swa

  1. HappyHippyDad

    Ideas for finding fault area in underground swa?

    Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the main consumer unit in the house to a garage consumer unit. The poor readings are not on the outgoing circuits in the garage. There must be a join...
  2. M

    5 core swa cable calcs

    Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable calcs etc? Apologies but just moving in to the 21st century never used 5 core before
  3. P

    UK Solar SWA cable run 10mm or 16mm

    Morning, I was just looking for some advice on what other sparks would do for the following scenario:- A detached Garage is going to house a 7.4kw Solar Array and around 12kw of battery storage. The supply needs to return back to the main house (cable run approx. 22m) to DNO/consumer location...
  4. J

    SWA as cpc to submain-Suitability, & PC's on RCD's.

    Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the warehouse via a 2 core 16mm SWA buried under concrete with the SWA used as cpc (60A BS88 is the protection). Mains intake in the warehouse is a 3 phase...
  5. R

    UK Class II enclosure + gland recommendation for divorcing SWA armour at TT outbuilding/shed?

    As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring of a two core SWA supplying an outbuilding/shed. The supply to the property is overhead TT, so DNO provide phase and neutral only, a sub 20 ohm rod...
  6. newfutile

    Swa outer connected both ends

    During an EICR I havr encountered swa feeding 1 lamppost not glanded at the post end, the feed is connected to the chassis of the 3 phase DB. I was thinking this would attract a C3 code, but I thought I post it and ask others what they think? It's fed from a 6 amp type a hagar rcbo tho it...
  7. S

    Running 2 phase in swa

    Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and another ac unit has been added due to a design error. Questions are, can you get a 2phase mcb to fit a schnider PoN board? Are you allowed to supply 2...
  8. S

    SWA/SY cable in a fibre duct

    OK. I can already feel the eyes rolling I am working in a yard where we are having trouble with vandalism. There is absolutely no way of getting a cable (easily) down the to front gate, as the perimeter is hedging and the car park is concreted entirely. The ONLY duct to the gate from the...
  9. cliffed

    Swa armouring let it be Earth

    How come some qualified electricians will argue & argue about earthing the armouring of the cable. Seen many jobs where they use plastic junction boxes & no earth continuity on the armouring. Regardless of how many cores are used it still needs earthing. Their biggest argument is it’s only for...
  10. M

    Where is the correct place to terminate a seperate earth ran with a SWA ??

    Hi all. I have noticed there are two schools of thought here when running a separate earth with a SWA to a large DB, where is the correct place to terminate the earth ? . We can go straight in to the internal copper earth bar as we have spare unnumbered holes for it , or we can lug it and go on...
  11. S

    SWA protection to car charger query

    Qualified electrician has installed Zappi car charger outside house. Grid incoming goes to DNO cutout then to SPD then to meter then to henley block then to RCCB then to SWA cable out wall and to charger mounted on outside wall (about 4m length SWA). I just learnt that RCCB gives no overcurrent...
  12. T

    Advice on cable for EV Charge Point Cable

    Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single Phase and I have appointments booked with my supplier and DNO to upgrade meter tails and cutout fuse respectively. I'll get a spark to do all the...
  13. S

    Correct way of routing SWA supply for flats ?

    Hi Fellow electricians, I’m recently qualified and I would like clarification on swa supplies for flats, my boss says this is okay but I’m not sure. So my question is if my supply is downstairs can I run my SWA through joists under floor boards and stud wall cavities without rcd protection. it...
  14. I

    Suitability of SWA armouring as CPC

    https://gadsolutions.biz/regulations/swa-as-the-cpc Anyone know how reliable the tables on this website are for determining whether the armouring of a cable can be used as it's earth? Not too sure how old the page of the website is so could have changed since it was made or could have been...
  15. naylorpd

    Stripping SWA for copper

    I'm in Azerbaijan, and in our company store we have a number of drums of cable, all upwards of 5 years old and basically unsaleable. We're looking at the possibility of selling for scrap and the usual question is whether to sell it as-is or to strip it ourselves down to bare copper.The selling...
  16. Dartlec

    Feed to flat in escape route - best option?

    I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted building. The ground floor is a separate front entrance, the upper flats have a side entrance with stairwell, which is protected with smoke and EL...
  17. kesterlester

    Are many potential uses of SWA **UNEQUAL** tee connectors illegal?

    It seems to be easy, these days, to buy fittings (often containing resin) that allow someone to tee into a pre-existing SWA cable. Some of these are equal tees, and some are designed so that the "new" branch cable has a smaller diameter than the main "through" SWA which was broken into. I'm...
  18. davesparks

    Flylead to SWA without a banjo.

    I've been working my way through some EICR remedials in a theatre and one of them is to sort out a slightly high Zs on a submain. Thankfully whoever installed it put the banjo on the gland and even put a bolt through it, they just didn't add a flylead, so its going to be relatively easy to fix...
  19. A

    SWA banjo fly lead size

    Hi all. Could I ask some advice please regarding SWA banjo fly lead sizing. Can anyone explain what sizing or how you size the required earth size when: A) The armourings are not used as cpc B) When armourings are used as CPC? I’m still learning and can’t find anything explain I guess this...
  20. S

    Swa install to hot tub

    Hi, looking for some advice, 6mm swa allready installed to a hot tub Client now wants additions and my calcs say the original swa is allready too small. 26a but its120m run, im advising 16mm 2core. However the swa installed is 4 core so was thinking of doubling cores together to save on time/...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock