Hi there,


Been doing periodics for 10 years now... Will someone clarify to me, now the 17th has come into effect, what regulations i'm testing to.... for example I was told by a very good spark that if the installation complies to 16th edition regs then its a pass with all the nessary notes explaning it must be upgraded, he even gives out one year certs to enforce this.

Another sparky however said that this isn't right and he is telling customers that everything must now comply to 17th edition. so if that means a re-wire so be it.
m4ttyd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-04-2009   #2 (permalink)
scotsparky
Respected Member
 
scotsparky's Avatar
 

Join Date: Apr 2009
Location: Glasgow
Posts: 1,048
Thanks: 16
Thanked 96 Times in 93 Posts
Default Re: PIR 16th Vs 17th please clarify

If ithats the case half the country would need rewires.

I test to 17th and on my defect sheet (page 2 ) mark whats needs done as recommendations. For instance rcd protection on circuits in an office. If the circuit is fine and without an rcd the Zs is low enouph for correct disconnection i would class 2 it. But would class 1 circuits where it could suppply something outdoors. Remeber PIRs are a report and if the cliet doesnt want to do anything thats his problem hes paying you to give advice.
scotsparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-04-2009   #3 (permalink)
Tapout,choke
Member
 
Tapout,choke's Avatar
 

Join Date: Oct 2008
Location: West lancs
Posts: 51
Thanks: 7
Thanked 0 Times in 0 Posts
Default Re: PIR 16th Vs 17th please clarify

Hi folks

correct me if I am wrong hear but I was under the impression that all socket outlets had to be protected by an rcd I-n 30ma indoors if they whereto be used by none competent persons
I would probably give this a code 1

But I would probably give this a code 2Additional protection not provided by 30-ma rcd for cables concealed in walls or ceilings for protection against penetration

I think we need to judge each installation on its own merits

Also I think we are all guilty of this how much you want thee remedial works ????
Tapout,choke is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-04-2009   #4 (permalink)
Jason.S
Super Moderator
 
Jason.S's Avatar
 

Join Date: Mar 2008
Location: In MY world.
Posts: 4,385
Thanks: 154
Thanked 530 Times in 475 Posts
Default Re: PIR 16th Vs 17th please clarify

If there are any code 1's on an installation, then its generally an instant unsatisfactory and the place shut down and locked off.

Code 2 would be a maximum for non RCD socket outlets IMO.
__________________
Whatever happens, don't blame me.
--------------------------------------------------------------------------------------
All opinions expressed by myself, are not necessarily those of Electricians Forums.
Jason.S is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-04-2009   #5 (permalink)
old dog
Senior Member
 
old dog's Avatar
 

Join Date: Jul 2008
Location: london
Posts: 358
Thanks: 4
Thanked 42 Times in 38 Posts
Default Re: PIR 16th Vs 17th please clarify

code 1 requires urgent attention
code 2 requires improvment
code 3 requires further investigation
code 4 dose not comply with bs 7671 / 2008
therefore an installation comleted to the 16th edition
would be a code 4
old dog is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-04-2009   #6 (permalink)
scotsparky
Respected Member
 
scotsparky's Avatar
 

Join Date: Apr 2009
Location: Glasgow
Posts: 1,048
Thanks: 16
Thanked 96 Times in 93 Posts
Default Re: PIR 16th Vs 17th please clarify

true old dog.
__________________
If you hear a bang its me please get an ambulance!!
scotsparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-04-2009   #7 (permalink)
spark1
Senior Member
 

Join Date: Mar 2009
Location: merseyside
Posts: 126
Thanks: 0
Thanked 16 Times in 16 Posts
Default Re: PIR 16th Vs 17th please clarify

Quote:
Originally Posted by old dog View Post
code 1 requires urgent attention
code 2 requires improvment
code 3 requires further investigation
code 4 dose not comply with bs 7671 / 2008
therefore an installation comleted to the 16th edition
would be a code 4

Using this as a rule then an installation completed to the 13th edition would also be a code 4 ![satisfactory]
Undersized Main Earth
Probably No Main bonding
No Supplementary bonding
Possibly Voltage Operated type Elcb
No cpc to lights
No RCd protection ...Anywhere...
I could go on......

No . I Test to B.S 7671 2008 but Code accordingly...............As a matter of interest any NICEIC sparks should take note that Codes 1 AND 2 are now deemed to result in an Unsatisfactory result on a P.I.R
spark1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-04-2009   #8 (permalink)
m4ttyd
Junior Member
 

Join Date: Sep 2008
Posts: 7
Thanks: 0
Thanked 2 Times in 2 Posts
Default Re: PIR 16th Vs 17th please clarify

I've not herd that a code 2 is a fail if your niceic registered. I don't think that right.... Its a very grey area that i think needs to be addressed....
obviously a lot is down to the testers discresion but if I have very few codes 3 & 4's and one code 2, I tend to pass this.... As for No RCD being a code 1 thats not right as its not causing an immediate threat to danger its code 2 max.... and if this was my only code 2 I would pass it..
m4ttyd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-04-2009   #9 (permalink)
ron55
Member
 

Join Date: Dec 2008
Posts: 38
Thanks: 1
Thanked 5 Times in 5 Posts
Default Re: PIR 16th Vs 17th please clarify

Quote:
Originally Posted by Jason.S View Post
If there are any code 1's on an installation, then its generally an instant unsatisfactory and the place shut down and locked off.

Code 2 would be a maximum for non RCD socket outlets IMO.
Hi Jason

As much as I would love to do this, I don't think you have the legal right to shut off someone's supply and lock it off. They are commissioning you to do a report and ultimately it's down to them what cours of action will be taken.

Cheers, Ron
ron55 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-04-2009   #10 (permalink)
AMST09
Member
 

Join Date: Apr 2009
Posts: 37
Thanks: 0
Thanked 5 Times in 5 Posts
Default Re: PIR 16th Vs 17th please clarify

A code 4 is not up to current regulations (17th) but is not considered to be dangerous...eg green earthing conductor instead of green and yellow (only thing I can think of off the top of my head )

Just to add a PIR is not a certificate its a report on the status of the electrics
You are not then liable for the whole installation
If the client chooses to ignore what is put in the report then thats up to them
But you cannot insist that someone has a rewire or modifications done
It is completely their decision

Last edited by AMST09; 23-04-2009 at 09:43 PM.. Reason: Automerged Doublepost
AMST09 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks


LinkBacks (?)
LinkBack to this Thread: http://www.electriciansforums.co.uk/inspection-testing-certification-electrical-installations/5664-pir-16th-vs-17th-please-clarify.html
Posted By For Type Date
IET Forums - PIR - and how to code according to my site QS This thread Refback 13-07-2009 11:54 AM

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
17th edition refresher... how do i know if ive got the 16th?? snowiespark Electrical Courses & Electrical NVQ's 5 07-10-2009 06:28 PM
PIR 16th Vs 17th please clarify,here it is baldsparkies Inspection, Testing and Certification of Electrical Installations 2 12-05-2009 06:42 PM
16th / 17th edition change over timsey Electrical Forum | General Electrical Forum 1 07-05-2009 11:20 PM
2391 to 16th or 17th Edition Shakey Inspection, Testing and Certification of Electrical Installations 8 09-06-2008 04:55 PM
16th or 17th sparkies2306 Electrical Forum | General Electrical Forum 6 09-12-2007 01:25 AM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK