Hello All,
I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual current-operated circuit breaker on the supply side (25A, 30mA trip current). The RCD is there because some of the circuits supply power to outbuildings...
Called out to fault on RCD tripping maybe twice in a month for sometime.
Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which made matters worst.
So refitted original RCD Type AC for the time being.
Insulation Resistance measurements were 20 M ohms.
Ring continuity fine...
Hello
Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January.
Existing is a TT system with a solar installation fitted.
Current install has a 100A TP incomer, meter, C63 TP MCB, solar install, 100ma RCD, distribution board fitted with...
Hi,
I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can change the consumer unit but when put on an RCD the sockets trip. IR readings on the sockets are low but the customer isn’t in a position to have them...
Hello!
I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me to do a battery storage setup, specifically with EPS for battery power.
I'm stuck on my RCD selection because basically, I'm going to shift 4x...
At my place of work we have just had multiple LED advertisement screens fitted outdoors, the company specified 16amp RCBO’s for each set of screens. On powering up, the circuits were nuisance tripping due to earth leakage. So the company who installed swapped the rcbo for MCB’s.
The screens...
My builder has sprung a job on me.
New circuit required for a hob.
The CU has a single 30mA RCD, type AC.
I am still unsure exactly when I should insist on type A, and when I should just advise.
Would you guys be insisting on type A in this case, thus fitting a new CU (as it is an old NSB wylex...
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD feeding all the circuits in the consumer unit is AC type. Based on this, I believe I have to change this to an A type which is fine but the question...
Cant get my head round this :(
I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but no real answer. I have 2 intermittent faults on the go, one Dual RCD board, one split load, 1 RCD.
Dual 2 RCD
Occasionally the left RCD trips when...
Hi,
I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs.
I switched off all the power to the house by pulling down the double red switch on the rcd box.
When I turned it back on the individual rcd switch for the downstairs circuit tripped.
I turned...
Hi everyone,
I wondered if anyone could help me with something that has been niggling me please?!
When a Solar PV feed in circuit is installed and added onto a spare way of the RCD protected side of a split load dual RCD consumer unit (i.e. other final circuits are protected by that same RCD)...
Hi all.
Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!!
So, have an intermittent RCD trip at my home. Big old house with an installation of nearly all old tinned copper wiring, that for the last couple of years, hasn't missed a beat. Old...
Hi all
I have seen a schematic drawing for a control panel recently where they (whoever drafted the drawings, designed the panel) show a RCD before the 230v/24v dc PSU, and the PSU is the only device downstream of the RCD
in my mind this has no merit. The 24v secondary d.c side of the PSU...
Client has purchased a night flat in Edinburgh. Its perfect for using as a ST rental during the festival as the agents claim £6k a week is the value based on rooms and location. It was nicely decorated in 2018 and has a twin RCD Board . Wiring etc etc looks very good .Its a tidy install ...
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit type A in the future, but if following what is says in wiring matters should have type F for my inverter drive washing machine, as if that will ever...
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly. A few months ago it became so frequent that we had the RCD replaced. It would trip regardless of what load breakers were shut or open. No fault could...
Hi everyone,
Quick question can you fit an RCD without any neutral connections?
If I have a 3 pole circuit breaker which has all 3 poles terminated with a 3 phase supply (L,L,L excluding neutral or earth) on the primary side and I am using only 2 phases on the secondary side (L,L) to create a...
Hi Guys,
Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma and cannot find a person that has the expected knowledge and can explain and help, as yet unable to find information even from respected persons.
Let...
Hi all,
Grateful for your expertise regarding my confusion on the below.
Context:
French rural domestic property
Single phase supply, TT earthing
Supplier side RCBO (standard in France, usually next to the meter) - "disjoncteur de branchement" - 500mA, single pole protection, unspecified...