Old 03-02-2008   #1 (permalink)
DanBrown
Member
 
Join Date: Dec 2007
Posts: 33
View DanBrown's Photo Album
Default Testing Zs at Lighting switch's with no neutral

Could anyone just give me a bit of advice regarding a Zs test at a light switch, as the tester i have just baught is the ''Fluke 1653'' tester and it uses a 3 wire test earth, live, neutral to aquire the Zs.

Am i right in saying that you have to do it manually by shorting live / earth at C/U and do a ohms check then add this to your Ze test?.

Your thaughts would be appreciated, Thanks


Last edited by DanBrown; 04-02-2008 at 10:52 AM.
DanBrown is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2008   #2 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 275
View ian.settle1's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

The neutral is to allow the meter to work. So why not connect the neutral to earth to allow meter to work?
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2008   #3 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Dan

connect line (used to be called phase) to earth bar at the cu (supply isolated obviuosly!)

and measure between line and cpc at the light switch on low resistance ohms. This is your (R1+R2) value, and when added to the Ze is your ZS. Its very unlikely this will be recorded on your schedule of test results, as the highest Zs value should be a the switched live conductor on the last light in the circuit.

If you measure Zs at the switch, you are (in theory) contravening the Electricity at Work Regulations
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2008   #4 (permalink)
DanBrown
Member
 
Join Date: Dec 2007
Posts: 33
View DanBrown's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

In response to your anwer ian.
What do you actually mean by saying put neutral to earth to make the tester work.
Thanks anyway

Last edited by DanBrown; 03-02-2008 at 07:39 PM. Reason: incorrect
DanBrown is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2008   #5 (permalink)
EasyFox
Senior Member
 
EasyFox's Avatar
 
Join Date: Sep 2007
Posts: 354
View EasyFox's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

He means put the meters blue & green leads to the cpc at the light switch.
But why do the Zs at a switch?
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2008   #6 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

I agree with Easyfox

i would just confirm R2 at the light switch, and do my Zs at the ceiling rose (calaculated from the (R1+R2) value

Dan, i use a Megger. If we are on 'no trip loop' we use three leads, and normal earth fault loop is two leads (which connect to line and cpc). Cant recall how the Fluke carries out the Zs or Ze test, but do you have a two or three lead option? it wont be called 'no trip loop' but somenthing similar
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2008   #7 (permalink)
DanBrown
Member
 
Join Date: Dec 2007
Posts: 33
View DanBrown's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Hi Guys,
Thanks for all your responses, The only reason i asked about testing at a light switch is to double check and make sure that the maximum Zs i recorded was actually the maximum Zs, seem s a bit stupid on my behalf but im kinda new to testing my work off. I am aware that with the theory and the actual Zs should be at the furthest part of the circuit as this has the highest resistance reading. Just wanted to 100% check and make sure my reading's were correct.

In response to you previous question tony, the tester uses 3 wire only, and it has ''non trip'', when you dis-connect the neutral lead from the tester it says ''lead''. You must be right in saying put neutral + earth leads onto earth terminal and live to live. I'll give it a try....

Thanks Guys
DanBrown is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2008   #8 (permalink)
alan
Junior Member
 
Join Date: Jan 2008
Posts: 23
View alan's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

All the leads in rotary sw to Z Tester should be on L-PE

At light put green crock to earth, blue to neutral and then red to phase.
alan is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2008   #9 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

Alan,

but that was his original problem, he's at a light switch so doesnt have a neutral!!!!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2008   #10 (permalink)
alan
Junior Member
 
Join Date: Jan 2008
Posts: 23
View alan's Photo Album
Default Re: Testing Zs at Lighting switch's with no neutral

He tests at the light fitting, if there no neutral there ,patient the idea

alan is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
lighting snatch Commercial and Industrial Electrical 9 19-04-2008 04:12 PM
lighting chain testing Preacher man General Electrical Discussion 2 12-09-2007 10:09 PM

Google Search
Google

All times are GMT +1. The time now is 06:04 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Hotel Las Vegas : Loans : Mortgage : Online Advertising : Loans

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29