doing a test for zs the tester will give an r1+r2 just by doing this one test and nothing else.


johnosman is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
lighting snatch Commercial and Industrial Electrical 9 19-04-2008 04:12 PM
lighting chain testing Preacher man General Electrical Discussion 2 12-09-2007 10:09 PM

Google Search
Google

All times are GMT +1. The time now is 07:53 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Personal Loan : School Girl Costumes : Web Advertising : MPAA : Loans

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33