Discuss Vitesse lighting marshalling box lcm in the Lighting Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

cliffed

-
Arms
Reaction score
644
Anyone know if there's an override control on this.
Lights were commissioned,but now don't come on at all.
Just wondering anyone come across this before,I know it may have to be commissioned again,but no lights at moment,but if a pain
 
Yea that doesn't switch off either,a smart system like this,it plays up,& there is no override,this is at a school,so it's a real headache.
Will get all reprogrammed.
 

Reply to Vitesse lighting marshalling box lcm in the Lighting Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock