Hi Everyone,
Thank you in advance for your assistance, I"m assuming that having an unenclosed main switch is against the rules ?
Should it be sited within the same Consumer Unit or a separate enclosure ? The Consumer Unit, meter and main switch are housed within a wooden formica cupboard (2nd...
I am considering fitting a car charger using 6mm SWA to a new isolator switch in the meter cupboard and then 6mm T&E to the CU. It would save running the SWA all the way to the CU. Does anyone else do this and if so, which isolator is best for SWA? Thanks
I’ve just replaced a faulty 63A double pole isolator supplying a feed to a consumer unit several meters away to a flat.
ive come to do the notification on the niceic web page and there is no appropriate category to tick other than
circuit addition or alteration in a special locatiom
install a...
Hi all,
I have been asked to fit an extractor fan to a bungalow, normally I chase out a box for the fan isolator and locate it above the bathroom door, is there a reason I cant locate it in the loft, im guessing due to accessibility or something, but just wanted to check?
Many thanks,
Martin
Anyone know if there is a reg in regards to supply going in to the top of a rotary isolator. We are changing the isolators over for ac units, long story short they won't reach the top terminals now, so feed can only go in bottom. Just a 2.5mm 3 core swa.
Cheers
Hello all,
Just wondering if my en-suite is wired correctly .
There is a timed extraction fan and bathroom light in there .
There is an isolator switch outside the door. When you turn off the isolator the light stops working too.
Is this correct?
Should the isolator not stop the fan only and...
Setup:
Consumer unit fed via sub main from a 60A fused isolator switch. This is connected to the service head MET via a 2m earth connection.
How would one go about both calculating and documenting the Zs?
Would you be treating the fused isolator switch as it’s own db and therefore be...
I came across this today when changing a shower isolator that was stuck in the on postition.
40A Hager RCBO feeding 10mm² twin + earth to a pull cord shower isolator. On the load side of the isolator there was 10mm² going off to the shower as you would expect, but also from the isolator was...
Hi,
I have just replaced an old isolator switch on our shower and have discovered after wiring that the old live wire is a little exposed through the cable shield (presumably where it has been snagged in the ceiling at some point - see photo). I'm a little concerned that this could be a...
Hi There
Just wanted to double check if I have two separate supplies to a cooker and hob which are both hard wired and fed from 2 separate RCBOs do I need to fit two cooker isolators in the new kitchen. Many Thanks
Hi , I've recently moved into a propery with an electric shower installed , there is no isolation switch in the bathroom, the showers seems to be wired directly from the consumer unit , it is on its own supply and can be isolated at the board , is this sufficient to pass an electrical test ? Or...
What would you recommend as an 80A DP mains isolator switch?
Background: My DNO fitted a 100A cut-out fuse on 16mm2 service cables, despite their own published policy requiring 25mm2 service cables for such a fuse rating. (At least, the fuse carrier is labelled 100A). So, they are coming out...
HELLO
I have to install one oven(13amp) and one induction hob (30amp)
but those appliances not next to each other!2 meter between them!
just i would like to know ,which appliances need localy isolator switch whitin 2 meter?!
my plan to put oven isolator switch in the cupboard ,where will be...
Domestic single phase supply, TNCS, 25mm tails.
From supply to Fused switched isolator : Earthing conductor is 16mm.
From isolator to CU : Earthing conductor downgraded to 6mm for what ever reason I don't know.
Is there something in the regs that says after an isolator the conductor can be...
Hi there,
I have been asked to install a 32a supply for a hot tub for a client. I haven’t installed a supply for a hot tub before and having done a bit of research I am getting mixed answers about doing this on a PME system. I have a DB under the stairs with plenty of spare ways so I would be...
Hi everyone,
I'm still training so some advice would be appreciated :)
We have a shed about 60m from the house where would like a supply. I've already ran some 2 core 4mm SWA and wired up a CU with a 30mA incomer, it will be protected upstream by a 16A MCB. I went for 2 core because I want the...
I don't do PV, so not overly familiar with specific regulations.
Yesterday I was changing a consumer unit, and the isolator for the PV was adjacent to the consumer unit.
Due to needing a bit more space, I had to move this isolator a few cm and noticed it was single pole, switching L only.
A...
Hi guys.
Electrician will soon rewire my kitchen and some questions arises about sockets and isolator switches.
I think they look ugly and don't want them on sight.
Is it possible to install only two isolator switches one for oven and hob, and the second for electric instantaneous water heater...