Discuss 100+ volts down earth ???? in the UK Electrical Forum area at ElectriciansForums.net

JD6400

-
Mentor
Arms
Reaction score
742
Just had a call from two of our men who are testing an agricultural dealership , they have found 100 + volts on one of the lighting cpc's .
To cut a long story short , they have cut around 2 and a half meters out of the 10 meter the circuit ( 1.5 T+E ) and have it laid on the floor . They say that they are getting +500 between all conductors ( Two different Fluke MFT's ) , but when they put power on it ( without connecting the cpc either end , they are still getting 100 + volts on it !

Any thoughts !????
 
Just had a call from two of our men who are testing an agricultural dealership , they have found 100 + volts on one of the lighting cpc's .
To cut a long story short , they have cut around 2 and a half meters out of the 10 meter the circuit ( 1.5 T+E ) and have it laid on the floor . They say that they are getting +500 between all conductors ( Two different Fluke MFT's ) , but when they put power on it ( without connecting the cpc either end , they are still getting 100 + volts on it !

Any thoughts !????


Is the cpc connected to the MET? Have they done a R1 + R2 test? It sounds like a induction/eddy current if there is a break in the cpc. Find the break in the cpc re connect it and the 100+ volts should go away!
 
Yeah sounds like a coupled or induced voltage. Use an analogue voltmeter for exactly the same test and it will probably show 0v.
 
Induction voltages are more common in systems wired in singles ie cpc with phase and no neutrals to cancel out phase induction. However they can occur in systems wired I. Twin & earth my guess is that the induction voltage is carried across on the switch wires (again no neutrals). If an induction voltage is carried across to the cpc it goes away when the cpc is connected to the MET. I don't know why though I'm not that clever!
 
At the moment it is a 2.5m length of T+E laid on the floor ( cut out of the circuit ) , with live and neutral connected but not the earth . All conductors have megged out at +500 on two separate Flukes , but they are still getting over 100 v on the earth conductor ?
I have since spoken to them again , and they say that it appears to be the same on other lighting circuits as well .
They are bringing it back to the stores , and I will check it out next Tuesday when I am back down the yard again .

Thanks for the reply anyway .
 
If they've meggered the three conductors and all was okay then it has to be an induced voltage onto the CPC which is not connected therefor it's floating. If they're worried about it then connect the CPC so it's at earth potential and check the leakage current with an earth leakage clamp meter. Otherwise save a lot of messing about and try the original test with an analogue tester as I previously suggested.
 
Nice to see i'm not the only 1 that still uses an Analogue meter

I'm beginning to think they should only allow sparkies to use analogue testers for the first few years when hopefully they're experienced enough to know the importance of an instruments input impedance and how it affects the results it's going to give on certain tests ;).
 
Not trying to teach granny to suck eggs, but yet certainly sounds like induced voltages. Have they checked Earth continuity on the lighting circuits ?
 
I hear what you all are saying and appreciate the input , but it is on a 2.5m length of cable .
Would that be long enough for this to happen ?
 
I have to admit that they did , and as expected it did disappear .
But it apparently created quite a spark on the whole circuit .
I originally suggested that they have a fair few fluorescents in the place , but none were on at the time .
It is the first time I have come across this on such a scale and especially on such a short length of cable .
 

Reply to 100+ volts down earth ???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
622
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
784
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock