Default Re: No R1 on ring main?

Ok, sorted. I was using a plug top with a link between live and Earth and the link had come out. Now, what worries me is the boards. They are old crabtree boards. The main earth is 6mm and the boards have a 80Amp 30mA RCD up front. I know it is ideal to renew the board but the council won't pay unless it is Cat 1 and essential. Surely this isn't 'essential' as it just means that when the RCD trips, every circuit is affected.
Thoughts gents.......
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-02-2008   #12 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 574
View ian.settle1's Photo Album
Default Re: No R1 on ring main?

Quote:
Originally Posted by cirrus View Post
Ok, sorted. I was using a plug top with a link between live and Earth and the link had come out. Now, what worries me is the boards. They are old crabtree boards. The main earth is 6mm and the boards have a 80Amp 30mA RCD up front. I know it is ideal to renew the board but the council won't pay unless it is Cat 1 and essential. Surely this isn't 'essential' as it just means that when the RCD trips, every circuit is affected.
Thoughts gents.......
And the council LABC are supposed to certify work is ok under Part P when notified..

What a bloody good laugh sounds like do as I say but not as I do...
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-02-2008   #13 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: No R1 on ring main?

Quote:
Originally Posted by cirrus View Post
Ok, sorted. I was using a plug top with a link between live and Earth and the link had come out. Now, what worries me is the boards. They are old crabtree boards. The main earth is 6mm and the boards have a 80Amp 30mA RCD up front. I know it is ideal to renew the board but the council won't pay unless it is Cat 1 and essential. Surely this isn't 'essential' as it just means that when the RCD trips, every circuit is affected.
Thoughts gents.......

Ok,

glad you got your readings sorted

bottom line is that this breaks a number of regs (16th edition). It depends if the council 'defines' what Cat I is. When an old dear falls down the stairs due loss of lights due to a spurious trip on an unrelated circuit, they may take notice, particularly if sued.......
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-02-2008   #14 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: No R1 on ring main?

I know Tony - so what do the regs state?
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-02-2008   #15 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: No R1 on ring main?

Quote:
Originally Posted by cirrus View Post
Ok, sorted. I was using a plug top with a link between live and Earth and the link had come out. Now, what worries me is the boards. They are old crabtree boards. The main earth is 6mm and the boards have a 80Amp 30mA RCD up front. I know it is ideal to renew the board but the council won't pay unless it is Cat 1 and essential. Surely this isn't 'essential' as it just means that when the RCD trips, every circuit is affected.
Thoughts gents.......
well it breaks a number of regs (16th edition) and is a safety matter if an old dear falls down the stairs due to loss of lights after a spurious fault on an unrelated circuit trips the RCD
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-02-2008   #16 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: No R1 on ring main?

I understand the H&S aspect but am not sure exaclt what regs it contravenes
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-02-2008   #17 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: No R1 on ring main?

Cirrus

i can quote the regs to you tomorrow when i got the book in front of me

main one is seperation of circuits, then theres the requirement for an RCD used as amain isolator to minimum 100mA S type

If, for example, you had smokes installed you can also be contravening seperate BS regs

get back to you tommorrow
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 17-02-2008   #18 (permalink)
Mutts
Junior Member
 
Join Date: Feb 2008
Posts: 14
View Mutts's Photo Album
Default Re: No R1 on ring main?

Hey cirrus

sorry to get involved this late but i have only just started to use this forum, Anyway heres my understanding of what going on.

r1 = the end to end reading on the phase conductor on the ring
r2 = the end to end reading on the on the cpc (earth) conductor on the ring
rn = the end to end reading on the nuetral conductor on the ring

these readings should be taken at the consumer unit using a low ohms continuity tester.

so if you are not getting an end to end reading on the phase conductor you are not getting an r1 reading. which would suggest that somewhere on the ring circuit the phase coductors have seperated. (eg fallen out of the back of a socket outlet or been damaged in some way) ive also had cases where the grubb screw on the socket outlet has been screwed against the insulation and is not making contact with the copper conductor inside so look carefully. if your really unlucky the problem could be in a junction box somewhere.

The reason why you are still getting a zs reading is because the ring circuit is fed from both "legs" of the ring

hopefully you'll find it but if you don't you need to seperate the ring main and create 2 x 16 amp radial circuits.

As for the RCD protection on a TT system. You need to have a 100ma RCD time delay mainswitch But you need to make sure you also have 30ma RCD protection on the usaul circuits ie Socket outlets, showers etc. Are there RCBO's available for the consumer unit you are dealing with?

Its always worth doing all your essentail tests before working on existing circuits as well as after at least you know what your up against from the beginnig

Good luck dude.........Mutts
Mutts is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #19 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: No R1 on ring main?

Quote:
Originally Posted by Mutts View Post
Hey cirrus

sorry to get involved this late but i have only just started to use this forum, Anyway heres my understanding of what going on.

r1 = the end to end reading on the phase conductor on the ring
r2 = the end to end reading on the on the cpc (earth) conductor on the ring
rn = the end to end reading on the nuetral conductor on the ring

these readings should be taken at the consumer unit using a low ohms continuity tester.

so if you are not getting an end to end reading on the phase conductor you are not getting an r1 reading. which would suggest that somewhere on the ring circuit the phase coductors have seperated. (eg fallen out of the back of a socket outlet or been damaged in some way) ive also had cases where the grubb screw on the socket outlet has been screwed against the insulation and is not making contact with the copper conductor inside so look carefully. if your really unlucky the problem could be in a junction box somewhere.

The reason why you are still getting a zs reading is because the ring circuit is fed from both "legs" of the ring

hopefully you'll find it but if you don't you need to seperate the ring main and create 2 x 16 amp radial circuits.

As for the RCD protection on a TT system. You need to have a 100ma RCD time delay mainswitch But you need to make sure you also have 30ma RCD protection on the usaul circuits ie Socket outlets, showers etc. Are there RCBO's available for the consumer unit you are dealing with?

Its always worth doing all your essentail tests before working on existing circuits as well as after at least you know what your up against from the beginnig

Good luck dude.........Mutts

Mutts, probably a typo, but surely you meant create two 20A radials?

And a 30mA on a shower, when was this a requirement? (unless of course you've gone 17th, in which case you can bin the 100mA for starters.......)
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-04-2008   #20 (permalink)
Had8Lives
Member
 
Join Date: Apr 2008
Posts: 54
View Had8Lives's Photo Album
Default Re: No R1 on ring main?

How are you connecting the ends of the ring at the board when you test?

Regarding the 6mm earth, I'd Code/Cat 1 it and replace with 10mm.


Last edited by Had8Lives; 12-04-2008 at 04:28 PM. Reason: Automerged Doublepost
Had8Lives is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks

LinkBacks (?)
LinkBack to this Thread: http://www.electriciansforums.co.uk/inspection-testing-certification-electrical-installations/446-no-r1-ring-main.html
Posted By For Type Date
Electricians Forum | Electrical Forum | A forum for electricians in the UK - Powered by vBulletin This thread Refback 15-02-2008 08:33 PM

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
ring main for computers new2this Commercial and Industrial Electrical 22 1 Week Ago 10:24 PM
Faulty ring main aaronstuart Inspection, Testing and Certification of Electrical Installations 5 14-09-2008 10:18 PM
Lighting spur off ring main Earthy General Electrical Discussion 4 11-08-2008 06:54 PM
Ring Main coling General Electrical Discussion 12 15-06-2008 10:00 PM
Ring Main Continuity Test Help clegg333 General Electrical Discussion 10 19-04-2008 12:30 PM

Google Search
Google

All times are GMT +1. The time now is 10:08 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38