Discuss incorrect insulation resistance reading in the Inspection, Testing and Certification of Electrical Installations at Electricians Forums Discussion Boards; Hi all, be gentle. I have been asked to renew a cu so did some testing before commiting myself to the job. The board is fairly old with breakers and ...- 08-12-2011 #1New to Electricians Forums
- Join Date
- Aug 2011
- Posts
- 26
- Thanks
- 28
- Thanked 0 Times in 0 Posts
incorrect insulation resistance reading
Hi all, be gentle.
I have been asked to renew a cu so did some testing before commiting myself to the job.
The board is fairly old with breakers and main switch. I was doing a ins resistance test on a radial that fed 4 sockets in the kitchen and a two way board in the garage. The cable at the board is 6mm and goes under the floor and reapears at the sockets and garage in 2.5mm. There appears to be a jb under the kitchen floor that is covered in expensive lino, glued down.
When i did my test i got a slow reading >999 for the line/neutral and line /earth but a reading of 0.00 for earth/neutral. I believe this is a short caused by touching cables in the jb i cant get to or damage to the cable with a screw or nail bridging the earth/neutral.
Have i read my meter correct and therefore my damage assumption is correct or is there something else that could be the problem.
My issue is i cant get to the jb to check it. Should i suggest a rewire of this circuit to allow me to fit hte new cu with working rcd,s.
Thanks for any help
- 08-12-2011 #2Electricians Arms Member
- Join Date
- Aug 2010
- Location
- Woking
- Posts
- 7,304
- Thanks
- 388
- Thanked 694 Times in 643 Posts
Re: incorrect insulation resistance reading
Hum. My guess is that rewiring the circuit will be messy so I'd talk the options through with the customer. Changing a CU with an issue as you outlins isn't a great idea!
- 08-12-2011 #3New to Electricians Forums
- Join Date
- Aug 2011
- Posts
- 26
- Thanks
- 28
- Thanked 0 Times in 0 Posts
Re: incorrect insulation resistance reading
thanks murdoch
Do you think that my assumption of the problem was probably correct
- 08-12-2011 #4Electricians Arms Member
- Join Date
- Aug 2010
- Location
- Woking
- Posts
- 7,304
- Thanks
- 388
- Thanked 694 Times in 643 Posts
Re: incorrect insulation resistance reading
Probably, but without looking who knows. Have you tried your scheme's technical help line?
-
- 08-12-2011 #5
Re: incorrect insulation resistance reading
What size of OCPD is on the 6mm cable at the main CU? I'd be a little concerned at the cable size changing from 6mm->2.5mm without it being fused down (is it possible they've spured off the cooker circuit?). You may be lucky and find the earth/neutral fault at one of the sockets.
As Murdoch suggests discuss with the client and present the options.
- 08-12-2011 #6Electricians Forums Respected
- Join Date
- Dec 2010
- Location
- North of London South of Edinburgh
- Posts
- 1,112
- Thanks
- 164
- Thanked 175 Times in 160 Posts
Re: incorrect insulation resistance reading
I aggree with topquark re the 6mm to 2.5 that needs sorting.
Not being funny but you did disconnect the neutral fron the neutral bar in the CU before doing the test!
Similar Threads
-
0.27 of insulation reading
By KillerKlown in forum PAT TestingReplies: 3Last Post: 01-03-2012, 06:35 PM -
resistance reading between neutral and earth
By Dan oh! in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 6Last Post: 11-11-2011, 07:36 PM -
Fluke Insulation Resistance No Reading
By notoriousgib83 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 11Last Post: 22-06-2011, 11:37 PM -
0.001 insulation reistance reading
By geordie in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 6Last Post: 25-02-2011, 07:02 AM -
No reading for insulation resistance fluke 1652b
By Kay in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 10Last Post: 04-01-2011, 02:31 PM -
Low insulation resistance reading neutral to earth
By paulc01689 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 17Last Post: 18-11-2010, 03:47 PM -
Insulation Resistance - Neutral - Earth Reading Issue?
By chrisgc in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 18Last Post: 13-10-2010, 10:17 PM -
Insulation Resistance - no reading...
By Dom in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 11Last Post: 29-03-2010, 08:58 PM -
Low Insulation Resistance Reading
By down2earth in forum Electrical Forum, General Electrical ForumReplies: 2Last Post: 05-12-2009, 02:58 PM -
looking for electrician lancashire
By calculator in forum Electricians Unite - Jobs In Your AreaReplies: 2Last Post: 04-02-2009, 02:02 PM



LinkBack URL
About LinkBacks

Reply With Quote















80A 100mA RCD in Domestic TT...
27 Minutes Ago in Electrical Forum, General Electrical Forum