A customer has a big bedroom with only 1 pendant in the middle of the room, He asks you to make 2 lights in this room, making 2 pendants one either end of the bedroom.

What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?

Also as its only minor works and in a bedroom, its not notifiable... Correct?


But still needs a MWC giving to the customer..
Also it is still permissable to carry out minor works if bonding is not present in the installation..
magic-sid is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #2 (permalink)
claire_r
Member
 

Join Date: Aug 2008
Posts: 83
Thanks: 11
Thanked 14 Times in 13 Posts
Default Re: Minor Works.. No RCD on Circuit ?

i would have thought its an alteration so needs to be rcd protected and brought up to 17th edition.
claire_r is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #3 (permalink)
magic-sid
Respected Member
 

Join Date: Aug 2008
Posts: 536
Thanks: 16
Thanked 19 Times in 18 Posts
Default Re: Minor Works.. No RCD on Circuit ?

What would be the cheapest option for the customer do you think...??

As said many times, for small jobs like this if its going to cost the customer alot you will end up loosing work..

Do most of you just tell the customer for what seems like a small quick job is actually going to cost quite abit and if they say No, then just take it on the chin..

Its just a "P off" it has to be this way for the customer and the electrician... But i know.. regs are regs!
magic-sid is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #4 (permalink)
xraytek
Senior Member
 

Join Date: May 2009
Posts: 177
Thanks: 6
Thanked 33 Times in 28 Posts
Default Re: Minor Works.. No RCD on Circuit ?

Quote:
What our my options to comply with 17th as the CU is to 16th so lighting is not RCD protected?
1) In my opinion a note on the certificate will be enough if an RCD is only providing supplementary protection. Thats how I interperet 131.8 anyway, and will be interested in other opinions.
2) Replace the lighting MCB with an RCBO

Quote:
Also as its only minor works and in a bedroom, its not notifiable... Correct?
I believe so

Quote:
But still needs a MWC giving to the customer..
Yes

Quote:
Also it is still permissable to carry out minor works if bonding is not present in the installation..
No because you will NOT be complying with regulation 131.8
xraytek is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #5 (permalink)
magic-sid
Respected Member
 

Join Date: Aug 2008
Posts: 536
Thanks: 16
Thanked 19 Times in 18 Posts
Default Re: Minor Works.. No RCD on Circuit ?

Quote:
Originally Posted by xraytek View Post
No because you will NOT be complying with regulation 131.8
Ive been told by others that if its Minor works not in a special location, then if bonding isnt up to scratch you can still continue the works.. Have i been informed wrong then..?
magic-sid is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #6 (permalink)
xraytek
Senior Member
 

Join Date: May 2009
Posts: 177
Thanks: 6
Thanked 33 Times in 28 Posts
Default Re: Minor Works.. No RCD on Circuit ?

There is a big difference between not being up to scratch, and not being present at all
xraytek is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #7 (permalink)
magic-sid
Respected Member
 

Join Date: Aug 2008
Posts: 536
Thanks: 16
Thanked 19 Times in 18 Posts
Default Re: Minor Works.. No RCD on Circuit ?

Quote:
Originally Posted by xraytek View Post
There is a big difference between not being up to scratch, and not being present at all

Ha ha, I agree!!



I got this from an "Inspection & Testing" Text Book under the section, Minor Works Certs..

Confirmation of bonding
Has bonding been installed? If not, this should be
pointed out to the client, and identified in the comments section of the
certificate.
It is still permissible to carry out minor works if bonding is not present

in the installation.
magic-sid is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #8 (permalink)
chocolate
Senior Member
 

Join Date: Feb 2009
Location: Newcastle - the one up North !!!
Posts: 109
Thanks: 2
Thanked 8 Times in 7 Posts
Default Re: Minor Works.. No RCD on Circuit ?

If it is a 16th Edition CCU, then as long as main bonding is compliant with 16th edition regs, then you are half way there. Of course, if lighting isn't on RCD, then you will have to ensure supplementary bonding is in place.

If you put lights on RCBO, then check main bonding meets 17th edition.

HOWEVER, if new cable joining pendant ( original ) to pendant ( new ) is above the ceiling, then does the RCD requirement still apply ??????

BUT, if 2nd pendant is to be wired so that it switches independantly to the first, then cable drop to switch will possibly require RCD protection.
chocolate is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2009   #9 (permalink)
magic-sid
Respected Member
 

Join Date: Aug 2008
Posts: 536
Thanks: 16
Thanked 19 Times in 18 Posts
Default Re: Minor Works.. No RCD on Circuit ?

Quote:
Originally Posted by chocolate View Post
If it is a 16th Edition CCU, then as long as main bonding is compliant with 16th edition regs, then you are half way there. Of course, if lighting isn't on RCD, then you will have to ensure supplementary bonding is in place.

So aslong as incoming services are bonded then i am ok? And No RCD is needed? Sounds 16th to me...
magic-sid is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-07-2009   #10 (permalink)
electricAl
Senior Member
 

Join Date: Dec 2008
Posts: 376
Thanks: 12
Thanked 66 Times in 62 Posts
Default Re: Minor Works.. No RCD on Circuit ?

Sid, never be afraid to ring Elecsa if you have a specific question such as this.

The Techline guys will happilly put you on the right track.

Jeff & Steve are easy to talk to (if you can get a word in ) & very practical.
__________________
Two heads are better than one - even when they`re sheep`s
electricAl is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
***Useful Information For The Working Sparky*** amberleaf Electrical Forum | General Electrical Forum 205 3 Weeks Ago 03:21 PM
bathroom pendant / separate lighting circuit RCD mikex79 Electrical Wiring, Theories and Electrical Regulations 10 02-11-2009 09:29 AM
Lighting circuit trips RCD Shinner Electrical Forum | General Electrical Forum 16 07-05-2009 06:07 PM
Dedicated circuit not on an rcd Steve D Electrical Forum | General Electrical Forum 1 03-02-2009 03:06 PM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK