pat testing

  1. Z

    Eicr query

    Hello all, my question is regards to a eicr. I have come to a property to do a eicr and have come across the lighting circuit neutrals in single insulated with no earthing. The live have earthing, which are single but the neutrals have none. Would this constitute a c2 or a c3. Thank you in advance
  2. J

    Insulation resistance on modern installations

    On initial verification of new installations I have been having a hard time with insulation resistance. With RCBOs, fixed LED luminaires, intelligent dimmer controls and other sensitive equipment now the norm on almost all installations how do we overcome this and still carry out effective and...
  3. M

    Are we allowed to use 5 amp fuses in 13 amp plugs?

    I work for a charity (Besom) that gets equipment that needs to be PATted. A lot of these come with 5 amp fuses. Please do the regulations allow you to use 5 amp fuses, or are you supposed to change them to 3 amp? Most of these devices are low power & they will run perfectly well on a 3 amp...
  4. A

    Testing high level lighting circuits

    Good morning everyone, I have been asked to do the initial verification on a newly completed building. so all the light fittings have been installed, false ceilings have been closed off,..etc. what is your suggestion for testing the lighting circuits?( continuity, IR tests) some of them are at...
  5. N

    What are the changes to PAT- new 5th Edition CoP

    Hello, We have a load of PAT testing coming up,... unfortunately. I'm aware that we have now moved from the 4th Edition to the 5th Edition of the code of practice (September). Has much changed?
  6. Moley

    How to replace the Kewtech KT77 date backup battery

    If you have a Kewtech KT77 and its asking you to enter the date and time each time you turn it on it means the backup battery is dead. I've seen sites charging over £60 to replace the battery. It's simple enough to do it yourself. The battery is available online for around £3 or from RS if you...
  7. S

    EIC to local council out of date??

    Hi after Issuing a EIC to a builder for electrical work(New ring and lighting to a kitchen extension,plus a new Ccu,) what would be a reasonable time that the builder should issue the certificate to the local council .He has only just done it but the cert was issued 18 months ago and the council...
  8. S

    Whats a Reasonable time to issue cert to council

    Good evening Guys.Quick Question . After carrying out a EICR for a new kitchen circuit and replacement consumer unit in December 2018, The builder has only just recently issued the certificate to the local council.Who have changed thier policy with a new man at the helm.I will state i am fully...
  9. R

    Kewtec KT77

    Not used my Kewtec KT77 since it was recertified in January. Switched on on Wednesday to be told it needed a service! How do I reset? If I leave it on it clears in 30 minutes. If I switch off and switch on it starts with no problems. Robert
  10. A

    Polarity test failure on SPD extension leads

    Evening all, This has probably been answered somewhere here, but in case it hasn't... I have a Fluke 6500-2 and had trouble testing SPD extension leads as you cannot drop the voltage to 250V using the IEC lead test button. I found a way to set up an auto test sequence to include EB and 250V...
  11. Lister1987

    Calibration - What actually goes on?

    Stupid thread time. We hear a lot about getting meters calibrated and checked regularly but not a lot of detail about what is actually done. Is it just testing against preset levels? If a level is off (beyond tolerance), how exactly is it corrected? Would love a point to point on exactly what...
  12. A

    Is my calibration showing my tester is faulty?

    Hi lads, I have a Megger 1552. I didn't really use it in the last couple of years. I was planning to get more into testing again, so sent it for calibration. Unfortunately, it failed. I was told it requires a new side socket where the test leads plug into the tester. As the tester is old...
  13. Z

    Eicr advice

    Hello all, I have a query on a eicr, I have been asked to do, the cu is installed vertically, just was wondering what code you would give. Thank you in advance 1595945271 1595945293 Please ignore the left side pic
  14. F

    Neutral to Earth

    how many ohms can you have neutral to earth without opening a 30mA RCBO. My thinking is If=V/R so, If=230/0.03 = 7.6Kohms So 7.7kohms will keep it closed
  15. OiNath

    PAT testing stored equipment

    Hi all, I've never posted in any sort of forum before, but this time... I cannot find answers anywhere. I need to know if items that are in indefinite storage still need PAT testing. I'm the maintenance man at an animal rescue centre, we have alot of equipment in storage e.g. heat mats...
  16. P

    Do you test the suppliers earth conductor for continuity??? (Initial verification)

    Hi guys, QUESTION: Do you test the suppliers earth conductor for continuity??? The guidance note 3 2.6.5 refers to regulation 643.2.11 which requires a continuity check be carried out on all protective conductors including: EARTHING CONDUCTOR, CPC's and bonding conductors. I am aware of the...
  17. S

    Help with certification

    Hi, Hope all are well, I just need clarification on a job Ive done with regards to the certification. I have wired an extension to house which includes a bedroom, kitchen and bathroom. The old house is installed to 17th edition. The extension has a new DB that the extension circuits are...
  18. A

    Fluke 6500-2 Surge Extension test

    Hello all, I am new to PAT testing and have a Fluke 6500-2. I am having an issue whereby I cannot seem to drop the voltage down to 250V when testing a surge protected extension lead. I have read in a couple of places that without a means of lowering it from 500V simply hit the IEC test button...
  19. C

    NAPIT Certification Scheme Pat Tester and testing help please

    Hi all, new to this forum and could do with some advice re Pat Testing. As the new law relating to EICR's to the private rented sector is coming up, I'm getting calls from my clients about the inspections but now they are also starting to enquire about having PAT testing done. I'm fully...
  20. J

    Plug -in Water Heater

    I came across a type of water heater that I haven't seen before. It has a 3 core flex attached and fits into the sink where an ordinary tap would usually go. I had to fail it as it had a two-pin continental style plug fitted and was being used with a unearthed adaptor. My question is would it...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock