protected

  1. B

    Previous fault

    Hi all, Today i came across a bit of a problem and to be honest not sure where i stand. Was called to go and look at a small job, to add a couple of extra sockets to a kitchen. Nice and easy surface mount. When i looked at the c.u it had been installed april this year, so i thought great rcd...
  2. R

    Domestic Hagar CU Terminal Bar

    Hi, I'm installing a 14 way Hager CU with a terminal rail supplied as standard with two neutral terminal bars and a larger earth terminal bar, the housing is helpfully marked with numbering. As I am installing three MCBs which will not be RCD protected I have an additional 5 way terminal bar...
  3. Z

    Illegal fuse box!

    Was on site today when the kitchen fitting brigade rocked up..5mins later i gets the call..kitchen fitters/electrician wouldnt do any electrical work in the kitchen..the fuse box was illegal!The consumer unit had been changed just over a year ago,and the guy had fitted a 16th split load board...
  4. B

    Max Zs readings where circuits are protected by 30ma RCD's

    I have noticed, a lot of max Zs readings on test certs (Where RCD's are applicable) are being blanket recorded at 1667 ohms. On a personnel note I consider this to be poor practice, and prefer to see max Z's taken from tables 41.2 41.3 and 41.4 of chapter 41 of the good old guide. My reasons are...
  5. A

    Spur off a 3036 protected circuit?

    I've been asked to add a spur (or possibly extend the ring) on a BS 3036 protected circuit. Dead basic job, just needs an extra socket in a bedroom. From my understanding, this can be put down as a Minor Works, but all sockets now have to be RCD protected to comply with the 17th, so if I'm...
  6. M

    RCD Question

    Hi Guys, a quiery for you, ( by the way I live in Western Australia) I was doing some work at the house today and was disconnecting some sockets for renovations, so i isolated the circuit but had to cut the T&E to get it out at the other end. Now the thing is that I have 3 phase incoming red...
  7. C

    Cable within domestic garage

    Can any one help me, does the cable fitted above the surface of a domestic garage wall need to be protected by conduit or will being clipped to the walls suffice? Cable will be RCD protected. Assessment evidence so it has to be correct. Thank you.
  8. M

    niceic assesment tomorrow!

    Hi to you all, got my assessment tomorrow and i was just wondering if there was anything in particular i should watch out for?Its for...
  9. D

    FCUs as circuit protection for part of circuit

    I'm sure we've all come across these scenarios: 16A supply to garage from consumer unit to a socket and an FCU feeding the lights with a 5A BS1362 fuse. 32A ringmain extended to feed conservatory with FCU with 3A BS1362 fuse feeding garden/patio lighting. Central heating supply from...
  10. C

    Extending/adding concealed cables?

    Evening I know the regs say that cables buried less than 50mm in a wall or partition need to be mechanically, or rcd protected, but if these circuits arent rcd protected what does everyone do when they extend a circuit? Add RCBO's? or mechanically protect the added cable? Not just for sockets...
  11. B

    socket/ kitchen sink

    hi all would like to know yor opinion on this one should i fail a installation purely on the basis that there is a twin socket on a kitchen wall practically above the drainer of the kithen sink would like your input pls, ta much
  12. R

    addition to lighting circuit

    Hi anyones thoughts, Whats the general concensus for an adding to an existing upstairs lighting circuit, main bonds in place, supplementary bonding to 16th in bathroom and protected by a 6a mcb:rolleyes: circuit is non rcd protected would you apply the 17th to the existing circuit or just the...
  13. J

    Shed Installation Disconnection time?

    Hi I have a socket Radial off a 20A MCB and a lighting Radial off 6A MCB in a shed the board is fed by a 32amp MCB protected by an RCD on a TNCS syatem in the house. If I want the first point of fault ie the shed to trip first should I be using an RCBO for a TT system that trips under .2s? This...
  14. C

    Should I put RCD on??

    Hi I have installed some downlighters/shower lights but these should be protected by an RCD - thing is on the Consumer Unit it does not seem to have RCD in the location I need it to be. I have attached a pic for ease of reference. The showerlights are on the same circuit as the rest of...
  15. E

    Kitchen Grid Switch

    Hi all, just planning a kitchen and wanted to use a 3 gang grid switch instead of having multiple fcu around one area of kitchen. I would propose to break into the ring from a nearby dbl skt down to grid switch (2 x 13a unswitched skts, 1 x 3a fuse carrier for hood). Any advice ideas, is...
  16. 1capybara

    WIRES BETWEEN PANELS PROTECTED ON LINE SIDE ONLY, not by load side breaker?

    Is This is an America code [NEC] code thing only? Or does 17th edition or IEC have the same thing? A wire runs between 2 panels is rated to carry 400 amps. Its fed from a 600A breaker on the line side, and has a 400 Amp breaker on its load side [the panel being fed from the other one]. Under...
  17. M

    Loft Radial Circuit...

    Hi, i would like to add some extra sockets to my loft , on inspection of the existing cct installed in the loft it looks like its a radial that has been taken from the upstairs ring, spured from the back of a bedroom wall socket. I know this is not ideal but if i was to add a Fused RCD socket to...
  18. C

    Lighting circuits not protected by RCD

    Just carried out an inspection on a domestic property - there is RCD protection on the sockets, water heater & Garage supply but no RCD protection on the lighting circuits & cooker. Just wondering what code to attribute to this - thinking code 4??
  19. H

    Multi Plug Socket Saftey

    Can I plug multi socket extensions into a 5 Way Plug Socket Extension Adapter Surge Protector. For clarification purposes can I plug one of these: 4 way switched extension, 5.0m: Amazon.co.uk: Kitchen & Home into on of these: New 5 Way Plug Socket Extension Adapter Surge Protector...
  20. B

    Zs reading across RCD

    Hi all with a heathy ZE ..22 on a TN-s system i had a R1+R2 of .40 oh my suprise to find that the Zs was 1.01at the furthest socketrechecked my ZE.22?? rechecked ZE from out going terminals of RCD .60 has any one else found this ps i realise that this reading is fine as RCD protected just...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock