Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Inspection, Testing and Certification of Electrical Installations
Forgot Password? Join Us!

Inspection, Testing and Certification of Electrical Installations This Section is STRICTLY for testing PROBLEMS which members have occured, misunderstood readings, Periodic Inspection Reporting, Mathematical Equations/Solutions, Part P and other legislation which require you to Inspect and Test.

Reply
 
LinkBack Thread Tools Display Modes
Old 18-04-2008   #11 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: testing for Ze and PFC.

Quote:
Originally Posted by Ross Trician View Post
Shakey would that mean then that if I installed a suitable spike etc at the incoming supply then I would have to ensure that all the instalations on the system (not just the 2 areas I have worked on) are correctly earthed and terminated etc throughout? and that they have adequate Ze, Zs, pfc tests etc?

What do you mean about the rcd wont work for the instalation?

( apologies for the many questions but it is helpfull when you get answers from someone who knows them)
Ross, sorry, the RCD will work, but you should not use it

Look at 314.1 (got the 17th in front of me now, but its the same as in the 16th)

"every installation shall be diveided into circuits as necessary, to:

(i) avoid hazards and minimize inconvenience in the event of a fault

(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit

(iv) reduce the possibility of unwanted tripping of RCD's due to excessive protective conductor currentd prodeuced by equipment in normal operation)

so for these three reasons, you cant use front end RCD's, unless they have lower value RCD's downstream, (like in a TT), but under the 17th, that will mostly go anyway

in answer to you first question, the Ze is ONLY at the origin, everythin else will be Zs - and yes, you take responsibility for the lot. The pint is, to certificate your work, as you know, you HAVE to include the supply characterisitics, Ze, PFC etc, which, unless you spike at the origin (or get PME installed etc) you wont have

sorry fella!
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-04-2008   #12 (permalink)
Ross Trician
Junior Member
 
Join Date: Jan 2008
Posts: 22
View Ross Trician's Photo Album
Default Re: testing for Ze and PFC.

cheers Shakey and all of you for the coments and help, yes I think it is the tip of the ice burge too,
I will see if a pme is possible and if not consider options from there.

It also depends I supose if they want to do anything about it, you know the old "it's always been like it and has always worked fine" scenario.

to be honest it is quite possibly one of those jobs that you perhaps want to avoid, more trouble than its worth etc...lol.
Ross Trician is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-04-2008   #13 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: testing for Ze and PFC.

Quote:
Originally Posted by Ross Trician View Post
cheers Shakey and all of you for the coments and help, yes I think it is the tip of the ice burge too,
I will see if a pme is possible and if not consider options from there.

It also depends I supose if they want to do anything about it, you know the old "it's always been like it and has always worked fine" scenario.

to be honest it is quite possibly one of those jobs that you perhaps want to avoid, more trouble than its worth etc...lol.
yep I think its one of those as well Ross....

I have no doubt they will not want to do anything about it - but that also means that you should follow their lead!!!!
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-05-2008   #14 (permalink)
Had8Lives
Member
 
Join Date: Apr 2008
Posts: 48
View Had8Lives's Photo Album
Default Re: testing for Ze and PFC.

I agree Steve.
Had8Lives is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-06-2008   #15 (permalink)
BillR3
Junior Member
 
Join Date: Jun 2008
Posts: 4
View BillR3's Photo Album
Default Re: testing for Ze and PFC.

Just a word of warning if you are going to fit earth rod(s)

As you know our 4 legged friends are susceptible to electric shock more than humans due to their contact with the ground so you will have to barrier off the earth rod(s) location(s) if you end up using your TT system to keep them from danger.

BillR3
BillR3 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-06-2008   #16 (permalink)
jibtech
Member
 
Join Date: Jun 2008
Posts: 61
View jibtech's Photo Album
Default Re: testing for Ze and PFC.

yes possibly the funniest part of college when the lecturer explains the ground fault voltages can easily floor a heffer

and then he explains that cows are curious beasts and the whole herd will more than likely wander over to take a look .......thud....thud...thud....thud

hahaha at 3000 quid a cow maybe more?? you better hope you can run faster than the farmer and his shotty

ps i think i would avoid this job unless the clients reaction was such that i was convinced he wants to put it totally right and proper and pay for it.cant see that happening though

jibtech is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 01:38 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Savings : Bad Credit Loan : Remortgages : Dvd for sale : Credit Cards

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28