Afternoon everyone..
During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the main consumer unit in the house to a garage consumer unit. The poor readings are not on the outgoing circuits in the garage.
There must be a join...
Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable calcs etc? Apologies but just moving in to the 21st century never used 5 core before
Morning, I was just looking for some advice on what other sparks would do for the following scenario:-
A detached Garage is going to house a 7.4kw Solar Array and around 12kw of battery storage. The supply needs to return back to the main house (cable run approx. 22m) to DNO/consumer location...
Been looking at a CU change in a small office and would appreciate comments on the following.
Office is supplied from the mains intake in the warehouse via a 2 core 16mm SWA buried under concrete with the SWA used as cpc (60A BS88 is the protection). Mains intake in the warehouse is a 3 phase...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring of a two core SWA supplying an outbuilding/shed. The supply to the property is overhead TT, so DNO provide phase and neutral only, a sub 20 ohm rod...
During an EICR I havr encountered swa feeding 1 lamppost not glanded at the post end, the feed is connected to the chassis of the 3 phase DB.
I was thinking this would attract a C3 code, but I thought I post it and ask others what they think?
It's fed from a 6 amp type a hagar rcbo tho it...
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and another ac unit has been added due to a design error.
Questions are, can you get a 2phase mcb to fit a schnider PoN board? Are you allowed to supply 2...
OK. I can already feel the eyes rolling
I am working in a yard where we are having trouble with vandalism.
There is absolutely no way of getting a cable (easily) down the to front gate, as the perimeter is hedging and the car park is concreted entirely.
The ONLY duct to the gate from the...
How come some qualified electricians will argue & argue about earthing the armouring of the cable.
Seen many jobs where they use plastic junction boxes & no earth continuity on the armouring.
Regardless of how many cores are used it still needs earthing.
Their biggest argument is it’s only for...
Hi all. I have noticed there are two schools of thought here when running a separate earth with a SWA to a large DB, where is the correct place to terminate the earth ? . We can go straight in to the internal copper earth bar as we have spare unnumbered holes for it , or we can lug it and go on...
Qualified electrician has installed Zappi car charger outside house. Grid incoming goes to DNO cutout then to SPD then to meter then to henley block then to RCCB then to SWA cable out wall and to charger mounted on outside wall (about 4m length SWA). I just learnt that RCCB gives no overcurrent...
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point.
Supply is a standard Single Phase and I have appointments booked with my supplier and DNO to upgrade meter tails and cutout fuse respectively.
I'll get a spark to do all the...
Hi Fellow electricians, I’m recently qualified and I would like clarification on swa supplies for flats, my boss says this is okay but I’m not sure. So my question is if my supply is downstairs can I run my SWA through joists under floor boards and stud wall cavities without rcd protection. it...
https://gadsolutions.biz/regulations/swa-as-the-cpc
Anyone know how reliable the tables on this website are for determining whether the armouring of a cable can be used as it's earth?
Not too sure how old the page of the website is so could have changed since it was made or could have been...
I'm in Azerbaijan, and in our company store we have a number of drums of cable, all upwards of 5 years old and basically unsaleable. We're looking at the possibility of selling for scrap and the usual question is whether to sell it as-is or to strip it ourselves down to bare copper.The selling...
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted building.
The ground floor is a separate front entrance, the upper flats have a side entrance with stairwell, which is protected with smoke and EL...
It seems to be easy, these days, to buy fittings (often containing resin) that allow someone to tee into a pre-existing SWA cable. Some of these are equal tees, and some are designed so that the "new" branch cable has a smaller diameter than the main "through" SWA which was broken into.
I'm...
I've been working my way through some EICR remedials in a theatre and one of them is to sort out a slightly high Zs on a submain.
Thankfully whoever installed it put the banjo on the gland and even put a bolt through it, they just didn't add a flylead, so its going to be relatively easy to fix...
Hi all.
Could I ask some advice please regarding SWA banjo fly lead sizing.
Can anyone explain what sizing or how you size the required earth size when:
A) The armourings are not used as cpc
B) When armourings are used as CPC?
I’m still learning and can’t find anything explain I guess this...
Hi, looking for some advice,
6mm swa allready installed to a hot tub
Client now wants additions and my calcs say the original swa is allready too small.
26a but its120m run, im advising 16mm 2core.
However the swa installed is 4 core so was thinking of doubling cores together to save on time/...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.