Thread: Minor Works.. No RCD on Circuit ?

Discuss Minor Works.. No RCD on Circuit ? at the Inspection, Testing and Certification of Electrical Installations within the ElectriciansForums; A customer has a big bedroom with only 1 pendant in the middle of the room, He asks you to make 2 lights in this ...
  1. #1
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    752
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Minor Works.. No RCD on Circuit ?

    A customer has a big bedroom with only 1 pendant in the middle of the room, He asks you to make 2 lights in this room, making 2 pendants one either end of the bedroom.

    What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?

    Also as its only minor works and in a bedroom, its not notifiable... Correct?


    But still needs a MWC giving to the customer..
    Also it is still permissable to carry out minor works if bonding is not present in the installation..

  2. #2
    Member claire_r's Avatar
    Join Date
    Aug 2008
    Posts
    88
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    i would have thought its an alteration so needs to be rcd protected and brought up to 17th edition.

  3. #3
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    752
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    What would be the cheapest option for the customer do you think...??

    As said many times, for small jobs like this if its going to cost the customer alot you will end up loosing work..

    Do most of you just tell the customer for what seems like a small quick job is actually going to cost quite abit and if they say No, then just take it on the chin..

    Its just a "P off" it has to be this way for the customer and the electrician... But i know.. regs are regs!

  4. #4
    Electricians Arms Member xraytek's Avatar
    Join Date
    May 2009
    Posts
    218
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?
    1) In my opinion a note on the certificate will be enough if an RCD is only providing supplementary protection. Thats how I interperet 131.8 anyway, and will be interested in other opinions.
    2) Replace the lighting MCB with an RCBO

    Also as its only minor works and in a bedroom, its not notifiable... Correct?
    I believe so

    But still needs a MWC giving to the customer..
    Yes

    Also it is still permissable to carry out minor works if bonding is not present in the installation..
    No because you will NOT be complying with regulation 131.8

  5. #5
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    752
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    Quote Originally Posted by xraytek View Post
    No because you will NOT be complying with regulation 131.8
    Ive been told by others that if its Minor works not in a special location, then if bonding isnt up to scratch you can still continue the works.. Have i been informed wrong then..?

  6. #6
    Electricians Arms Member xraytek's Avatar
    Join Date
    May 2009
    Posts
    218
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    There is a big difference between not being up to scratch, and not being present at all

  7. #7
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    752
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    Quote Originally Posted by xraytek View Post
    There is a big difference between not being up to scratch, and not being present at all

    Ha ha, I agree!!



    I got this from an "Inspection & Testing" Text Book under the section, Minor Works Certs..

    Confirmation of bonding
    Has bonding been installed? If not, this should be
    pointed out to the client, and identified in the comments section of the
    certificate.
    It is still permissible to carry out minor works if bonding is not present

    in the installation.

  8. #8
    Senior Member chocolate's Avatar
    Join Date
    Feb 2009
    Location
    Newcastle - the one up North !!!
    Posts
    115
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    If it is a 16th Edition CCU, then as long as main bonding is compliant with 16th edition regs, then you are half way there. Of course, if lighting isn't on RCD, then you will have to ensure supplementary bonding is in place.

    If you put lights on RCBO, then check main bonding meets 17th edition.

    HOWEVER, if new cable joining pendant ( original ) to pendant ( new ) is above the ceiling, then does the RCD requirement still apply ??????

    BUT, if 2nd pendant is to be wired so that it switches independantly to the first, then cable drop to switch will possibly require RCD protection.

  9. #9
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    752
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    Quote Originally Posted by chocolate View Post
    If it is a 16th Edition CCU, then as long as main bonding is compliant with 16th edition regs, then you are half way there. Of course, if lighting isn't on RCD, then you will have to ensure supplementary bonding is in place.

    So aslong as incoming services are bonded then i am ok? And No RCD is needed? Sounds 16th to me...

  10. #10
    Electricians Arms Member electricAl's Avatar
    Join Date
    Dec 2008
    Posts
    388
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Minor Works.. No RCD on Circuit ?

    Sid, never be afraid to ring Elecsa if you have a specific question such as this.

    The Techline guys will happilly put you on the right track.

    Jeff & Steve are easy to talk to (if you can get a word in ) & very practical.
    Two heads are better than one - even when they`re sheep`s

Similar Threads

  1. ***Useful Information For The Working Sparky***
    By amberleaf in forum Electrical Forum | General Electrical Forum
    Replies: 208
    Last Post: 03-08-2010, 03:14 PM
  2. bathroom pendant / separate lighting circuit RCD
    By mikex79 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 10
    Last Post: 02-11-2009, 08:29 AM
  3. Lighting circuit trips RCD
    By Shinner in forum Electrical Forum | General Electrical Forum
    Replies: 16
    Last Post: 07-05-2009, 06:07 PM
  4. Dedicated circuit not on an rcd
    By Steve D in forum Electrical Forum | General Electrical Forum
    Replies: 1
    Last Post: 03-02-2009, 02:06 PM

Visitors found this page by searching for:

do minor works require rcds

retrospective minor works

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24