I live in an ex council house in manchester which I imagine was built around the 1940s.
Upon renovating the severely outdated living room, I removed two ceramic wall fitted lights that had switches and were independent to the main light fitting in the room. I didn’t really pay attention to the...
Brief run down for you all
Checked end to end of ring that’s sound
Meggered LN sound NE sound LE 0.03
Split the ring same stuff
Split it again same stuff again
Long story short stripped all sockets off on the ring and every single leg has a LE fault
Was rewired 2010
Only logical thing I can...
Hello
I am adding a couple of sockets to an old industrial installation. I am replacing the existing sockets and adding two more into the ring. The installation is earthed through the metal conduit and an RCB has been retrofitted to the circuit after the old style fuse board. Is it...
Christmas crew, hope you all enjoying yourselfs. Ive been reading a thread on another forum about parallel paths. In certain installations, namely industrial/ some commercial, where the use of metal conduit, SWA, and steel framed building prevails. In such installs there is really is no way to...
Hiya Guys, I have a gas central heating boiler that is not switching on at all.
It's connected to a clock timer and then to a fused spur.
Boiler technician was out today to say the boiler is fine and I need an electrician, hence this post !
He said we have cross polarity on the fused spur. He...
I have a cable twin + earth coming from wall switch with 3 amp fuse - I want to connect it to some LED lights with a flex connector. LEDs have no earth, so what do I do with the earth wire coming from switch to flex connector?
Thanks
EICR recently done, Swa sub mains armouring used for cpc & MEBPC.
Installed 40 years ago, water/gas/structural bonding required, these are @ 10mm
Tncs earthing system @ origin which is remote from buildings 120mm tails.
The sub mains vary in sizes from 25mm to 50mm….what’s your thinking on...
Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and RCDs. I have read around this as much as I can but being relatively newly qualified my experience isn't as much as the collective members here so I...
I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use multiple electric heaters on a 32amp breaker if needed. The circuit consists 4 double sockets plus one single socket on the end, in a weatherproofed...
Can anyone tell me what the requirements are regarding visual inspections on earth sources, ie rods/conductive concrete etc? The scenario Ive got is that the original earth was a rod however it appears as if conductive concrete was installed subsequently but theres no documentation to support...
Having just replaced an immersion element with its life expired cable and switch, I'm thinking of replacing the switch (20A double pole) with a smart version so that I can control the hot water from my phone etc.
Both the immersion heater and the current switch have earth terminals, however the...
When replacing a light housing, I found the RCCB was somehow tripped. I first used a pen tester to check the wires and found them normal (no voltage). I then used a multimeter to test again. Here are the results:
L-N 7.4 v
L-E 6.8 v
N-E 3 V
After the RCCB was tripped, the readings were zero...
Earth has been snipped off, obviously.
I thought that earth wasn't required since the connections appear to be in some sort of maintenance free box, but is this right? If not, i can't see anywhere the earth could go.
EDIT just clocked the double insulated symbol, so i'm presuming that even...
Hello I’m a student learning about industrial wiring and circuits and we’re about to start learning about how to do loop impedance calculations. I have made a drawing of a three phase installation and was wondering if anyone could give me information on how I get the Ze Zs and R1 + R2. How would...
So despite living working in a country blessed with 300 days of sunshine I have not got my head around this solar thing, there is very few companies here who know what they are doing and buy off the shelf kits and rarely do they perform as sold and in many cases unregistered ones actually...
Is there any guides on how much earth leakage is acceptable in an industrial setting ie MCC. The reason i ask is it seems to be most sites have a degree of leakage which I’m not sure is due to many VSDs being used but recently a panel I saw had 0.6amps leakage but the motor starter was all good...