Discuss Calculating current supplied to led drivers in the UK Electrical Forum area at ElectriciansForums.net

P

Proper Job

Hi folks.
On the site I'm working, another company is fitting out a little gym with ---- loads of led's in the ceiling. The strips are 100 mm apart and cover the area of roughly 8 metres by 8 metres. They are divided into 3 rectangular grid like formation.
So here is where the numbers come in.
I'm not going to say my opinion yet as truly I'm not very sure of the answer. Their installer tells me that for one of those large rectangles the led's use 700 watts and at 24 volts ( from the driver) therefore 700Ă·24 = 29 amps!! So this guy wants me to give him 3 time this meaning 9 Ă— 10 amp circuits.

This cannot be correct??
 
Just watch the start up current. We had an issue with a customer that had a new LED install where the switches had all failed. When we put a PA on it the startup was over 800amps!
 
Holy shhhmoke. 800 amps! What did you end up doing for the switching of thst ct then? Contactor?
Ya it is very bright but they are putting a large diffuser overy the whole thing otherwise you'd be walking out of there with a handsome tan!.
So so that 29 amps gets inversely change down to 3 amps on the incoming side then eh hmmm ?? interesting Mr bond
 

Reply to Calculating current supplied to led drivers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Forum people. First time post here. I have a pair of semi flush fittings that are currently 10 Halogen capsules per fitting. I want to...
Replies
17
Views
2K
how to calculate the needed power rating to light up 6 cool white and 6 white HPL chip like this ? what is the compatible driver specific to light...
Replies
0
Views
661
I have purchased a 16 mm 10 watt Cree LED (XM-L2) and a constant current voltage driver, the spec sheet for the LED has a maximum of 3 amps. I...
Replies
6
Views
1K
Hi all, This is my first time posting something on this forum. I'm busy putting together a design for some LED lights that are going to be...
Replies
0
Views
1K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock