Hi
A job that I'm currently looking at requires a 300A 3ph supply to a unit. The cable will be 100m long so the calc comes out at 240mm2. This cable is to be pulled down a duct, the main issue is it's weight and size will be a battle. I'm thinking of running two 95mm2 in parallel that would make...
Just been speaking to a neighbor who has recently had a new boiler installed.
For some reason (probably not CPS) they have not used the DP FCU that the old boiler was wired into and instead put a plug on it and used an existing double socket.
Has this been done to avoid having to issue a MWC...
Working with imperial sized conduit. It is 5/8".
Would like to fit double back boxes to replace the original singles, the problem being is that the knock outs are 20mm, so they are too big to fit the conduit bush to. I have been to a few electrical wholesalers trying to source parts from...
Have been working in a building installing emergency lighting. Was taken back by the size of the Main Intake Room. Biggest Intake Room I've ever been in!
Like to see other people's pics and experiences of any other interesting buildings etc.
Thanks
Sam
Sam cook
Thread
attach
cost
equipment
install
looks
panel
probably
using
wonder
working
I currently have an intermittent issue with a disabled alarm system. The pullcord has a fault monitor connected across it in the form of a resistor and diode in series which I suspect is the culprit. The diode only reads continuity one way as expected but the resistance through it the correct...
Hi all I've recently fitted a underfloor heating system using heatmiser controls and a Worcester Bosch oil system boiler but I'm a bit unsure as to what connection to make to the boiler. On the heatmiser wiring center I have an in and out boiler enable volt free, and at the boiler I have L N E...
Hi all,
I'm not an electrician, I come here for advice.
I wondered if it would be possible and safe to run a long, thick, armoured cable from my outdoor plug on my conservatory underground around 20 metres to power an outdoor light?
Or would I need a full new circuit ran from my consumer unit...
Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints?
Here is what I have worked out so far for the circuit -
Ib=p/(Ulx√3) = 12000/(400 x 1.732) = 17.32Amps
From Table B6 I selected a C20 which has a max Zs of 0.87 Ω
20>17.32...
Good Morning,
Due to busy times i need to start using a sub-contractor to help with the work load, i have spoke to Stroma (who i'm currently with) and they have said i need to get a contractors agreement put in place.
Has anyone had any experience with using sub-contractors? If so, apart...
Well I thought I had all the tools and gadgets going! I bought a dust and debris eliminator (DADE) this week and I'm really impressed.
It's used for catching the dust from drilling downlighters. Probably the simplest tool I own, but definitely one of the best (perhaps after my wire coat...
Hello,
Can anyone please assist me in the following:
My client wants to feed a Mono water pump from a distance of approx. 360 metres.
I have a choice of using PVC/PVC cable taped to a catenary wire. I am not happy with this method and would prefer to run PVC/PVC/SWA cable underground. The...
Im travelling abroad to a country that has no earthing arrangement and my friend would like me to do a bit of work on his house. My question is Whether or not i could create a link between the Neutral and Earth bar to create a tncs system.
I know it sounds strange but i have just been thinking...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.