Thread: PIR 16th Vs 17th please clarify
- 22-04-2009 #1
PIR 16th Vs 17th please clarify
Hi there,
Been doing periodics for 10 years now... Will someone clarify to me, now the 17th has come into effect, what regulations i'm testing to.... for example I was told by a very good spark that if the installation complies to 16th edition regs then its a pass with all the nessary notes explaning it must be upgraded, he even gives out one year certs to enforce this.
Another sparky however said that this isn't right and he is telling customers that everything must now comply to 17th edition. so if that means a re-wire so be it.
- 22-04-2009 #2Electricians Arms Member
- Join Date
- Apr 2009
- Location
- Glasgow
- Posts
- 1,432
- Thanks
- 0
- Thanked 1 Time in 1 Post
Re: PIR 16th Vs 17th please clarify
If ithats the case half the country would need rewires.
I test to 17th and on my defect sheet (page 2 ) mark whats needs done as recommendations. For instance rcd protection on circuits in an office. If the circuit is fine and without an rcd the Zs is low enouph for correct disconnection i would class 2 it. But would class 1 circuits where it could suppply something outdoors. Remeber PIRs are a report and if the cliet doesnt want to do anything thats his problem hes paying you to give advice.
- 22-04-2009 #3
Re: PIR 16th Vs 17th please clarify
Hi folks
correct me if I am wrong hear but I was under the impression that all socket outlets had to be protected by an rcd I-n 30ma indoors if they whereto be used by none competent persons
I would probably give this a code 1
But I would probably give this a code 2Additional protection not provided by 30-ma rcd for cables concealed in walls or ceilings for protection against penetration
I think we need to judge each installation on its own merits
Also I think we are all guilty of this how much you want thee remedial works ????
- 22-04-2009 #4Administrator
- Join Date
- Mar 2008
- Location
- In MY world.
- Posts
- 5,466
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: PIR 16th Vs 17th please clarify
If there are any code 1's on an installation, then its generally an instant unsatisfactory and the place shut down and locked off.
Code 2 would be a maximum for non RCD socket outlets IMO.
- 22-04-2009 #5
Re: PIR 16th Vs 17th please clarify
code 1 requires urgent attention
code 2 requires improvment
code 3 requires further investigation
code 4 dose not comply with bs 7671 / 2008
therefore an installation comleted to the 16th edition
would be a code 4
- 22-04-2009 #6Electricians Arms Member
- Join Date
- Apr 2009
- Location
- Glasgow
- Posts
- 1,432
- Thanks
- 0
- Thanked 1 Time in 1 Post
Re: PIR 16th Vs 17th please clarify
true old dog.
If there is a smoking section in a resteraunt can there be a urinating section in the swimming pool??
- 23-04-2009 #7
Re: PIR 16th Vs 17th please clarify
Using this as a rule then an installation completed to the 13th edition would also be a code 4 ![satisfactory]
Undersized Main Earth
Probably No Main bonding
No Supplementary bonding
Possibly Voltage Operated type Elcb
No cpc to lights
No RCd protection ...Anywhere...
I could go on......
No . I Test to B.S 7671 2008 but Code accordingly...............As a matter of interest any NICEIC sparks should take note that Codes 1 AND 2 are now deemed to result in an Unsatisfactory result on a P.I.R
- 23-04-2009 #8
Re: PIR 16th Vs 17th please clarify
I've not herd that a code 2 is a fail if your niceic registered. I don't think that right.... Its a very grey area that i think needs to be addressed....
obviously a lot is down to the testers discresion but if I have very few codes 3 & 4's and one code 2, I tend to pass this.... As for No RCD being a code 1 thats not right as its not causing an immediate threat to danger its code 2 max.... and if this was my only code 2 I would pass it..
- 23-04-2009 #9
Re: PIR 16th Vs 17th please clarify
- 23-04-2009 #10
Re: PIR 16th Vs 17th please clarify
A code 4 is not up to current regulations (17th) but is not considered to be dangerous...eg green earthing conductor instead of green and yellow (only thing I can think of off the top of my head
)
Just to add a PIR is not a certificate its a report on the status of the electrics
You are not then liable for the whole installation
If the client chooses to ignore what is put in the report then thats up to them
But you cannot insist that someone has a rewire or modifications done
It is completely their decisionLast edited by AMST09; 23-04-2009 at 09:43 PM. Reason: Automerged Doublepost
Similar Threads
-
17th edition refresher... how do i know if ive got the 16th??
By snowiespark in forum Electrical Courses & Electrical NVQ'sReplies: 5Last Post: 07-10-2009, 06:28 PM -
PIR 16th Vs 17th please clarify,here it is
By baldsparkies in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 2Last Post: 12-05-2009, 06:42 PM -
16th / 17th edition change over
By timsey in forum Electrical Forum | General Electrical ForumReplies: 1Last Post: 07-05-2009, 11:20 PM -
2391 to 16th or 17th Edition
By Shakey in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 8Last Post: 09-06-2008, 04:55 PM -
16th or 17th
By sparkies2306 in forum Electrical Forum | General Electrical ForumReplies: 6Last Post: 09-12-2007, 12:25 AM



LinkBack URL
About LinkBacks




Reply With Quote







Bookmarks