Apologies, it's just i was working on council properties previously with another company and they always installed
View attachment 37425
Wylex 100A DP Supply Isolator

but now with another company also working on kitchen rewires and CU upgrades but we are not installing the above. And when mentioned they said due to them not being spec'd by the client so was just wondering whether these are a requirement so the installation has a means of isolation other than removing the main fuse...

So to clarify, if the tails from meter to CU are going to be longer than 3m, the DNOs suggest the installation of a suitable switch fuse to protect the cable run from the meter to the CU as they will not guarantee disconnection times of the main fuse and it's not there to protect your equipment and cabling, it's there to protect the DNO infrastructure.

The installation of an isolator for runs less than 3m is useful as it allows upgrades to be carried out beyond it in the future. Without it, you're in the realms of requiring the seal fairy to come along and hack off the service head or meter seals to isolate the installation for say a CU change. With it, you can safely isolate and lock off the whole installation. But it is optional.

It's also worth noting that some electricity meters also have an isolator on the outgoing terminals which can serve the same purpose. Personally if I'm having the power turned off, I always try and fit one to avoid the hassle of DNO/supplier interaction in the future.

Hope that clarifies things :)
 

Reply to 100amp Switch Fuse required or not required? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
228
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
812
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock