Thread: Minor Works.. No RCD on Circuit ?
Discuss Minor Works.. No RCD on Circuit ? at the Inspection, Testing and Certification of Electrical Installations within the ElectriciansForums; A customer has a big bedroom with only 1 pendant in the middle of the room, He asks you to make 2 lights in this ...- 29-07-2009 #1
Minor Works.. No RCD on Circuit ?
A customer has a big bedroom with only 1 pendant in the middle of the room, He asks you to make 2 lights in this room, making 2 pendants one either end of the bedroom.
What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?
Also as its only minor works and in a bedroom, its not notifiable... Correct?
But still needs a MWC giving to the customer..
Also it is still permissable to carry out minor works if bonding is not present in the installation..
- 29-07-2009 #2
Re: Minor Works.. No RCD on Circuit ?
i would have thought its an alteration so needs to be rcd protected and brought up to 17th edition.
- 29-07-2009 #3
Re: Minor Works.. No RCD on Circuit ?
What would be the cheapest option for the customer do you think...??
As said many times, for small jobs like this if its going to cost the customer alot you will end up loosing work..
Do most of you just tell the customer for what seems like a small quick job is actually going to cost quite abit and if they say No, then just take it on the chin..
Its just a "P off" it has to be this way for the customer and the electrician... But i know.. regs are regs!
- 29-07-2009 #4
Re: Minor Works.. No RCD on Circuit ?
1) In my opinion a note on the certificate will be enough if an RCD is only providing supplementary protection. Thats how I interperet 131.8 anyway, and will be interested in other opinions.What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?
2) Replace the lighting MCB with an RCBO
I believe soAlso as its only minor works and in a bedroom, its not notifiable... Correct?
YesBut still needs a MWC giving to the customer..
No because you will NOT be complying with regulation 131.8Also it is still permissable to carry out minor works if bonding is not present in the installation..
- 29-07-2009 #5
- 29-07-2009 #6
Re: Minor Works.. No RCD on Circuit ?
There is a big difference between not being up to scratch, and not being present at all
- 29-07-2009 #7
Re: Minor Works.. No RCD on Circuit ?
Ha ha, I agree!!
I got this from an "Inspection & Testing" Text Book under the section, Minor Works Certs..
Confirmation of bondingHas bonding been installed? If not, this should be
pointed out to the client, and identified in the comments section of the
certificate. It is still permissible to carry out minor works if bonding is not present
in the installation.
- 29-07-2009 #8Senior Member
- Join Date
- Feb 2009
- Location
- Newcastle - the one up North !!!
- Posts
- 115
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Minor Works.. No RCD on Circuit ?
If it is a 16th Edition CCU, then as long as main bonding is compliant with 16th edition regs, then you are half way there. Of course, if lighting isn't on RCD, then you will have to ensure supplementary bonding is in place.
If you put lights on RCBO, then check main bonding meets 17th edition.
HOWEVER, if new cable joining pendant ( original ) to pendant ( new ) is above the ceiling, then does the RCD requirement still apply ??????
BUT, if 2nd pendant is to be wired so that it switches independantly to the first, then cable drop to switch will possibly require RCD protection.
- 29-07-2009 #9
- 30-07-2009 #10
Re: Minor Works.. No RCD on Circuit ?
Sid, never be afraid to ring Elecsa if you have a specific question such as this.
The Techline guys will happilly put you on the right track.
Jeff & Steve are easy to talk to (if you can get a word in
) & very practical.
Two heads are better than one - even when they`re sheep`s
Similar Threads
-
***Useful Information For The Working Sparky***
By amberleaf in forum Electrical Forum | General Electrical ForumReplies: 208Last Post: 03-08-2010, 03:14 PM -
bathroom pendant / separate lighting circuit RCD
By mikex79 in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 10Last Post: 02-11-2009, 08:29 AM -
Lighting circuit trips RCD
By Shinner in forum Electrical Forum | General Electrical ForumReplies: 16Last Post: 07-05-2009, 06:07 PM -
Dedicated circuit not on an rcd
By Steve D in forum Electrical Forum | General Electrical ForumReplies: 1Last Post: 03-02-2009, 02:06 PM



LinkBack URL
About LinkBacks



Reply With Quote







Bookmarks