    Default PIR 16th Vs 17th please clarify

    Hi there,


    Been doing periodics for 10 years now... Will someone clarify to me, now the 17th has come into effect, what regulations i'm testing to.... for example I was told by a very good spark that if the installation complies to 16th edition regs then its a pass with all the nessary notes explaning it must be upgraded, he even gives out one year certs to enforce this.

    Another sparky however said that this isn't right and he is telling customers that everything must now comply to 17th edition. so if that means a re-wire so be it.

  2. #2
    Electricians Arms Member scotsparky's Avatar
    Join Date
    Apr 2009
    Location
    Glasgow
    Posts
    1,432
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: PIR 16th Vs 17th please clarify

    If ithats the case half the country would need rewires.

    I test to 17th and on my defect sheet (page 2 ) mark whats needs done as recommendations. For instance rcd protection on circuits in an office. If the circuit is fine and without an rcd the Zs is low enouph for correct disconnection i would class 2 it. But would class 1 circuits where it could suppply something outdoors. Remeber PIRs are a report and if the cliet doesnt want to do anything thats his problem hes paying you to give advice.

  3. #3
    Member Tapout,choke's Avatar
    Join Date
    Oct 2008
    Location
    West lancs
    Posts
    87
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    Hi folks

    correct me if I am wrong hear but I was under the impression that all socket outlets had to be protected by an rcd I-n 30ma indoors if they whereto be used by none competent persons
    I would probably give this a code 1

    But I would probably give this a code 2Additional protection not provided by 30-ma rcd for cables concealed in walls or ceilings for protection against penetration

    I think we need to judge each installation on its own merits

    Also I think we are all guilty of this how much you want thee remedial works ????

  4. #4
    Administrator Jason.S's Avatar
    Join Date
    Mar 2008
    Location
    In MY world.
    Posts
    5,466
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    If there are any code 1's on an installation, then its generally an instant unsatisfactory and the place shut down and locked off.

    Code 2 would be a maximum for non RCD socket outlets IMO.

  5. #5
    Senior Member old dog's Avatar
    Join Date
    Jul 2008
    Location
    london
    Posts
    358
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    code 1 requires urgent attention
    code 2 requires improvment
    code 3 requires further investigation
    code 4 dose not comply with bs 7671 / 2008
    therefore an installation comleted to the 16th edition
    would be a code 4

  6. #6
    Electricians Arms Member scotsparky's Avatar
    Join Date
    Apr 2009
    Location
    Glasgow
    Posts
    1,432
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: PIR 16th Vs 17th please clarify

    true old dog.
    If there is a smoking section in a resteraunt can there be a urinating section in the swimming pool??

  7. #7
    Senior Member spark1's Avatar
    Join Date
    Mar 2009
    Location
    merseyside
    Posts
    126
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    Quote Originally Posted by old dog View Post
    code 1 requires urgent attention
    code 2 requires improvment
    code 3 requires further investigation
    code 4 dose not comply with bs 7671 / 2008
    therefore an installation comleted to the 16th edition
    would be a code 4

    Using this as a rule then an installation completed to the 13th edition would also be a code 4 ![satisfactory]
    Undersized Main Earth
    Probably No Main bonding
    No Supplementary bonding
    Possibly Voltage Operated type Elcb
    No cpc to lights
    No RCd protection ...Anywhere...
    I could go on......

    No . I Test to B.S 7671 2008 but Code accordingly...............As a matter of interest any NICEIC sparks should take note that Codes 1 AND 2 are now deemed to result in an Unsatisfactory result on a P.I.R

  8. #8
    Junior Member m4ttyd's Avatar
    Join Date
    Sep 2008
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    I've not herd that a code 2 is a fail if your niceic registered. I don't think that right.... Its a very grey area that i think needs to be addressed....
    obviously a lot is down to the testers discresion but if I have very few codes 3 & 4's and one code 2, I tend to pass this.... As for No RCD being a code 1 thats not right as its not causing an immediate threat to danger its code 2 max.... and if this was my only code 2 I would pass it..

  9. #9
    Electricians Arms Member ron55's Avatar
    Join Date
    Dec 2008
    Posts
    43
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    Quote Originally Posted by Jason.S View Post
    If there are any code 1's on an installation, then its generally an instant unsatisfactory and the place shut down and locked off.

    Code 2 would be a maximum for non RCD socket outlets IMO.
    Hi Jason

    As much as I would love to do this, I don't think you have the legal right to shut off someone's supply and lock it off. They are commissioning you to do a report and ultimately it's down to them what cours of action will be taken.

    Cheers, Ron

  10. #10
    Member AMST09's Avatar
    Join Date
    Apr 2009
    Posts
    37
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: PIR 16th Vs 17th please clarify

    A code 4 is not up to current regulations (17th) but is not considered to be dangerous...eg green earthing conductor instead of green and yellow (only thing I can think of off the top of my head )

    Just to add a PIR is not a certificate its a report on the status of the electrics
    You are not then liable for the whole installation
    If the client chooses to ignore what is put in the report then thats up to them
    But you cannot insist that someone has a rewire or modifications done
    It is completely their decision
    Last edited by AMST09; 23-04-2009 at 09:43 PM. Reason: Automerged Doublepost

+ Reply to Thread
Page 1 of 9 1 2 3 4 5 ... LastLast

Similar Threads

  1. 17th edition refresher... how do i know if ive got the 16th??
    By snowiespark in forum Electrical Courses & Electrical NVQ's
    Replies: 5
    Last Post: 07-10-2009, 06:28 PM
  2. PIR 16th Vs 17th please clarify,here it is
    By baldsparkies in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 2
    Last Post: 12-05-2009, 06:42 PM
  3. 16th / 17th edition change over
    By timsey in forum Electrical Forum | General Electrical Forum
    Replies: 1
    Last Post: 07-05-2009, 11:20 PM
  4. 2391 to 16th or 17th Edition
    By Shakey in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 8
    Last Post: 09-06-2008, 04:55 PM
  5. 16th or 17th
    By sparkies2306 in forum Electrical Forum | General Electrical Forum
    Replies: 6
    Last Post: 09-12-2007, 12:25 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24