Hi all,
I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.
He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution...
Hi guys, I've questioned something at my workplace and after receiving my answer I'm not overly convinced and would like some other experienced gods to chime in :)
On a new install in an existing property today I went to bond the Water and noticed it was already done, clearly many moons ago...
Hi guys, I'm having trouble deciphering some manufacturer's specifications / installation instructions for a three phase dual 32A outlet EV charger.
The model in question is the W22 wall mounted unit:
I can see that there are 2x 30mA RCD's inside the unit mounted on DIN rail.
I'm unsure...
Afternoon all.
Can I confirm that a protective conductor in section 16 of an EIC refers to bonding to services etc rather than a cpc of a final circuit?
I have a 6mm main protective bonding conductor from a 1981 install; adiabatic equation says this is sufficient and no signs of thermal damage. (Discussed in separate thread).
Gas was not bonded, it's a big job to run new cable so I've used redundant water bonding as now all plastic to bond gas...
Just been to a 1981 TN-C-S installation to fit new CU. Both Earth and Main protective bonding conductors are 6mm, which I understand was typical back then. 16mm tails with 60A DNO fuse.
Upgrading earth and bonding is gonna be tough as run up cavity and round the corner, I ain't never gonna pull...
Hi guys, I've been doing a bit of research into electrical software/apps as an alternative to the really bad Stroma software (Tracker Mobile) I currently have, I've sampled EasyCert Mobile which I found really straight forward however the layout in which it asked the questions didn't follow the...
Hi hope someone can help, i need to record the protective device on a MWC and not sure which to enter.
I have removed an old bathroom heater on a 20A radial and rerouted cabling to feed an RCD FCU, the load side of which feeds into the bathroom serving towel rail with a local DP (20A) switch...
Any thoughts about connecting main protective bonding conductors into the MET instead of distribution boards?
Watched a spark do it the other day and never really thought about it myself. Achieves the same result so it shouldn't be an issue.
Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints?
Here is what I have worked out so far for the circuit -
Ib=p/(Ulx√3) = 12000/(400 x 1.732) = 17.32Amps
From Table B6 I selected a C20 which has a max Zs of 0.87 Ω
20>17.32...
hi everyone,
I have got a job to do in a local hairdresser to change a consumer unit fed off an economy 7 meter.
My question is do you need to test and notify the works like you would in a domestic dwelling? Also is it mandatory that the incoming services of water/gas are bonded with 10mm...
Does anyone know where i can get hold a pair of shrouds for the fluke t140 voltage tester, mine came glued on when i got it years ago, when i pulled them off they cracked, it hasn't been used in a while only just getting back into the game so i need a pair to pass calibration.
I've seen some...
have come accross kitchen job where x 2 ovens are on a lollipop circuit.
6mm t/e from csu to 45a dp switch and then small 2.5 t/e ring with 2 oven outlet plates.
each oven only 2.4kw max.
question is if tested ok, ie zs and ring end to ends, is this ok to leave as is?
Noted today an interesting comment on page 43 of christopher kitchers Practical guide to inspection, testing and certification of Electrical Installations ( a great book )
Under Shower curcuits he states:
For this type of circuit it is possible to have a cable which has a current rating of less...
I've been asked to install a shower unit in a clients house and he only wants me to change the shower itself. The consumer unit has BS3036 rewireable fuses and no RCD protecting any of the circuits, including the existing shower circuit. He has already bought the new shower and only wants me to...
Hi everyone.
I'm after abit of help calculating cables sizes and protective devices for a 3 phase DOL motor.
I haven't worked on 3 phase equipment for many years and 3 phase calculations is as far back as college so please excuse my ignorance on the subject and not knowing answers to perhaps...
OK, going to keep this short.
Supply is 150mm 4 core SWA, with NO supplymentary earth ( calcs done by others, )
QUESTION IS. Do you NEED to run an earth ( is it a regulation) from banjo on inside to earthing terminal inside board. Common sense and a simple ohms continuity test (0.01 ohms)...
Guest 004
Thread
current
earth
earthing
enclosure
incomer
inside
main
panel
protective
submain
swa
Bit nervous about putting this on the open board, normally stick to the trainee section.
Hope i can get some help. I have recently qualified so dont be to harsh if im not 100% correct.
Ive been asked to help an older spark to pull a a 3 phase SWA cable. Ive been asked to design the circuit...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc