I've recently found the green light flashing and the red light on on our SMA 4000TL with the message 'Insulation resistance, check generator' on the display.
Checking the ERROROB2.CSV files I can see that this isn't the first time it has errored in this way, it has happened on odd occasions for...
Last year at night I was carrying out Electrical Inspection and Testing and Found the 300mm 4 core SWA sub main cable to a chapel was recording 0.09 ohms on carrying out high insulation resistance testing between phases. 25 thousand pounds later its rectified.
Would love to hear other people's...
Does any of you clever chaps know what the resistance of a 5kVA transformer should be? It's a 240-110 CTE.
I have a resistance of 0.16 Ohms (1400A)
If I recall what little transformer theory I covered years ago the impedance will increase when energised but how much I have no idea...
i've recently installed a new Consumer unit at home and will be using it as my first niceic assessment. I'm getting an insulation resistance reading of 1.7 on a lighting circuit in the osg it says minimum reading of 1 is this going to be ok?
I've discovered what section of the circuit is giving...
I am installing a C/U and the kitchen has some old Down lights installed with 10 x 12 volt transformers connected. I know I could disconnect all the transformers but I don't plan to do that as it will be a real pain due to how the plasterboard has been bodged. Some opinions suggest the IR...
Nicebloke
Thread
12v
connected
insulation
insulation resistance
insulation resistance test
resistance
test
transformers
Evening chaps,
In the process of taking my 2394/2395 testing course and just trying to fully get my head around insulation resistance testing predominantly in occupied domestic property's where it isn't possible to dissconnect all loads from the circuit.
I am aware of the need to link out the...
I've just done an EICR on an install earthed TT . The Ze on the rod was high 245 ohms , which in theory is fine as it is less than 1667 and the equation Ra X 0.03 > 50v is satisfied .
When the gas and water bonds are reconnected the Ze drops down to 4.4 ohms ,
Do I put another rod in ?
The...
Hi all got asked to do a pat job for client I under stand what I'm looking for check plug,fuse ,Lead,apliance for damage use pat machine we have this metro pat yellow box with three test buttons earth bond with a fuse selection and clamp I think pick half of rated fuse , insulation...
Lonespark
Thread
continuity
don't
earth
electrical work
pat
questions
resistance
Hello all
I used to believe that the power of circuit is running from live to neutral,then go back to the distributor.But when I see ring final circuit,I get confused...I know the power goes from both side of live cable,then it goes back to the circuit breaker?
Sorry about my poor...
dyschen
Thread
circuit
current
electrical work
final
resistance
ring
ring final
wiring
Hi,
How can I change earth resistance (R) value into soil resistivity (Rho)? Is this formula correct, ⍴ (Rho) = 2πAR (A = Distance between pegs, R = Earth resistance).
Regards,
L.
Hi all,
I'm an architecture student and would be extremely grateful for some advice with a tool/machine that im making. Basically i'm creating a large hot wire cutter and need to pass enough power through to heat a 1.6mm, (or 2mm gauge) 1m long nichrome wire to a temperature suitable for...
Hi everyone. I'm looking for advise on how to test IR on commercial lighting. There's so many lights on 1 circuit , do I have to take out all the lamps in all the lights to perform the test or can I simply test between LN -E ?
Even though I have spent lots of time testing domestic installs and...
Hello All,
1.Star connected earthed neutral Source to Star connected earthed neutral load? Say if a L-G fault occurs between the source and load, How does the fault current gets distributed? To the source side neutral or load side neutral?
2.Star- Star Transformer. Neutral earthed on both the...
Is this right anyone?
So basically I'm gonna test the whole consumer unit with an insulation resistance test rather than every circuit would you do basically I need to show my college and I've only been testing since last week and need to show an insulation resistance test of the whole board and...
Hi I want to test the whole board at once with an insulation test so turn off main isolator and breakers turn tester to 500v? And is the best thing to do, the incoming tails L+N put in a link between them and connect your probes to the link and other to earth also can you still operate light...
Hi folks,
Was sent out to a job today to add in a hot water pump underneath a kitchen sink in a kitchen that had recently been done up. Took with me just a socket thinking that the electrician doing the kitchen work would have RCD'd it - but no. The woman had her own joiner do the work so I'm...