tests

  1. L

    Energy supplier refuses to restore power until inspected?

    Dear experts, I had a phone call from a landlord who wishes to let a studio flat out after it has been unoccupied for about a year. A prepayment meter is installed which has obviously ran out of credit and there is no power to the property. Apparently the energy company won't restore the power...
  2. Prime Design

    IR Tests & Fault Finding

    Hi fellow electricians, I'll get straight to the point. How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead...
  3. P

    complete tests

    Hi there. could someone tell me when carrying out testing and the installation fails a particular test i.e IR, does the person testing stop right there, informs the person ordering the inspection & test and fails the installation or come back again when the fault is rectified? would the testing...
  4. Baker1988

    sequence of tests

    Hi i am doing some college home work (which i am fine with) its to do with the sequence of tests and i have been looking in guidance note 3 and in 2.7.4 is the sequence of tests but can i ask who does "f" 'insulation resistance of non conducting walls and floors' i ave never heard of this before...
  5. F

    Practice Exam Tests

    Does anybody have any information about free downloadable test exams for CG2365 or similar, I am presently trying to locate 2365-202/203 Many thanks in advanced Newboy Multiple choice practise software for the City and Guilds 2365 210 exam communicating with others
  6. G

    Sequence of testing

    Afternoon all, i was wondering if any of you could help me with this question.. Why must testing be done in sequence?
  7. O

    Street lighting testing!!! Help !!

    Hi all , i am am about to be starting with a new firm who insist on all electrical test s to be done on each column with a new lantern. Could anyone help me with the procedure of these test and exactly how to perform them as I know they would differ from a domestic testing . Any help...
  8. N

    3 Phase motor on AHU

    Hi everyone. Have a problem iv not come across before. So the motor has stopped running on the AHU in our building. It's controlled by an inverter. First thing I done is check the inverter was running (which it was), then checked for voltage at the motor terminals. To my surprise (and probably...
  9. A

    Led floodlights tripping but dead tests clear...

    Hi, just finished a job installing 12no 100w led floods from ansell lighting and they are causing me problems. The lights are switched alternate over two switches, so one switch does 6 and so does the second. First of all I has them connected to a B10 crabtree loadstar mcb which tripped 9/10...
  10. M

    Testing question

    hi all I am currently working as a mate the contractor I'm working for which I shall not name does the following test. he only measures zs doesn't do continuity r1 r2 he says that there is a good earth return if these results are within those permitted, he takes his ze from his zs to obtain his...
  11. N

    Fluke 1652c

    Going shopping tomorow. Thinking of buying above. Anyone have one.Are they a good piece of kit,user friendly?? Any tests they can't do,with regards to installation tests and periodic? I can't think of any. Thanks in advance
  12. D

    Annual EICR Tests

    Guys, I work for a company that do a lot of annual testing. As a company we test 100% of each DB every year as clients request. We have noticed now that some of the older DBs the screws on neutral bars are beginning to become worn. (Yes we do use correct screwdrivers and tighten then to the...
  13. NDG Elecs

    RFC testing shenanigans

    Hello Chap/ettes, Testing a RFC today. End-End values spot on: 0.19/0.21/0.34. All IR tests good bar N1-CPC2 which was 0.0 mega ohms. N2-CPC2 was >299 mega ohms. Why, if I am getting 0.21 and 0.34 on the end-end am I not getting 0.0 m ohms on both neutrals? Is it to do with the resolution of...
  14. S

    Am2

    Hi everyone, Im going to be doing my am2 in September, I'm very confident with the build. The only thing I can't get around is the live tests, what order do the live tests go in? Also some help on fault finding. Cheers jimi
  15. S

    Eicr

    Hi guys, how many eicr tests do you think is reasonable to carry out in a 7 hour day that's including paper work and not a bodged test lol mainly on 3 bed houses with aprox 6- 10 circuits
  16. J

    Ir test on bs 3036 wylex board

    Hi all, l recently did a eicr on a fish and chip shop. 3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means. When it came to the IR test, l tested the norm tests, L-E, L-N & N-E. Bearing in mind that we are now supposed...
  17. Midwest

    What tests do you carry out for a Minor Works Certificate

    I've been reading here & elsewhere about issuing a MWC for accessory replacements, and the merits of. Me personally I agree with issuing a MWC for a like for like replacement of a socket outlet for example.However, my MWC requires results for essential tests: 1) R1+R2 or R2. 2) Insulation...
  18. J

    voltage query

    Hi, iv changed an outside light for a customer and completed all the necessary tests. After powering up I got 230v between L and N but strangely 120v between L and E. The tests were done at the jb prior to the light fitting. Any ideas what could be causing this? Thanks in advance!
  19. S

    fluke 1652 multifunction tester

    Hi, quick question, Do the test leads need to be nulled for ze & pfc. I have been told they don't as there resistance is negligible. Cheers
  20. D

    What Tests Do I Need To Do?

    Basically I've got my Level 3 Testing and Inspection exam soon. Now I know from friends who have done it already that I will 100% be testing a shower circuit and a motor circuit, I'm having a complete brain spaz at the moment and I can't remember what tests need to be done for those circuits...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock