Excess bare live conductor at terminations - code?

Discuss Excess bare live conductor at terminations - code? in the Inspection, Testing and Certification of Electrical Installations at Tilers Forum; When wiring is terminated in a shoddy manner at a socket outlet and there is about 6mm of bare conductor exposed at the L and N terminals, what do you ...
  1. #1
    Electricians Arms Member
    Join Date
    Dec 2010
    Location
    Manchester
    Posts
    233
    Thanks
    25
    Thanked 74 Times
    in 50 Posts

    Default Excess bare live conductor at terminations - code?

    When wiring is terminated in a shoddy manner at a socket outlet and there is about 6mm of bare conductor exposed at the L and N terminals, what do you code it?
    Personally I think a 2 is appropriate as it may give rise to danger - not a 1 as you can't touch it, but certainly more serious than a 4

    Simon.

  2. #2
    Member
    malcolmsanford's Avatar
    Join Date
    Jul 2010
    Location
    Kent working in the smoke for now
    Posts
    7,018
    Thanks
    766
    Thanked 1,630 Times
    in 1,364 Posts

    Default Re: Excess bare live conductor at terminations - code?

    WDML if this a terminal in a socket. or a light or a CU which in normal use would not have any mechanical stresses like vibration on it why would you deem it is in need of improvement to a degree that it could become dangerous.

    Yes a motor or a piece of equipment that moves you could if you felt there was a chance of bare conductors touching due to that movement code it but I would never code it a 2 as you are then most likely to deem the installation unsatisfactory.

    If you want to code it then perhaps a 4 for 134.1.1 for workmanship

  3. #3
    Member
    robsparky1975's Avatar
    Join Date
    Oct 2009
    Location
    isle of wight
    Posts
    1,326
    Thanks
    48
    Thanked 126 Times
    in 112 Posts

    Default Re: Excess bare live conductor at terminations - code?

    yes a code 2 requires improvement.your correct on assumtions with the use of codes imo on this.

  4. #4
    Member
    robsparky1975's Avatar
    Join Date
    Oct 2009
    Location
    isle of wight
    Posts
    1,326
    Thanks
    48
    Thanked 126 Times
    in 112 Posts

    Default Re: Excess bare live conductor at terminations - code?

    code 4 maybe then,dont have the reg number to hand but every accessory shall be terminated correctly.

  5. #5
    Member
    malcolmsanford's Avatar
    Join Date
    Jul 2010
    Location
    Kent working in the smoke for now
    Posts
    7,018
    Thanks
    766
    Thanked 1,630 Times
    in 1,364 Posts

    Default Re: Excess bare live conductor at terminations - code?

    Code 2 Requires Improvement

    This code is to be used to indicate that the observed deficiency requires action to remove potential danger.

    Taken from the ESC guide as a reference

    We are saying that if the insulation of a conductor as been stripped so far at a screw terminal that there is bare conductor showing, and if this is encased in an enclosure that requires a tool to access it, and there is no influences of vibration or mechanical stress on the cable it is a danger, to who?

  6. #6
    Electricians Arms Member
    Join Date
    Dec 2010
    Location
    Manchester
    Posts
    233
    Thanks
    25
    Thanked 74 Times
    in 50 Posts

    Default Re: Excess bare live conductor at terminations - code?

    OK thanks Malcolm, makes sense... just thought about possibility of arcing to back box etc


    Oh, and the installation was unsatisfactory anyway... Someone had changed the BS3036 fusebox for a BS3871 consumer unit - many many moons ago - but didn't bother to do some essentials like extending the CPCs to reach the earth busbar - they were just left in mid air!
    Had to sort those on the spot.

    Basically the story throughout the house was the original installation was sound, but let down by poor workmanship on the additions and alterations.

    Not seen one as bad for a while - but I have got the remedials

    Simon.
    Last edited by WDMDL; 03-10-2011 at 01:03 PM.

Similar Threads

  1. Using CPC as live conductor.... ok i know, but...
    By uksparks in forum Electrical Forum: General Electrical Forum
    Replies: 125
    Last Post: 03-03-2014, 09:54 PM
  2. NICEICís Connection magazine (using CPC as a live conductor)?
    By BigSi in forum Electrical Forum: General Electrical Forum
    Replies: 59
    Last Post: 25-04-2013, 03:32 AM
  3. Use of cpc as a live conductor - EICR Coding
    By LlandrilloSpark in forum Electrical Forum: General Electrical Forum
    Replies: 16
    Last Post: 02-04-2013, 09:58 PM
  4. Live earth conductor
    By JD Hogg in forum Electrical Forum: General Electrical Forum
    Replies: 13
    Last Post: 23-06-2012, 10:19 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread