incorrect insulation resistance reading

Discuss incorrect insulation resistance reading in the Inspection, Testing and Certification of Electrical Installations at Electricians Forums Discussion Boards; Hi all, be gentle. I have been asked to renew a cu so did some testing before commiting myself to the job. The board is fairly old with breakers and ...
  1. #1
    New to Electricians Forums
    Join Date
    Aug 2011
    Posts
    26
    Thanks
    28
    Thanked 0 Times in 0 Posts

    Default incorrect insulation resistance reading

    Hi all, be gentle.

    I have been asked to renew a cu so did some testing before commiting myself to the job.

    The board is fairly old with breakers and main switch. I was doing a ins resistance test on a radial that fed 4 sockets in the kitchen and a two way board in the garage. The cable at the board is 6mm and goes under the floor and reapears at the sockets and garage in 2.5mm. There appears to be a jb under the kitchen floor that is covered in expensive lino, glued down.

    When i did my test i got a slow reading >999 for the line/neutral and line /earth but a reading of 0.00 for earth/neutral. I believe this is a short caused by touching cables in the jb i cant get to or damage to the cable with a screw or nail bridging the earth/neutral.

    Have i read my meter correct and therefore my damage assumption is correct or is there something else that could be the problem.

    My issue is i cant get to the jb to check it. Should i suggest a rewire of this circuit to allow me to fit hte new cu with working rcd,s.

    Thanks for any help


  2. #2
    Electricians Arms Member Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    7,304
    Thanks
    388
    Thanked 694 Times in 643 Posts

    Default Re: incorrect insulation resistance reading

    Hum. My guess is that rewiring the circuit will be messy so I'd talk the options through with the customer. Changing a CU with an issue as you outlins isn't a great idea!


  3. #3
    New to Electricians Forums
    Join Date
    Aug 2011
    Posts
    26
    Thanks
    28
    Thanked 0 Times in 0 Posts

    Default Re: incorrect insulation resistance reading

    thanks murdoch

    Do you think that my assumption of the problem was probably correct

  4. #4
    Electricians Arms Member Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    7,304
    Thanks
    388
    Thanked 694 Times in 643 Posts

    Default Re: incorrect insulation resistance reading

    Probably, but without looking who knows. Have you tried your scheme's technical help line?

  5. The Following 3 Users Say Thank You to Murdoch For This Useful Post:

    ambrad (08-12-2011), topquark (08-12-2011)

  6. #5
    Electricians Arms Member
    topquark's Avatar
    Join Date
    Apr 2010
    Posts
    3,190
    Thanks
    957
    Thanked 514 Times in 462 Posts

    Default Re: incorrect insulation resistance reading

    What size of OCPD is on the 6mm cable at the main CU? I'd be a little concerned at the cable size changing from 6mm->2.5mm without it being fused down (is it possible they've spured off the cooker circuit?). You may be lucky and find the earth/neutral fault at one of the sockets.

    As Murdoch suggests discuss with the client and present the options.

  7. #6
    Electricians Forums Respected tony mc's Avatar
    Join Date
    Dec 2010
    Location
    North of London South of Edinburgh
    Posts
    1,112
    Thanks
    164
    Thanked 175 Times in 160 Posts

    Default Re: incorrect insulation resistance reading

    I aggree with topquark re the 6mm to 2.5 that needs sorting.

    Not being funny but you did disconnect the neutral fron the neutral bar in the CU before doing the test!

Similar Threads

  1. 0.27 of insulation reading
    By KillerKlown in forum PAT Testing
    Replies: 3
    Last Post: 01-03-2012, 06:35 PM
  2. resistance reading between neutral and earth
    By Dan oh! in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 6
    Last Post: 11-11-2011, 07:36 PM
  3. Fluke Insulation Resistance No Reading
    By notoriousgib83 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 11
    Last Post: 22-06-2011, 11:37 PM
  4. 0.001 insulation reistance reading
    By geordie in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 6
    Last Post: 25-02-2011, 07:02 AM
  5. No reading for insulation resistance fluke 1652b
    By Kay in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 10
    Last Post: 04-01-2011, 02:31 PM
  6. Low insulation resistance reading neutral to earth
    By paulc01689 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 17
    Last Post: 18-11-2010, 03:47 PM
  7. Insulation Resistance - Neutral - Earth Reading Issue?
    By chrisgc in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 18
    Last Post: 13-10-2010, 10:17 PM
  8. Insulation Resistance - no reading...
    By Dom in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 11
    Last Post: 29-03-2010, 08:58 PM
  9. Low Insulation Resistance Reading
    By down2earth in forum Electrical Forum, General Electrical Forum
    Replies: 2
    Last Post: 05-12-2009, 02:58 PM
  10. looking for electrician lancashire
    By calculator in forum Electricians Unite - Jobs In Your Area
    Replies: 2
    Last Post: 04-02-2009, 02:02 PM

Visitors found this page by searching for:

low insulation resistance readings

insulation resistance reading 0.00

electriciansforums.co.uk low insulation resistance readings line to earth

insulation resistance readings

twoway cu insulation test

incorrect insulation resistance values

insulation resistance test results 0.00 m

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31