Went to look at a simple job, where the customer wants a number of recessed downlights installed in there bathroom replacing their existing fitting. They have bought their own 'B&Q special' fittings although they are not fire rated, and as i normally like to fit fire rated downlights i was after...
Went to house today. Rewired just 6 months ago. Tt - no rcd, ze 203. Low ceilings wanted metal light fittings added. 8 way consumer unit circuits tripled up in mcb. I said you need to get this sorted first. Contact the installer. Sorry but i'm not fitting the metal light fit tings which even a...
Having complete complete brain fade here...
what are the wire twisty things called the DNO use to support the concentric cables? and are they available to the trade?
I have a job coming up that needs a 16mm concentric span overhead. can anyone point me in the right direction?
Hi Guys,
Need some advise on RCD protection, I have just tested 112 rooms in a Travelodge in Wales and there is no RCD protection on the bathroom lights, the ceiling is over 2.25m and the light fitting is a L.E.D class 2.
Looking in the regs in section 701 & 415 and from posts I have read on...
Dean31
Thread
bathroom
class
fittings
light
lighting
protection
rcd
Hi folks, hope you all are well.
I've been asked to replace 3x battens fittings (6ft) to smaller fittings (4ft) in a office.
I reckon I can get them all fitted in 1.5 hours easily.
How much would you charge? Job is in Oldham. The location is only 8 minutes drive.
Thank you.
Hey All,
I have a client who's about to buy up the units next door to his current warehouse, and fit it all out similar to his current warehouse and move buildings (double the size).
We currently use a pair of 5ft Fittings per aisle under his mezzanine floor but we're looking at fitting...
Not sure if its of interest to anyone here, but we have a massive supply of assorted brand new Glamox Lighting, all appears to be High Frequency and ranges from all types of Maintained / Non maintained Emergency Lights to large Louvre and fluorescent fittings, along with some nice architectural...
Studded Punk
Thread
available
commercial
emergency
fittings
lighting
lights
products
Hi can any one tell me is it a regulation in a wood cutting workshop or mechanics garage to have vapour proof fluorescent fittings. Do i right it down on a electrical condition report.
Many thanks
Hi just after picking your brains. Had some quotes on LED fittings and as the client wants it as cheap as possible I have opted to explore the option of buying single anti corrosive 70w fittings and using LED lamp inside of them. All well and good except I need three of these emergency. They...
Hi
Can anyone suggest what type of light fittings are best suited to illuminate a flat roof skylight.
Customer has had a skylight fitted on a flat roof and at night just looks like a black hole in the ceiling
which she wants illuminated. Presumably some form of up lighters could be used but...
Hi all,
if using 2.5mm can i put a 16A MCB on a lighting circuit? never needed to before so a little unsure, but can't remember of they're limited to a certain amperage.
thanks
Hi all,
does anyone know if when running circuits in conduit , whether running a socket circuit and a lighting circuit together ,
is acceptable when passing through the light fittings ( fluorescent)
i personally think it is not as 2 circuits need to be isolated to replace each light and the...
Hi All,
I went up to look at a small office room that has three t5 54w light fittings. Each fitting is a double. The lights turn on and strike immediately. Once they are on the will slowly dim down then slowly go bright again ever once in a while (not flickering and light is equal along...
Here goes.....Im doing the 2357 C&G course. For one question I have to do a cable calculation for power and lighting circuits.
I am having issue with the ground floor lighting circuit, in a domestic dwelling, as in I am way off the 3% tolerance for volts drop.
Details as follows:
Plan view of...
Matty G
Thread
cable
ceiling
circuit
first
fittings
lighting
point
problem
switch
Hi all. I'm facing a little problem. We have fitted some light fittings that prefer type D mcbs (manufacturer said type c probably ok, but they are tripping). Unfortunately Hager do not make a type D breaker for my 17th ed CU. any ideas how to overcome the issue?
thanks
Does anyone use these? if so how much are you paying and where from? I have to quote to install several at a commercial office but im having no luck sourcing them locally, my wholesaler contacted Thorn but the prices they were quoting him were almost full retail
Hi all advice please just wired up a bathroom this week removed x 2 wall lights light fittings are of age old brass open lamp fittings. Light fittings are to go in the same place . The new installation consists of x 2 wall lights 1x fan and x2 3watt led lights recessed in a shelf at one end of...
527.2.1.
A flat with a multitude of downlights. I am not convinced that the G5.3 fittings are firerated and they are mounted through a double boarded ceiling which is a fire barrier (confirmed with the original architects). The fittings are made from a pressed metal which is very thin and...
I am selling these ones off cheap at the moment, they are Philips branded and retail at 40 quid each, selling them off 10.75 each which is a bargain.
I have a few boxes left and the price includes the t5 lamp and hard wiring adapter
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.